Re: The Hidden Hydronic Problem Nobody Checks: Water Velocity
We had what was thought to be a small case of velocity erosion on a new commercial building. Upon removing the leaking piping, it was discovered that the leak was caused by visible pipe wall erosion. Much like a riverbank looks after a heavy rain. Obvious erosion.
Over a span of a few years, small erosion issues would arise from time to time.
What we did to correct this was to add Variable Frequency Drives (VFD) to the heating systems' circulators, as well as microbubble air separators. This was done some thirty-plus years ago, and the results are still proving successful to this day.
I haven't seen much on velocity issues, but they certainly need to be considered. They are not always obvious and can cause a lot of headaches.
@RayWohlfarth Thanks for this video. It is a very helpful subject.
Intplm.
Re: Dryer vent duct
Get a level II inspection of the chimney first. Look at all the spalling near the top. A lot of freeze-thaw damage on that cold exterior chimney. Reline it with a properly sized smooth wall 316Ti or 316L ss liner. Sweep the liner into the Combustion Appliance Zone and cement in place. Once in the room, split it to the DHW and boiler, which btw appears to be running downhill. If you sweep it into the room, as allowed under the IRC Ch24, you don't need a clean out for gas.
According to Ch15 of the IRC, the max length of a Flexible Transition Duct or 'Slinky' is 8 ft. it can only attach to the appliance and not start further along. It must be stretched until the inner lining is smooth to maintain the minimum cross-sectional area. No male down fittings such as that band clamp on the elbow. Any Slinky must be listed to UL 2158A. It is not approved for direct contact with those hot vent connectors.
You need to rework those vent connectors, min. 3 screws per joint equidistantly spaced, no seams from 5-7 O'clock pitched up towards the chimney 1/4" per LF. The larger connector must be heavier gauge pipe. I'd replace that crummy ground key gas cock on the WH.
Ask Hector the Inspector how he wants it terminated: as-is or extended with hard duct out from the building 3 feet supported.
I would skip all the flimsy material and just run a continuous 4" smooth wall 316ss chimney liner as your one-piece exhaust duct. It exceeds the code. Use a ss wall termination extended out from the bldg. 3 ft. with a strong steel hanger off that post and angled away from the wood.
Re: Roof vent cap
Yes, that is a gas furnace vent cap. it is designed to keep rain from falling into the exhaust vent of a gas fired heating system of sorts.
This is not the first time something that was intended for one thing was used for another. I can give you an example of other devices used for things that they were not intended for. My biggest regret is when computers stopped including cup holders.
Re: Help Identifying Bathroom Faucet
Use AI. Supply houses are using AI and gotten it right. its just another option. Might work, might not. I have hotel maintenance doing it.
Re: Radiators Are In Stock
A friend of mine who grew up in philly told me they call it gravy out there when they put meat in the sauce. So i am blaming them for the confusion. Philly fans are always a pain in the ****.
Re: Taco needs to create an animation of how the 570 series zone valve works.
@hot_rod This is fantastic. I'm thinking I may Dremel all my 570 casings open from now on so I can watch them work.
(Does that seem excessive?)
JohnNY
Re: Taco needs to create an animation of how the 570 series zone valve works.
I spoke to Wales Darby today. What I had trouble wrapping my head around with this actuator is… what really makes it work is that it takes so long to open and close. Terminals 2-3 stay closed while the heat motor pulses voltage to keep the stem in the open position.
It's absolutely an ingenious design, especially for its time I suppose, but testing them depends heavily on understanding the mechanics of their movement. At least for me. Because I'm a plumber? Maybe. Or maybe it's because I spent a lot of time listening to Led Zeppelin on 11 with headphones on as kid.
JohnNY
Re: Taco needs to create an animation of how the 570 series zone valve works.
@Jamie Hall But, looking at the diagram, it is absolutely true that the #2 terminal is receiving power from two 24v sources. Seems like trouble to me. And I don't understand the movement of the "heater switch." It ha also been said that the Heat Motor receives intermittent power and it relies of the slow workings of the valve to make or break the 2-3 closure.
I have to see it work or my head will surely explode.