Re: Just wondering
Yes October/November. They knew they had a problem and hoped it would magicly heal over the summer
Re: Replacing 30 year old Vesta oil boiler….
I like the fact that you have a good contractor that has already completed work for you in the past and you were satisfied enough to call them back again. I might call and ask them if they are an Energy Kinetics dealer. Although Burnham makes a good product, the American Made EK products use some energy saving technology that has proven to lower operating costs. The EK boilers can also provide domestic hot water at a lower cost than a propane or electric water heater.
Re: Lochinvar WBN080 lockout
Here is a resistance chart from the manual of the other model in the other thread I posted. Keep in mind this is for thermistor type sensors. Self resetting Snap type thermal switches are usually open (infinite resistance) or closed (low resistance). I believe 1/2 of the ARHL (Auto Reset Hi-Limit) is NOT a thermistor and actually is a Snap type thermal switch. Having thousands of Ohms resistance in series with the 24 VAC current path to the Gas Valve makes no sense.
Re: Lochinvar WBN080 lockout
I believe the dual sensor is (1/2) sensor is a thermistor (S1 on the diagram), so variable high resistance that changes with temperature, usually NTC (Negative Temperature coefficient), temp goes up the resistance goes down. The other (1/2) sensor is a (needs to be) thermal snap switch type (Auto Reset Hi-Limit, Orange / Gray wires) which when closed at room and normal boiler operating temperatures has a very low resistance, like less than 1 Ohm to support the load current of the Gas valve. At least that is what the wiring diagrams are telling me. You should have the original documentation, are they significantly different than my postings ?
You may have the wrong sensor. Or your new sensor is defective. If you prefer chase out the 24 VAC that powers the Gas Valve and see where it stops.
Additionally the flame proving time should be long enough for a digital meter to settle if normal voltage is actually present. So an analog meter or and indicating load (such as lamp(s) that I like) should not be needed in this case.
If you replace the Gas Valve you probably need to do a combustion analysis. A combustion analysis may not be a bad idea for a tuneup when you get it running.
Caleffi Zone Valves
I like the new o-ring seals vs. fiber washers.
Re: What's a good humidity meter?
it is a very old school hygromteter, i think it was in my elementary school science books that were published in like 1970 and i think one of the middle school science rooms had one. i'm guessing they've been around since the 20's or 30's. that tube in the middle fills with water and keeps the wick wet.
Re: Sad day at work - wall mount toilet tank hole
I don't think there is an issue with a toilet tank in the wall as Any water line in the wall can eventually cause you problems to rip out wall going how many floors down... I have seen damage 4 floors down from a screw in pipe behind the kitchen started leaking 3 years after house was built
Here in Brooklyn every inch counts and it counts a lot🤑
9326yssh
Re: Firetube vs Watertube Boilers Explained: Which One Is Better for Steam Heating?
I am a boiler operator. Fire‑tube boilers are more suitable for low‑pressure (<1.8 MPa) applications in the 2–30 t/h range, while water‑tube boilers are typically used for high‑pressure, high‑temperature industrial processes. Neither type is inherently “better”—you select the boiler that best fits your specific process requirements.
If you have any questions, you can read the blog I wrote on my personal website:
Re: Is my heat exchanger hosed?
A couple of tests. Start the furnace with the blower off and the stat set to auto. Watch the flame closely and see if it changes when the fan starts. If it does the hx is toast.
The other way is to cover the flue outlet outside with plastic wrap or plastic bag secured with a rubber band. Have someone start and stop the fan while you watch the plastic bag for movement
Re: Caleffi Zone Valves
i hate those fiber gaskets, i especially hated them when i had to cut one out of sheet gasket because i had to break the union and couldn't get the old one to seal and I didn't have a spare.