What am I doing wrong

1568101118

Comments

  • maybemark
    maybemark Member Posts: 1,131
    amazon has them for 66 bucks
  • Gordy
    Gordy Member Posts: 9,546
    First get a,good thermometer to accurately check it. If it is bad you'll need it to check the new one to.

    I questioned it last night when outdoor temps were pretty consistent in the read out. Check a,weather station close to you on line it's colder than 30 out .
  • maybemark
    maybemark Member Posts: 1,131
    supply house has them for 46 bucks
  • SWEI
    SWEI Member Posts: 7,356
    First verify that the one you have is actually bad. Assuming it is, get it replaced under warranty.
  • maybemark
    maybemark Member Posts: 1,131
    it's still under warranty, I don't know if i told you, when i called up lochinvar to register it. They told me, no warranty, cause i am not a certified contractor
  • SWEI
    SWEI Member Posts: 7,356
    That may or may not be enforceable. Check with your state department of consumer affairs.
  • maybemark
    maybemark Member Posts: 1,131
    it's bad, it's not 30 outside, it's colder. i think my kitchen would be closer to being right, and that says 25
  • maybemark
    maybemark Member Posts: 1,131
    at this point in time, I just want a comfortable house
  • maybemark
    maybemark Member Posts: 1,131
    I can call the dealer I bought it from, and ask for a new one, I'll try that tomorrow
  • maybemark
    maybemark Member Posts: 1,131
    the weather station close to my zip code says 26, same as the kitchen outside thermoeter
  • maybemark
    maybemark Member Posts: 1,131
    any settings i should change to be able to bring down the temp, and make it more efficient
  • maybemark
    maybemark Member Posts: 1,131
    I set the shift reset to -5
    system 114/114
    flame 24%
    out air 29
    inside 73
    basement radiator is cold
  • maybemark
    maybemark Member Posts: 1,131
    my knee is killing me all day
    probably from the up and down the stairs yesterday
  • Gordy
    Gordy Member Posts: 9,546
    Last night your ohms were 32k at 25degrees it should have been around 40k
  • maybemark
    maybemark Member Posts: 1,131
    it wasn't 25, I think it was 30
  • maybemark
    maybemark Member Posts: 1,131
    maybe it was 28, because it was between 2 numbers
  • maybemark
    maybemark Member Posts: 1,131
    it doesn't matter the sensor is bad, and i need to replace it
  • maybemark
    maybemark Member Posts: 1,131
    system 114/114
    flame 38%
    out 29
    stat 73
  • SWEI
    SWEI Member Posts: 7,356
    maybemark said:

    it doesn't matter the sensor is bad, and i need to replace it

    Maybe. You need to put it in the same spot as a known good (or mostly good) thermometer, at two temps. Stick them both on the back porch for 10 minutes, then measure the resistance. Then put them both on a table inside for 20-30 minutes and measure again.
  • maybemark
    maybemark Member Posts: 1,131
    system 115/115
    flame66%
    out sensor 29
    I changed other settings
    out low -4
    out high 60
    sp low 140
    sp high 95
    out air shut 95
  • maybemark
    maybemark Member Posts: 1,131
    shift reset 0
  • SWEI
    SWEI Member Posts: 7,356
    When you change a bunch of things at the same time, your chances of figuring out what's going on go way down.

    That 'sp high' number is probably a bit high.

    The 'out air shut' definitely is ;)

    Some time tomorrow, you need to disconnect the outdoor air sensor, set the boiler to a fixed temp that you think might be about right, and run the tests I posted above. If the sensor tests out OK, the location is bad. Is there any chance the wall it's on has a hot pipe behind it?
  • maybemark
    maybemark Member Posts: 1,131
    no way is the wall warm there
    12" of brick
  • maybemark
    maybemark Member Posts: 1,131
    out air shut is defiantly (what)
    I just caulked the hole where the wire went thru, I did feel a tiny bit of cold, if cold is coming in, then hot is getting out

    what numbers should i change then?
  • Paul48
    Paul48 Member Posts: 4,469
    Mark.....You should have gotten a service manual with that boiler. It has a description of all the parameter settings and what they are.
  • maybemark
    maybemark Member Posts: 1,131
    I don't see any test you posted above
    Paul, i have the service manual
    it explains and shows defaults
  • maybemark
    maybemark Member Posts: 1,131
    Kurt, I'll change everything back the way you told me
  • maybemark
    maybemark Member Posts: 1,131
    I changed everything back how kurt told me the 1st time but I did put the shift reset to -2
    I also caulked the hole with the wire
    the sensor went up to 30, after i caulked the hole
  • maybemark
    maybemark Member Posts: 1,131
    117/117
    out 30
    inside 73
    flame 71%
  • Paul48
    Paul48 Member Posts: 4,469
    Shift the reset curve -15, and see if that target temp goes way down.
  • maybemark
    maybemark Member Posts: 1,131
    it will, I'll try it now
  • maybemark
    maybemark Member Posts: 1,131
    system 110/104
    out sensor 30
    inside stat 73
    flame 20%
  • Paul48
    Paul48 Member Posts: 4,469
    Leave it there and let the house cool off.
  • maybemark
    maybemark Member Posts: 1,131
    I think that's a good idea
  • Paul48
    Paul48 Member Posts: 4,469
    Even if the sensor is NG, you can still gain valuable info from it. It thinks it's 30 out, and 117 was to high a target....that's useful info.
  • maybemark
    maybemark Member Posts: 1,131
    what would think a good target number is for 30?
    things like this, someone who has been around, might have an idea. but, since I know so little, and the manual at times is like reading Greek.
    Now, if you ask me about finish carpentry, I would know
    thanks Paul
  • Paul48
    Paul48 Member Posts: 4,469
    There's no magic number. It's the number that holds the house at the perfect desired temperature.
  • maybemark
    maybemark Member Posts: 1,131
    ok, I understand that
  • Paul48
    Paul48 Member Posts: 4,469
    If you find the house getting cold, move to -10
  • maybemark
    maybemark Member Posts: 1,131
    system 106/104
    outside sensor 30 (we know thats wrong)
    inside 73
    flame 20%