Best Of
Frost free sillcock rated for continuous use
Another day, another thing I learn. About to pull the trigger on a 12" Woodford frost-free (based on reccos on this forum) I see in the specifications list: "Not rated for continuous use."
After a brief internet rabbit hole I understand that this has to do with the anti-siphon system: these are not rated for continuous pressure.
Any suggestions for a good quality sillcock rated for continuous use?
(As you may have guessed I'm adding a timer based irrigation system for our plants and so will keep the bib/sillcock always on in the summer.)
Re: Radiators getting hot when heating circuit off
I think we need a complete diagram of the way that is all plumbed…
In the meantime, if there are no valves I suspect you are seeing gravity flow in the radiators. How to fix the problem, though… depends on how things are actually hooked together.
Re: End of Season Report V4: Thermal Purge-O-Rama!
Wow lots a data to sort through!
On a design day, how long is the boiler run cycle? If the boiler fires before the 7 minute post purge ends, seems the short cycles are still present?
Also if you pull the boiler to room temperature every time, does it warm beyond condensing mode when it fires, for a single zone call for example?
Those are the two concerns with over-sized boilers, short run/ off cycles and the boiler runs too cold, as it covers the load before the return warms adequately.
As I recall one goal was the de-thunking of the zone valves frequently, did that get solved?
hot_rod
Re: End of Season Report V4: Thermal Purge-O-Rama!
I'm hoping to get the gas pressure issue fixed this summer and then add the setbacks back in next season, now that I'm pretty confident the all-zone purge scheme will handle the 'freeze protection' issue pretty well (even with setbacks on 2/3 of the zones). I haven't thought about it carefully, but it's probably possible to do the all-zone thermal post-purge with just some relays. It really works better than one might expect (at least in my house), due to the following:
- There's only about ~10k BTUs stored in the boiler after firing (for my 140KBTU/hr CI boiler)
- Any zones that haven't been active in a while will be filled with cool water, which can mix with and absorb the BTUs very quickly
- The overheating is minimal when the BTUs are distributed evenly throughout the house, and the inactive zones will typically have been a few BTUs below their setpoint anyway
- For the inactive zones, it will mostly just delay them calling for heat again for a bit longer
- It can very quickly cool the boiler down, virtually eliminating standby losses for oversized boilers
Re: End of Season Report V4: Thermal Purge-O-Rama!
Nice work! I would have kept the setback though, since that would eliminate one variable.
Now we need to come up with a multi-zone control that incorporates the post-purge feature. Caleffi, Taco, Argo et al, ya listening?
For hot-water systems with just one zone, the Beckett AquaSmart control has a thermal post-purge feature you can enable. I don't see a way to wire it for a multi-zone setup though.
Re: Specifications for 2-pipe system in large house, 1914
CI was always the first choice for HW or Steam and was never accepted for gas in most locations Now the new steam installs have gone away (mostly) and HW uses copper or pex the demand for CI fittings is pretty low compared to what is used to be.
Never seen CI in HD or Lowes and even the large supply houses like FW Webb their smaller branches usually only have malleable.
Re: Main vents on Steam system
Steam will continue to favor the path of least resistance…
Re: Outdoor Reset?
Here is a simple outdoor reset, it is the valve and the controller all in one. all that is needed extra is a 24volt transformer to power it up
and here is the instruction guide
Dave H_2
Re: 1966 heating oil tank
I went through pinhole leak tank failure in our house, and witnessed a few similar failures for friends and relatives. A few useful things I learned:
- If you have a decades old tank, it is not a matter of if, but when.
1) Tank leak patches:
Leaks are most often pinhole leaks. These can be (short term) mitigated by applying a magnetic patch (e.g. Rectorseal Magne-patch ) to the hole. So it maybe a good idea to have one or a few of these patches on hand, esp if your tank is old, so there is no delay slapping one or a few on, if a leak happens. Will not help with a massive leak, but will with a typical dripping pinhole. I see no downside to having them available. If you don't have them available, you have to wait until a tech can come out, who will slap one on, or until you can have such patch(es) shipped to you. BTW A poor man's magnetic patch is a strong neodymium magnetic disk, combined with a layer of bycicle tire rubber patch layer between it and the hole. My mother-in-law's tank sprung 5 pinpoint holes, and we used the improvised style patch on 3 of these, worked as good as the magne-patch. This tied us over until we could line up a tank replacement. I attached a pic of the purpose made magne-patch (expensive) and a neodymium magnet (cheap).
2) Sludge and leftover oil:
We are in southern MA, and here, it is pretty common for a tank installer, often an oil vendor or burner service company, to pump out the leftover oil into a tanker truck of temporary storage tank, and then pump it back into the new tank. The pump line has a filter but it may not be able to get rid of all the existing biologicals (mold, fungus and bacteria) in the old oil. It is easy to say "get rid of the old oil" or "time the replacement when your tank is empty" , but not everybody has the luxury of time and money to do this. When my tank went, it still had 250 gallons of oil, and I was not about just to chuck ~1K in oil. When they pumped the oil out, they used an overhead hose, and managed to leave the sediment at the bottom of the old tank. The usual installer (all of them we have dealt with) was able to dispose of the sediment for a small fee, along with the old tank. So we just added a biocide and a water dispenser additive when we filled the new tank(s).
3) Additives:
Oil additives you can readily buy are either water dispersants, or biocides. It is hard to find one that does both. I am skeptical about any additive that claims to get rid of sludge, (a "maybe"). Getting rid of ( dispersing) the accumulated water works well, and prevents the biologicals from breeding in the tank, which would lead to sludge formation. So IMO that is a good preventative measure.




![PXL_20250730_161408499[1].jpg](https://us.v-cdn.net/5021738/uploads/TWCHBQTTLRHH/pxl-20250730-161408499-5b1-5d.jpg)