Comments
-
what flame % is optimal
32 for chicago is not cold yet
it will be -10 sometime in Feb0 -
i know there is alot of water and metal in my system, I thought that is a good thing for these boilers to work efficiently0
-
Yes, definitely. If the rooms are that far out of balance, assuming all the valves were open, you'll have to pick the coldest room and dial the others back to match it.
I don't recall -- did you install an ECM circulator?0 -
ecm? I did not change the circs
the boiler must have timed out, when i got downstairs
115 (117)
flame 89%
it rose quite fast to
118 {117}
flame 820 -
118 {117)
flame 76%
outside 32
inside 720 -
You will need to make coffee.0
-
gordy
on a chicago 32 f what would you think i should have the flame % at for
what does that mean, make coffee?0 -
Do you understand why the boiler was not modulating?0
-
my outside reset was not right, I think0
-
Dunkin donuts.0
-
So you can baby sit the boiler tonight.0
-
now it went to 118 {118}
79%0 -
Room temp?0
-
I did not touch anything, and the setpoint went up 1 degree
room temp where stat is is 710 -
good0
-
should I leave everything alone?
is 79% flame an efficient flame?0 -
still the same as before
118/118
79 flame
32
710 -
should i turn the reset lower?
it was at 9, I turned it down to -10 -
Watch the room temp if it starts to climb, or drop shift accordingly.
Start balancing rads like Kurt said.0 -
is 79% good? for the flame?
I would think not, we will have much colder days than today0 -
Stop it with the flame. Your system is cold it needs to equalize.0
-
This is a process that takes time.0
-
it's just a question
the room that is the warmest is the fish room, but i do not want to change it. I have the stat in my bedroom, and I did have the valve turned down at 1st, but when we were looking for numbers, I turned the valve open
the lliving room went up to 68, I'm happy with that and the kitchen is 69 now, I am happy with this
I will cut down the bedroom, and i imagine the other rooms will improve0 -
Now your cooking. Once your system is balanced, and everything is warmed up the boiler will start to modulate down.0
-
Dave must be showering tenant upstairs)
system 147
flame 100%
tank 129 {136}
outside 32
inside 71
the pumps are off for heat, and tank pump is on
0 -
I turned down the valve in the bedroom the room with the stat0
-
Flame % means nothing here -- it's all about water temps and air temps.0
-
when i 1st went downstairs
flame was 20%
system 140
DHW was satisfied
the short time i was in the basement watching
system went down to 112 then slowly it went up with flame going up
I left
flame 100% 117/117
outside 32
inside 710 -
system 118/118
flame 99%
outside 32
inside 71
upstairs is good upstairs, but he says he feels the temp rising0 -
All of those measurements have an OAT of 32°F. You need to see what happens when the outdoor temp rises or falls.0
-
what is oat?
and i know chicago the temp will be alot colder than it is now0 -
OAT = Outdoor Air Temperature.
Again, the only things that matter here are the indoor air temp and the outdoor air temp.
Got any thermometers lying around? Tracking temps in several rooms can help a lot with balancing.0 -
119/118
flame 92%
outside 32
inside 710 -
I do have 1 other thermometer0
-
and I have a thermometer on the wall in the kitchen
the other thermostat is in the living room not hooked up, but with a battery in it
The only room that is the hot room is the fish room, but, that's ok, spend less electricity heating the tanks
and my bedroom, where the live thermostat is0 -
bedroom is 71
living room is 68
kitchen is 69 and rising
I am measuring fish room now0 -
I just had surgery 1 1/2 weeks ago on my knee, this is good therapy going up and down the stairs, but it is starting to hurt0
-
I tore my meniscus
118/118
flame 79%
outside 32
inside 710 -
I changed outdoor reset from -1 to -4
system 117/117
flame 65%
outside 31
inside 710 -
Your not using the remote function linked to your smart phone to change, and view the parameters?0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements