What am I doing wrong

145791018

Comments

  • maybemark
    maybemark Member Posts: 1,131
    living room is 69
    kitchen is 73
    bedroom is 74
  • maybemark
    maybemark Member Posts: 1,131
    system 109/109
    flame 69%
    outside 30
    inside stat room 73
  • SWEI
    SWEI Member Posts: 7,356
    I would start by lowering the target water temp at the end (the one with an OAT of 60-something) of the ODR curve -- maybe 5°F or so.
  • maybemark
    maybemark Member Posts: 1,131
    I just came up and brought the shift reset curve to -14
  • maybemark
    maybemark Member Posts: 1,131
    is the shift reset curve the same as what you are asking me what to do?
  • maybemark
    maybemark Member Posts: 1,131
    i see the ort in the manual, it has high and low
  • maybemark
    maybemark Member Posts: 1,131
    should I raise the shift reset higher? and if so, to what?
    then lower the out door air high?
  • SWEI
    SWEI Member Posts: 7,356
    Caveat: I have some experience with the Lochinvar controls, but I do not work with them as frequently as some here.

    The shift feature moves both ends of the curve up or down at the same time. I would set that to zero and move both endpoints down. I'm not sure where you were before you shifted down 14, but I might start moving the bottom down by 16 and the top down by 22. Then watch for a few hours.
  • maybemark
    maybemark Member Posts: 1,131
    default for the high outdoor air is70
    default for the low out door air is 180
    now you want me to change the shift reset curve to 0, which default
    then change the low to 16 and the high to 22?
  • Gordy
    Gordy Member Posts: 9,546
    Where are you at on shift?
  • maybemark
    maybemark Member Posts: 1,131
    the oda does not go as low as your asking for both high and low
  • SWEI
    SWEI Member Posts: 7,356
    Are the first two parameters still at the default settings? If so, you have effectively changed them to 56 and 166 with the -14 shift. We know that 56 makes no sense at all, so let's begin at the beginning. What are the two outdoor temps?
  • maybemark
    maybemark Member Posts: 1,131
    now I am on default, before swei I was at I think -14
  • maybemark
    maybemark Member Posts: 1,131
    I misunderstood, and tried to put them at the numbers you mentioned, not subtracting that number
  • maybemark
    maybemark Member Posts: 1,131
    now I am all messed up, my mistake . I'll go and subtract those numbers.
    What should i have the reset curve at?
  • maybemark
    maybemark Member Posts: 1,131
    forgot to tell you, the sensor for outside is the same as the temp showing in the kitchen 31
  • SWEI
    SWEI Member Posts: 7,356
    What is "on default" ?

    We want to work with four numbers here:

    Outdoor 1 Low
    Outdoor 1 High
    Set Point 1 at Low Outdoor Temp
    Set Point 1 at High Outdoor Temp
  • Gordy
    Gordy Member Posts: 9,546
    Set point you were default 180 drop that.
  • maybemark
    maybemark Member Posts: 1,131
    Kurt, with the numbers i thought you want me to go too, it won't let me go that low
    when i got downstairs, it has hit the set point, and the boiler was off
  • Gordy
    Gordy Member Posts: 9,546
    Set point outdoor air parameter.
  • maybemark
    maybemark Member Posts: 1,131
    Gordy, I feel we were close on what you were telling me to do.
    Kurt, I appreciate you helping, but I am misunderstanding what you want me to do
  • Gordy
    Gordy Member Posts: 9,546
    We are saying the same.
  • maybemark
    maybemark Member Posts: 1,131
    well, I am mixed up, because when i turn the knobs, they will not go to what he is asking for, unless I am turning the wrong knobs
    which is a good possiblity
  • maybemark
    maybemark Member Posts: 1,131
    kurt
    can you give me a list of numbers for
    the 4 main items on the menu
    hi
    low
    set pt h
    set pt low
  • SWEI
    SWEI Member Posts: 7,356
    Set the shift to zero and try these:

    0 Outdoor 1 Low
    64 Outdoor 1 High
    150 Set Point 1 at Low Outdoor Temp
    88 Set Point 1 at High Outdoor Temp
  • maybemark
    maybemark Member Posts: 1,131
    thanks Kurt
  • maybemark
    maybemark Member Posts: 1,131
    Kurt
    I changed everything you told me to do
    Thanks for the starting place
  • maybemark
    maybemark Member Posts: 1,131
    I guess I just wait now, nothing to do?
  • Tinman
    Tinman Member Posts: 2,808
    Watch the Bears?
    Steve Minnich
    SWEICanucker
  • SWEI
    SWEI Member Posts: 7,356
    Unless the place is truly unbearable, just take notes for now.

    We want to see what happens to the indoor temp when the outdoor temp rises or falls. The OAT will need to rise or fall at least 5-6 degrees before we can draw any conclusions. Once the OAT changes, watch the indoor temp for an hour or so afterwards.

    You're dealing with something over 1,000 pounds of water here plus probably 2x that in steel. It does not change speed quickly, which is a very good thing -- but you do have to know how to drive it.
  • maybemark
    maybemark Member Posts: 1,131
    ok kurt
    My tenant complained that it is too hot upstairs, he opened the window,
    It is much too warm for me on the 1st floor
    The temp evened out a little
    my bedroom, where I have the stat is 73
    the kitchen is 73
    the living room is 68 (always been colder in there.
    I am just wearing a tee shirt, and I'm sweating
  • SWEI
    SWEI Member Posts: 7,356
    It's only been 30 minutes since you changed those settings. Open windows if you need to, but let it run for at least an hour.
  • Gordy
    Gordy Member Posts: 9,546
    Watch the supply temps on the boiler. The new target in () will be lower and so should the actual. The lower you get it the more the boiler will like it for efficiency.

    If you remember your old target was 128 on the call for heat.
  • maybemark
    maybemark Member Posts: 1,131
    system 115/120
    flame 100%
    outside 27
    inside 32
    it's been over an hour and 1/2
  • maybemark
    maybemark Member Posts: 1,131
    sensor says 30
    kitchen thermometer says 26
    I don't know which one is right
  • maybemark
    maybemark Member Posts: 1,131
    system
    120/120
    flame 93
    outside 30
    inside 73
  • maybemark
    maybemark Member Posts: 1,131
    system 121/121
    flame 74%
    outside 30 (I think that sensor is bad) 25 kitchen thermometer outside
    inside 73
  • Gordy
    Gordy Member Posts: 9,546
    It happens. You need a good quality thermometer to check it against the ohm reading.
  • maybemark
    maybemark Member Posts: 1,131
    I know that the sensor is bad, now what, should i buy another one?
  • maybemark
    maybemark Member Posts: 1,131
    any suggestions on what i should do now? It is still too hot.
    with a bad sensor, I imagine I won't be able to get this boiler fine tuned