Best Of
Re: Cast iron boiler replacement with Navien High Efficiency Condensing Boiler NFB 200H
the boiler you have is a 135,000, 107,000 output. If that has been been adequate, why are you considering a 200?
hot_rod
Re: New Century House with Two Pipe Steam - Questions
That's called a "lock-shield" valve. And the part you're holding in the pic is the key.
Re: Draft inducer motor for gas boiler
We all first tried just replacing the motor , learn from our mistakes .. :)
Big Ed_4
Re: Wirsbo Manifold Pin Valves
Those valves should also have the indicator pin centered over the green dot when they are powered down. You loosen or tighten the mounting ring to adjust them.
I can't believe they are not all broken yet.
Rick
Re: Gas boiler heating house without call for heat
Either way should work, although having relays in series is just more stuff to fail. However it keeps the boiler wiring consistent with the OEM drawings.
Re: Gas boiler heating house without call for heat
With all the detective work you guys have done on my behalf, I kinda feel like I've let you down ordering a replacement part 😂
Re: Gas boiler heating house without call for heat
You need to know your meter…. on my digital meter 000.0 ohms means no resistance. Closed circuit. For an open circuit my meter would read OL which was translated from the infinity symbol (∞) on the old analogue meters in the original instruction manuals. But that was back in the day when old farts were converting from analogue Simpson multi meters to Digital stuff and they thought we needed to be told that ∞ = OL.
Re: Gas boiler heating house without call for heat
I ordered a replacement from Supply House. Will arrive tomorrow
Re: Gas boiler heating house without call for heat
relay is bad. once one contact welds it can hold the other contact closed or it could be a broken spring or dirt making it stick.
Re: Gas boiler heating house without call for heat
@109A_5 Great Video! I believe the opposite happened to @FrankMaraschino's relay. The contacts are not open like in the video, but they are closed or welded together so they do not open when the coil is not energized.
I just thought of a fix for this that will not need any parts. If you use the 5 and 6NO on the SR501 to do what that general purpose relay is supposed to do.
Diagram to follow:
Since all the CR1 contacts on the problem relay do is connect Y to R on the Transformer terminal board, then we can just use 5 and 6NO to connect R to Y on the transformer terminal board. The SR501 is already doing what the CR2 contacts are supposed to be doing, just use the SR501 to do both jobs.
It is easy to do… Just take the wire that is connected to G on the transformer terminal board and place that wire on Y on the transformer terminal board. Very simple fix…. Just remember to leave the CR relay out of the socket.