Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
Best Of
Re: Leaky siteglass
When I had a one pipe steam system and serviced the sight glass I would wait around long enough after a call for heat - the minute or thereabouts after shutdown when that system would drop into vacuum briefly - to make sure there were no such bubbles. Also keep in mind you won't see any bubbles if it's the top grommet leaking under vacuum. So if you have a vacuum leak like this and bubbles, probably a good idea to repeat whatever tightening you need to do on both the bottom and top grommets.
On vacuum systems I sometimes see bubbles rising from the bottom up to the water level. This indicates a slight air leak at the bottom grommet. A bit of tightening on the lower compression nut stops the bubbles.
1
Re: Low Water in Boiler - Wet Steam Likely
Estimated 75' main and dry return. Most of main is 2", last 30 feet reduces to 1 1/4 copper. Pressure gauge needle always rests on the stop.
Re: Toilet wax rings
Alan Not sure what you mean, are you talking 14 inch tall? I’m pretty sure they’re still sold all over the place. I like the 17 inch tall toilets. Whenever I sit down on a 14 inch, I feel like I’m losing my balance and I’m crashing down to the floor, lol
Speaking of which, is Chris installing a 17 inch tall? Highly recommended!
Speaking of which, is Chris installing a 17 inch tall? Highly recommended!
GW
1
Re: Disappearing water from glass gauge; Long shutdowns
I've seen these setups work well
for heating the basement... as long as it's full of water and doesn't leak, it's not a problem.
for heating the basement... as long as it's full of water and doesn't leak, it's not a problem.
Re: Replacement / Sizing of boiler
@Jamie Hall @hot_rod @Hot_water_fan All this talk about Linear and Nonlinear equations is making Maynard G Krebs' head spin. 

This conversation is totally tubular
Re: Pigtail
Will the extra 3-4 inches that the pressuretrol will be sitting higher from it's original position affect its function at all (since it is further away from where it was meant to be originally)?Aside from not needing to bend over as far to read or adjust it, it will have no other effect. As long as the wires will reach, you're in good shape.
Don't forget to add some water to the new pigtail before you mount the pressuretrol. Are you replacing it with a brass one?
Re: 1961 Wards boiler
Imagine if a doctor acted like that.Wow thanks for the quick response. "heat-loss calculation on the house". Not planned on doing that.So, you really dont care if its properly sized?
Ehh, just give him about 4 or 6 of those pills, every 2 to 8 hours........
Hes 72 years old anyway, he'll be checking out within the next day to 20 years.....
Re: 1.414 Math, 45 degree offsets, a quick tutorial




You can fake it with small pipe or PVC. Try holding 4" Victualic fittings or larger and trying to measure it uo yourself.
The indoor chiller I piped by myself on site with no help it was a replacement. 8" chilled water with the 45 deg rolling offset. The condenser water was 4" or5" can't remember. Yeah it took me a while.
The outdoor chiller I went to the job and measured everything once the chiller was set and had all the pipe cut and grooved at the shop. I was not going to lug all the equipment needed to groove that stuff and then have to set it up and lug it back. Probably took me a day to measure it and draw it so the shop could fab it. Then I pulled the pieces up through the roof hatch myself.
Guess that is why I am all busted up and can't work anymore.
Re: Occupation
Years ago while searching on the wall, I found a posting of many years back that had an introduction of each member.I'm sorry.
Each person told their history and location.
Somewhat like this discussion, most stood and delivered......except ChrisJ
ChrisJ
2
Re: Why is 1 zone Supply side cooler than Return
Geez. The more I learn, the more I dislike the previous owner.