Re: New Daikin - AC Mini Split
I've heard of leaks that are pressure (vacuum) dependent.
How confidant are you in your manifold, hoses, core extractor, etc.? I'm pretty sure my SMAN460 leaks internally, & I generally have to replace my Appion core tools every year or so.
Did you do a triple evac?
Re: Near boiler piping/replacement boiler
A heat load would add some more info to the question. 1800 sq ft X 25 btu/ ft guesstimate= 45,000BTU/hr required. That is on the coldest day.
80% of the heating season the load could be in the 30,000 range. So the boiler 152,000 you have could be 3-4 maybe 5 times what you need.
While` not hydronically ideal for that boiler, the circs are not causing efficiency issues on the return, unless the system has noisy air issues?
Here is a simple buffer piping, direct to load method. Indirect on priority with its own circ.
hot_rod
Re: Lochinvar burner cleaning
I've seen some rough ones but not as bad as hot rod's picture. I always do a combustion analysis after cleaning. There may not have one done in that pic, ever. The max that I recommend is 3 years between cleanings.
I always remove the back refractory and I use a Dremel tool with a stainless steel wire brush to clean the coils and a feeler gauge between the coils (there is a tool for this). I use CLR or Rydlyme to help break down the deposits. I'm going to try Axiom's product (thanks, hot rod). It takes me about 3 hours to do a though cleaning. This is what it looks like when I'm finished. This was a rough one which took almost 4 hrs.
Re: Near boiler piping/replacement boiler
The piping size is adequate for the load you have connected. 100' of fin tube could supply about 55,000 BTU/hr. Seems like plenty for 1800 square feet? No sense in having a boiler sized larger that the fin tube can put into the space. So a 60- 75,000 BTU/hr boiler would be adequate.
If your current boiler is twice that size, 120,000 or larger it probably short cycles and runs 70% efficiency range.
hot_rod
Re: Near boiler piping/replacement boiler
Three zones with 50'/zone = 150' x ~500 BTU/ft. @ 180° = 75,000 BTU. One inch pipe is fine for that load.
If you really want to do something, pipe it primary-secondary to keep the large boiler happy.
Re: Near boiler piping/replacement boiler
or a buffer tank. a buffer tank is probably the only thing you could do that might come close to paying for itself
Re: New Daikin - AC Mini Split
There is probably no air, moisture or non condensables. You could be pulling refrig out of the oil. Is the compressor cold like refrig is boiling off?
Re: New Daikin - AC Mini Split
Pulling the dissolved refrigerant outta the oil. It takes a lot longer to pull a vacuum on oil in a system that was operating.
Re: Is there a list of the best help forums for the various 'challenges' we encounter?