Re: What type of Vent on pipe near boiler in basement
Those look like Varivalve adjustable straight valves. They are not appropriate for main venting. They are intended to be used on steam radiators. You will want to remove those and the reducing bushings they are piped into. A Gorton #1, Gorton #2, Hoffman 75, or a Barnes and Jones Big Mouth would be appropriate main vents among others. You can find them at SupplyHouse. How long are your steam mains? Can you provide us a picture further out, maybe someone here can give you a better idea of what size vent you need.
Re: Balancing
How are the mains vented? Is a crossover trap from a main to a return failed open and putting steam in the return and closing all the traps along that main so that those radiators can't vent and heat?
Are the returns steam hot anywhere, are they basically the same temp as the supply mains?
Re: New Installation Circulator Flow Problem
The circ in the center looks like a larger motor, is it a 26 series high head? What model is that one. Maybe it is just a different vintage as the others, same size?
Two fingers disassembles a Discal for service. The cap and valve mechanism is replaceable if the needle or seat is damaged.
We see a Caleffi fix on that type air purger from time to time :)
hot_rod
Re: CARLIN EZ PRO gas conversion burner question - firing problem.
Funny, I just mentioned the flame rod in another thread and how difficult it is to reinsert correctly in A and B style heads. However, as @HVACNUT has pointed out, the condition you report is often the result of a combustion problem and in your case with no sooting it is reasonalbe to suspect it is excess air although similar flame rod results can arise with too little air. (exception being you talk about sputtering during operation. I don't know if you had been carefully familiar with the sound of operation before you noticed these restarts or if you have acquired that first hand knowledge during these drop outs such that you might not realize there can be a mildly wave like form to the sound of operation which isn't really sputtering. If this is really sputtering you've got the kind of problem where you ought to shut it down. I don't know if the gas valve could be fluttering. In some installations you might be able to observe the flame if there was an observation port. I sometimes make an observation port by drilling the door or plate where the unit is installed and adding a piece of quartz glass or equivalent but it is very unusual or would mean a crapload of excess air that the process is blowing itself out or marginally igniting and these are intermittent ignition so you wouldn't get a full 10 minute cycle as you describe if the flame were actually going out.)
and if the relay picks up within its retry limit, it won't lock out and it sounds like that is what is happening.
do you have the old 60200FR relay or the newer 60200FRS that has a display. that display allows you to push the up arrow (which if you can read the fine print on it has a microamp symbol) and that will display the microamps generated by the flame rod throughout the light and running process. (I wish it did not automatically return to regularly scheduled programming as quickly as it does as sometimes you are watching through a pure or repurge and just as the boiler fires it disappears and if you aren't quick you won't hit it again in time to see the reading the resulted in a drop out, if one occurs.). these days carlin tech doesn't really even want to talk to you about maginal flame rod pickup if you have the old relay. And, to be fair, despit the $150 you gotta throw for a new relay, it is so much easier to diagnose flame rod output compare to trying to meter it that I keep these relays on hand and replace them anytime I service a unit that has the old realy.
you are looking for something around 2.2 microamps but the control will run with maybe 1 (carlin doesn't tell me that number, only that that 1 is too low even though it may prove flame at that level).
slightly complicating to your post is that this cannot be an atmospheric boiler. the ezgas is used to convert a boiler that took an oil power burner, i.e. forced draft from the burner end, with a gas alternative. but the setup was never atmospheric. (at least I can't imagine how it could have been-maybe some clever macguyver has an atmospheric boiler they could eliminate the draft collar and find enough room to low mount the power burner and kind of seal the base of the combustion area. now you've got me thinking about trying this sometime in the shop for the fun of it, but I don't this you have atmospheric boiler.
IIRC the desired combustion set points are 3-6% oxygen and 8 to 11% CO2 which are fairly typical so I try to get within the range and then monitor CO and flame rod microamps with an eye towards less of the former and more of the later but balancing them to hit the desired 2 and change microamps and usually the range to accomplish that doesn't allow me a lot of luxury to play with efficiency numbers, they just end of being whatever they are.
so the question I posted (Aside from asking for tips on inserting the assembly back into the head), was also how you really assess if the microamps produced reflects any degradation in the rod itself and I haven't had that question answered yet. I will be putting it to my carlin connections when I see them at AHREpxo later this heating season. Because literally every flame rod issue I have encountered with an EXGas I have solved by checking the combustion set, but maybe there is some kind of degradation in the rod that means I am compromising either CO emissions (still well within nominal 400ppm limit although I would prefer below 100ppm and can't always quite make that) or efficiency in order to get the flame rod response I need to satisfy the primary safety control. it may be that it isn't a rod problem and I could consider downfiring the given burner. the setups are not easy for changing the firing rate, which is too bad. I have taken in later installations to adding a union on the downstream side of the gas valve to make it easier to change the orifice (one of the carlin techs told me when I mentioned that that that is how they set up for testing so they can change easily. I think they ought to ship 'em to be set up like that, bit I digress).
Re: Downspout drains underground under brick patio — no backup, but no water at exit either
Ok some other updates from today:
- I used the endoscope/borescope I got from Amazon (this one
)
I couldn't thread through much. Maybe got 3'-4' and couldn't get it to move forward, so not much to learn there - My masonry guy from earlier today suggested blasting water for a good 30min (a few days ago, I only did it for 5min or so) to see if I start seeing water at the discharge, and indeed I did after probably 15-20min. This probably raises more questions than it resolved however… e.g., how in the world does it take that long for the water to reach the discharge?? fwiw when I ran water in to the downspout on the right side (the yellow one), it took less than 30 seconds for me to start seeing water coming out of the discharge.
the straight line distance between the red and yellow marked down spouts is about 15' and presumably it's a pretty straight section of pipe connecting the 2 downspouts below ground, so I don't know how in the world it takes so much longer for the water in the red downspout to reach that discharge….. i suppose there could be a clog, but then again, it should probably take 5-10min to fill that entire network of pipes with water, not 15-20min. i still thinks there's probably a leak somewhere underground.
Re: another copper press fitting peeve: street female adapters
Any unusual fitting will cost you more. $9.45 for a 3/4" Propress slip coupling vs. $4.08 for a Propress coupling with a stop. Removing that dimple is expensive!
And $10.43 for a Propress cap. I'm loading up on Sharkbite.
Re: Using a hot-water radiator for one-pipe steam
1" is good for an EDR of 25 so at 20 your not pushing it. Could you use a 1" valve and reduce the riser to go into the valve? A reducer on a riser is less of a problem.
But. if you lay the rad down and put a 2-footer on it with a cheater it will give up. If not Sawzall it out.
The way you have it is probably fine.
Now that I changed my mind 3 times I am out LOL
Re: Water hammer in steam system
Need pictures. Water hammer is usually a pipe pitch problem. The condensate has to be able to drain out somehow,
Re: What type of Vent on pipe near boiler in basement
We need to know the total length and size (diameter) of the steam mains in your basement, not counting the radiator takeoffs or risers to upper floors, to tell you what size main vents you need.
bburd