Re: Combining baseboard and in-floor temperature issue
Sometimes it is easier to see how the water flow will work when you add some temperature numbers to the water and some pressure numbers to the water. Here are some Temperature numbers in the attached diagrams. There is a problem with @Mad Dog_2 diagram, (not just upside down). When you get to the inlet of the cold water to the mixing valve... the water temperature may be as high as 160° if the baseboard is ramped all the way up to the maximum temperature during a design temperature day. The reset curve may yield 180° supply to the baseboard with a 20°ish ∆T at the return. Since the mix cold inlet is attached to the baseboard return, the lowest temperature the mix valve could provide has to be no lower than the 160° inlet to the C on the valve.
I have modified @Mad Dog_2 's diagram in the second file. This will take the C on the mixing valve from the return of the low temp loops. That will let the Mix on the mixing valve have temperatures closer to the desired temperature because the C inlet will be drawing from the coldest water in the entire system.
In the second diagram, the low temp pump can run with the internal boiler pump without using the system (Baseboard) pump. Also the system pump can run without the low temperature pump if only a baseboard zone is calling. I believe this will eliminate the concern that @hot_rod mentioned "pumps in series".
I was trying to make the least amount of change to the existing design in order to make the contractor more likely to agree to the repiping. There is no way around placing a circulator within the MIX to radiant tubing to C on the Mixing valve and boiler return. There will be no pressure difference to force the water thru the radiant loops after you repipe the C on the mixing valve to the proper location.
Your plumber should get familiar with this Plumbing and Mechanical article https://www.pmmag.com/articles/88035-the-do-s-and-don-ts-of-three-way-thermostatic-valves-br-john-siegenthaler-pe/. This is the trade journal for his trade!

See how the pump location is between the Mix port of the mixing valve and the tubing manifold. This is how the professional should do the job.
In the next paragraph (diagram 2) it specifically states that the piping design your plumber used is NOT the "Best Practice" for radiant floor piping design
By adding a high temperature system to the mix, the cold inlet will not have access to any lower temperature water in order to "Mix Down" the floor temperature.
I have modified @Mad Dog_2 's diagram in the second file. This will take the C on the mixing valve from the return of the low temp loops. That will let the Mix on the mixing valve have temperatures closer to the desired temperature because the C inlet will be drawing from the coldest water in the entire system.
In the second diagram, the low temp pump can run with the internal boiler pump without using the system (Baseboard) pump. Also the system pump can run without the low temperature pump if only a baseboard zone is calling. I believe this will eliminate the concern that @hot_rod mentioned "pumps in series".
I was trying to make the least amount of change to the existing design in order to make the contractor more likely to agree to the repiping. There is no way around placing a circulator within the MIX to radiant tubing to C on the Mixing valve and boiler return. There will be no pressure difference to force the water thru the radiant loops after you repipe the C on the mixing valve to the proper location.
Your plumber should get familiar with this Plumbing and Mechanical article https://www.pmmag.com/articles/88035-the-do-s-and-don-ts-of-three-way-thermostatic-valves-br-john-siegenthaler-pe/. This is the trade journal for his trade!

See how the pump location is between the Mix port of the mixing valve and the tubing manifold. This is how the professional should do the job.
In the next paragraph (diagram 2) it specifically states that the piping design your plumber used is NOT the "Best Practice" for radiant floor piping design

Re: Young People - The Smart Phone Generation
My niece tells me I'm from Generation K - for "kranky". I tell her at my age I've got plenty to be cranky about.
Bob
Bob

5
Re: InSinkErator Garbage Disposal
Same here but I didn’t immediately figure out the disposal could be adjusted. Wasted a few minutes resetting to improve alignment.ethicalpaul said:The video on their site shows you locking the disposal ring, then you can twist the disposal in either direction to align it. The disposal still spins in the gasket after the ring is locked.Yeah, coincidentally I just installed one a couple weeks ago and that was my experience


2
Re: Rat 🐀 stories........
I wouldnt have fired anyone willing to go against that beast in my basement.

1
Re: Pro opinion on near boiler piping on a new steam boiler.
It looks like overall a good job but they should have got an oil tech to help them set up the burner and get the vent right. I don't fault them for not knowing, i do fault them for not getting help.
They should have quoted replacing the venting as part of the job too, new vents are cheap insurance against have some getting stuck open and ruining the new boiler.
They should have quoted replacing the venting as part of the job too, new vents are cheap insurance against have some getting stuck open and ruining the new boiler.

2
Re: Combining baseboard and in-floor temperature issue
Cockamamie sounds Old English to me...everything sounds more important with a British twist! Even idiot ! And Bonehead! Knucklehead! How about nincompoop! Mad Dog 🐕 🤣
Re: Combining baseboard and in-floor temperature issue
Yes..as HR says, you want the Rafiant zone Circulator pulling away (pumping away!) From the Mixed port of the 3 Way Valve. The Taco Circs I use have Flow Checks in them. IFC (integral Flow Check), so You don't need a Swing check if that's what you mean..Its maybe 4-6 hours work to fix it. If the guy insists on his Cockamamie piping, move on. Mad Dog 🐕I did testify as an expert witness in 2 court cases in my career. I believe that Cockamamie is a technical term @Mad Dog_2. This can become overwhelming for some persons like Judges and Lawyers that are not in the trades. You may want to use more generic terms for those that may not be well versed on the trade slang. I might suggest "Bone Head" or "Idiot"
Re: The Case of the Unopening Gas Valve, this weeks case
I should have remembered the plugged vent scenario after an ice storm covered a NG regulator vent over solid with ice one miserable night.
I did consider the USMC method of cooling the 30 caliber machine gun barrels to unthaw the ice.
I did consider the USMC method of cooling the 30 caliber machine gun barrels to unthaw the ice.


2