Best Of
Re: Venting into a chimney
I couldn't find that model number so I could reference the listed instructions. However, if this is a condensing boiler, which I believe it is, then the venting must be listed to UL 1738 for positive vent pressure. That would probably mean a polypropylene plastic liner. Masonry chimneys are not approved for positive vent pressure. Most stainless liners are Not listed to 1738 for positive pressure or condensing.
Re: Venting into a chimney
To be clear on your query, I can not find any specifications on a Viessmann model BK200E anywhere in the old or new equipment catalogs i have access to. I do know that many of the Viessman gas and LP boilers are condensing boilers and do not fall into the Category I venting design that allows for chimney venting.
here are the venting categories:
Category I is characterized by negative pressure and non-condensing appliances. These systems rely on gravity to vent flue gases, and if there is a leak, air from the space will flow into the flue pipe rather than flue gas leaking out. Category I venting systems can use single wall, double wall, B-vent flue pipe, or even a chimney.
Category II is also under negative pressure but may produce excessive condensate. These appliances are typically condensing and have a combustion efficiency greater than 83 percent under ANSI test conditions. However, Category II products are no longer manufactured.
Category III operates with positive pressure and non-condensing appliances. If there is a leak in the venting system, flue gas will flow from the flue pipe into the space, which poses a safety hazard. Therefore, Category III vent pipes must meet additional safety requirements, such as being gas-tight with gas tight venting systems.
Category IV is positive pressure and condensing, typically used for high-efficiency appliances with an annual fuel utilization efficiency (AFUE) of 90 percent or higher. These systems require sealed joints and are often made of materials like PVC or CPVC.
I believe the Viessman boiler you have would fit into Category IV, but I can not be absolutely sure since the model number you posted is either incorrect or is from a time before internet records are available. Absent more information my vote would be the vent according to the manufacturers venting instructions.
EDIT: it appears that Viessmann does make a steam boiler for commercial use. I do not have information on older models, so it is possible that if @heron98105's old Weil McLain is a commercial boiler in the 20 HP range and above,
Then there may be a Viessmann steamer to replace it. I don't have access to older model numbers but the newer boilers may be one of these:
And this Viessmann may be able to be vented into a chimney after you follow @Jamie Hall's suggestion about inspection. The consensus is still "Follow the manufacturer's venting instructions."
Re: Venting into a chimney
Then the chimney vent is NO
You can use an abandoned chimney as a chase for the recommended vent material. but you can never use that chimney to vent a Cat. I vented appliance as long as the Cat. IV vent pipe is inside that chimney
EDIT:
In this instruction manual for venting Viessmann boilers, on page 83 there are instructions for using a chimney to vent a Cat. IV appliance. Viessmann venting instructions. I hope this answers your question.
Re: Venting into a chimney
Absolutely not...that is a 95% Condensing boiler (very low flue temperature). You can ONLY use the old chimney as a pipe chase, as the other guys stated. I'm using the exact same Viessman model on a project right now, but using PP (polypropylene) venting directly outside through basement wall. Mad Dog
Re: New steam boiler - newbie help
https://www.ideals.illinois.edu/handle/2142/4349
One can make their own conclusions from the study posted here years ago but it was arguing that in the case of steam that pick up plus pipe losses significantly greater than 30% were of no benefit but when significantly lower (10%), at least for the configurations and methodologies used in the study, 6deg F recovery time at design temps could be increased.
Re: Where to buy Calefactio Pump Flange 3/4" NPT in the States
The last ones I purchased (2019) from Hajoca, Salt Lake City
jpp@calefactio.com Jean-Philippe Pichette at Calefactio
(450) 951-0818 Quebec Office
(801) 972-0659 G & S Sales (Utah rep.)
(855) 982-1408 Hajoca, Salt Lake City (speak to Vern)
Re: Possible to wire furnace fan to thermostat controlling a boiler?
After reviewing the Regal furnace (i don't know your model number but this is the standard oil furnace control) and the Navien combi (i don't know your model number but this is the standard typical Navien control) and the Ecobee thermostat (i don't know your model number but this is the standard wiring for many of the Ecobee thermostats.). this is what I have come up with.
There is no need to purchase or add a relay. The Boyertown will need to be powered the entire time you want the thermostat to operate, because the Boyertown Regal is the 24 VAC source for the Ecobee.
If these wiring connections do not look familiar, then I will need the model number of the unfamiliar item, or a picture of the control board on the equipment or thermostat.
Re: Replacing 17 year old oil fired boiler/need help
All great advice, thank you everyone. I would like to remind you of the ascent plus side wall vented oil gas or lp fired combi boiler we offer. Its low mass (3 gallons) and can deliver up to 4 gpm of hot water at 67° rise. We offer this as low as 86k btu's to 123k btu's for oil and 73 k btu's to 135K btu's for gas or lp.
Small footprint no tank, Great efficiency and lower cost.
Feel free to reach out to our national sales manager to get more info as well as in touch with some factory trained dealers in your area. 570-872-6997
Re: Mini Split Location
To be fair my design temp is 72F and I run 68F at times.
I've never found it to be too low. With a txv the system has no issues controlling humidity. Not sure with minisplits and their EEVs but id hope it does as good or better than a TXV.
74F is too warm for me and forget 76.
I was thrilled my system was able to achieve 75 when it was 100 outside but I'm much happier with it cooler especially in the bedrooms.
I have a freezestat on my evap just in case but it's never been needed in 8 years so far.
That said... Even in my drafty uninsulated house I'm only at 533sqft per ton.
ChrisJ