Re: Pressuretrol issue
Don't shoot the messenger. If the pigtail is clean and the pressure gauge is moving up -- it's not the fault of either the pressure gauge, the pigtail, or the pressuretrol.
What is that monster feeding, and how big is it? The only way the pressure can rise is if the boiler is making steam faster than whatever it is feeding can use it, so we need to look at that.
What is that monster feeding, and how big is it? The only way the pressure can rise is if the boiler is making steam faster than whatever it is feeding can use it, so we need to look at that.
Re: An Important Skill for Teaching Tradespeople
Thanks, but the fork is firmly in place. 😅
Re: Is there a two pipe steam doctor in the house?
OK it was plugged 
Sorry, I didn't see the part where you said the plugged part wasn't in the photos. You wouldn't believe how many times people mis-read things in this world! I'm glad you got it all fixed up!
Sorry, I didn't see the part where you said the plugged part wasn't in the photos. You wouldn't believe how many times people mis-read things in this world! I'm glad you got it all fixed up!
Re: Dan Holohan Retires After 36 Years of Writing Magazine Columns
Thank you Dan for your wonderful writings. I never had a grandfather (I'm 74). But, when I read your stories, I feel like my grandfather is talking to me. Godspeed Dan. Aw
1
Re: Oil boiler and outdoor Wood Boiler
Typically speaking, that exchanger just gets cut into the existing return line prior to re-entering the indoor boiler with no need for closely spaced tees. The circulator on the OWB runs 24/7 so that exchanger is always hot, and when any indoor zone is running, it will essentially preheat the return water entering the oil boiler via the aforementioned heat exchanger.------------------------------------------------------------------------------------------
Is this garage attached or detached? If the former, maybe add it as a zone to your oil boiler so you also have backup? Otherwise just make a series or parallel loop out of it and hit all 3 exchangers at all times. If the latter, you'll want to run a separate loop from the OWB to that building also with its own circulator located on the OWB and just circulate 24/7 while controlling the fans with a thermostat. As for controlling the oil boiler, I would add an aquastat or Ranco type controller on the incoming OWB supply line at the heat exchanger and interrupt your oil boiler's TT signal with it, so that any time the OWB is above say 150*, the oil boiler will not fire. Whenever the OWB temp drops, the oil boiler will fire to make up the difference. If the OWB is something you don't intend to keep hot all the time during heating season, you may wish to have some sort of thermostatic bypass to prevent keeping the water jacket at oil boiler temp due to the 24/7 circulation of the OWB circ.
Regarding leonz, please disregard everything he/she said. It's 100% false.
This is the first time I have made a comment like this and hopefully the last.
You can be as insulting as you want to me but not even you can change the
laws of physics, thermal mass and how forest eaters work and don't work.
Leonz
1
Re: Minnesota Right to Repair Law
We have several Deere Gators at work. My team of mechanics are so skilled, some of them wont think twice about buying a brand new truck, lift it, change gear ratios or hacking into the computer to boost performance. But when we went to Deere for a replacement parking brake, they said we have to haul the gator to them to be evaluated by one of their techs and repaired....
I bought a pair of chocks for it.
I bought a pair of chocks for it.
1
Re: Why must The 12 psi fill pressure be increased for 3 floor house?
And all of this is totally due to corporate America's peddling of pumps, pressure relief valves, pressure regulating valves, zone valves, etc.,etc. Give me an open system, convection flow, hand fed with the 'expansion/fill tank' in a closet on the top floor just slightly higher than the top floor radiators . Not to mention the altitude reading on the tri-dicator . What's that for again ?🤔🤔🤔?