Re: Equalizer Return
I'm still staying with it's a drain for the header and a vent for the loop to keep it from siphoning out of the boiler. Without the vent the loop wouldn't matter it would just siphon over the hump.
Not understanding the applying pressure thing. You can't push down into a tee or wye without pushing in both directions. It's gonna push equally outward from the boiler as it is into it.
Re: Equalizer Return
Just my opinion.
When the boiler is not firing there will be more pressure at the bottom of the boiler than above the water line. Atmospheric pressure will be pushing down on the water and the top of the boiler is vented to the atmosphere.
As the boiler builds pressure the pressure on the water at the water level pushes down on the water which will tend to force water out the return. Since the same pressure is pushing down on the water from the header through the equalizer the water level is equalized and the water level in the equalizer should roughly match the sight glass. Without the equalizer water could be pushed into the return.
This may change depending on the system. In a one pipe system with the end of the steam main connected to the return the equalizer may not be needed as @ethicalpaul has shown. In a two-pipe system with no pressure in the returns due to steam traps that could be a different issue as could a large one pipe system in an apartment building with 100s of feet of pipe the pressure at the far end of the steam main may not equalize as well as it would at the boiler.
Weather you need an equalizer to drain the header is another issue. Properly piped boilers with low velocity in the boiler risers may not require an equalizer for a header drain.
This site abounds with picture on various posts of boiler with crappy piping that work fine without an equalizer or an improperly piped equalizer.
But if you install a boiler how do you know if it will work or not?
Most would install the equalizer because the MFG recommends it even if it is not "needed". It would cost a lot more to go back and install it if the job does not work than the cost of a few fittings and some pipe and some labor.
Re: Recessed radiator grills
What do you mean by grills? What is wrong with them as is? Is this for child protection?
Re: Correcting my 2 Zone Monoloop System (Need Help)
thank you all again. I'll get some time this week and weekend to mess with it again and report back if I was able to solve my issue. @EdTheHeaterMan , @mattmia2 , @offdutytech
Re: LWCO Blowdown....Under a Little Pressure?
For me, the main thing is to make sure the burner automatically shuts down while you're dumping the LWCO.
If it doesn't, the LWCO doesn't work and that's bad.
Re: LWCO Blowdown....Under a Little Pressure?
Whatever works. I see no particular problem with either of your methods. Main thing is to get that blowdown valve fully open. My own preference is to not just open it, but to open it, let it swoosh, close it, let the LWCO refill, open again, rinse and repeat until the swoosh is clean — then top off and go. Usually two or three swooshes will do… but as I say, whatever works.
Re: LWCO Blowdown....Under a Little Pressure?
It looks like they recommend flushing it during boiler operation:
http://s3.supplyhouse.com/manuals/1350816480646/83711_PROD_FILE.pdf
Re: Delta Bath Faucet O-Ring sizes for RP25513 stem
I gave up some time ago and bought a kit with a whole bunch of different size o-rings. Very handy…
Re: Correcting my 2 Zone Monoloop System (Need Help)
I have never used a balancer on any small residential system. I find that with a circulator zone system, it is self balancing via the thermostat. if a zone is cold, that thermostat will stay on while the other zone thermostat is satisfied. If you are trying to balance individual radiators on a particular one pipe main, that is usually done with a damper in the radiator cabinet. If you are trying to get the two radiator branch to balance with the other radiators, try doing the individual radiator thing. and when using PEX for those branch runs, try using the next size larger PEX. Use 3/4" for the 1/2" pipes, and use 1" to replace 3/4" pipes.