Best Of
Re: Boiler Zone 2 won't ignite boiler
Hello Dean60068,
So when the system had the RA832As the behavior was exactly the same as it is now with the Taco SR502 switching relay ?
Can you take off the cover of the SR502 and take a picture of everything inside ?
What thermostats do you have ?
The zone 2 LED does come on with a zone 2 call ? I don't see it on in the picture.
Red arrows, Priority off and jumper installed ?
Re: Boiler Zone 2 won't ignite boiler
" Yes, it is acting the same way it did when I had the RA832As . "
This makes it very puzzling that so much was replaced and yet a strange problem persists. By the symptoms it seems like it was a relay issue or now a SR502 issue. With the Isolated End switch controlling the boiler the boiler should not be sensitive to which zone is calling.
I guess if I were there I would verify all the power supply voltages when it acts up, 120 VAC and the 24 VAC in the SR502 and the boiler.
I also would verify the voltage across the thermostat zone terminals, that they (both zones) go close to zero volts and the voltage across the Isolated End switch terminals also goes to zero with either zone calling.
When either or both zones calling the Isolated End switch terminals should have 0 voltage across them, and 24 VAC with no call. The voltage across the non active Isolated End switch terminals comes from the boiler (or an aquastat).
I would also use jumper wires as a test instead of the thermostats.
With zone 1 off and zone 2 calling (if the boiler does not start) I would jumper the Isolated End switch terminals and see if the boiler starts.
Re: (Updated with pictures.) Likely gas leak after installing new thermocouple?
according to the first photo attached at the beginning of the thread. There looks like plenty of slack on the tubing to reshape it under the pilot assembly to soften that bend. Here’s a nice video clip I found that shows what many are explaining about the loose nut under the pilot light. If you’re not comfortable maybe a neighbor can help with the video assist.

Re: Underperforming system in cold temps
Just looking at the control module, multiple knobs, this boiler probably has ODR outdoor reset function. Is that being used, a sensor mounted outside on a north wall, for example? That would explain the varying SWT temperature
That control display screen or info screen should tell you boiler supply, boiler return, and maybe boiler target, the temperature it is trying to get to? The operation manual would tell you how to access that info. Those would be the most accurate measurements as they are usually probes into the fluid stream, not strap on.
In my mind if the 3 way valve has 110 or whatever in the H port, the mix port, or AB port should be able to see 110. There should be no blending if the valve closes off the cold, or B port?
If the thermostat satisfies before the boiler reaches the setpoint temperature, you may not see the target temperature being reached. The load is satisfied, the boiler should ramp down.
At days end, are you warm and comfortable now and at the coldest days? If so you may not need to screw with it?

Re: Circulator wiring with Taco SR504 switching relay
Just an update. Using the ZR terminal did the job. So much better than before. I believe I will save a lot on wood this way. Again thanks for everyone's support.
Re: Simple Steam Heat Thermostat Recommendations
I too have single pipe steam system and was able to get a mercury Honeywell T87 just before mercury was banned years ago. It has performed flawlessly for a few decades - set it and forget it for the most part. Its possible these thermostats can still be had on Ebay etc.
All the Best,
RTW

Re: Boiler Zone 2 won't ignite boiler
Holy Crap!!!
HVACNUT you have solved the puzzle! I flipped the switch to the damper and now it appears the system is working.
Why did flipping that switch work? It was opening on the first cycle.
Re: Underperforming system in cold temps
Does the supply pipe going into the mixing valve feel like it is 150F?
And is that the supply pipe coming from the top or bottom in that photo with the Taco mixing valve?
I don't see the "supply sensor" going into the taco mixing vavle. Is it just bent over and not visible in photo? where is that sensor on your piping? What is that wire nut connecting?
Looks like someone has been fairly aggressive with a screwdriver on that mixing valve.
Re: Sight glass full, boiler cycles on and off every 30 seconds.
First step is to drain the water to an acceptable level. About halfway full, give or take. I guess would be that it's cycling on pressure, which is building up due to the excessive water levels.