Re: Heat loss calc..
Ok, the team has spoken! Thank you everyone for your input!
I'm a long time reader of the forum..
@EdTheHeaterMan , yes the old 1970's Burnham America boiler is cycling on/off in short 3 minute-ish cycles as you describe, while the 20yr old Bell&Gossett pump runs a bit longer at maybe 30 min? Your numbers make sense, thanks.
@hot_rod, I currently have 2000sqft + 95' of finned tube over 2 zones (65' 1st floor, 30' 2nd floor). House is comfortable when the heat is running.
I'm planning on combining both zones into a single 95' split zone to get me into condensing temps with a new mod con combi, and avoid a small second floor zone that may cycle.
The Rinnai mod con Combi I'm considering only comes in 60k or 90k for CH, both with199k DHW, both turn down to 15k for CH.
Favoring the 90k unit as I will be adding 1000sqft (+45' finned tube) +1 bath addition next year (a final total of 3000sqft + 135' finned + 2.5bath).
Re: 25 Years ago.....
I know of no person in any industry or profession that has done more to educate the rank & file, motivate them, and bring them together than Dan Holohan…Very, very fortunate to have rode the wave behind his Surfboard ..mad Dog
Mad Dog_2
Re: 25 Years ago.....
Reminds me of how far back our little group here goes. Life is very good with friends… And friends who share our interests and values are golden. Thank you Dan for bringing us all together a lifetime ago.
Re: Literature on Geothermal
Here is an out and back system in upstate NY, 35K load. 4 loops of 1" HDPE, 1000' loops. It's been covering the load for a few winters now.
hot_rod
Re: NJ Boiler replacement decision points...
Then get a heating only boiler and keep your standalone water heater. It's a valid concern.
Re: Near boiler piping/replacement boiler
Run to failure..unless you have extra disposal income....Mad Dog
Re: Near boiler piping/replacement boiler
If it's not broke don't fix it.
Get quotes on new boilers (you will be shocked). Then start saving. Do an accurate heat loss and get the right size equipment and the right contractor.
Consider an Energy Kinetics boiler.