Best Of
Re: What To Look For When Replacing a Natural Gas Boiler
Take a look at IBC boilers, specifically their SL model. It has left or right side connections which can make Munchkin replacements easier.
In my area, Viessmann boilers are competitively priced. It's the Lochinvar's that are $$$$$.
Re: Makeup water causing boiler failure due to thermal shock
If it causes a problem I think it is likely to be something that warps and leaks later and won't be something you can definitively tie to the thermal shock. Usually the feed is relatively slow compared to the volume of the boiler so the temp change isn't that fast unless the boiler was almost empty.
Re: Commissioning new Peerless 63-06
Well guys, it seems a frickin' miracle has occurred here overnight. I was awakened in the early hours today to some of the more reassuring sounds my system has made over the years and the sense (from under the covers) that a decent amount of heat was coming from my bedroom radiator. I came downstairs to comfortable warmth along the way. And after setting the (electric) tea kettle to boil I headed to the basement boiler room to find my recalcintrant wee beasty sitting quietly at completion of the call for heat with the sight glass level precisely at my Sharpie mark of NWL. Mind you an inch below where I left it but a clear sign from the boiler deities.
I climbed back upstairs to check my problematic living room baseboards. Strains of The Hallelujah Chorus echoing in my head as all five checked out toasty warm from end to end, including #4 (the long one) that had simply coughed a few times when I opened the steam trap at its end during a heat call the day before, and pulled out the trap element, fully expecting or maybe just hoping steam would come rushing to the opening? Maybe? Sorry, cough, gurgle, gurgle ... looking for something here?
After a cup of coffee and a little breakfast the tstat was calling for heat so I went downstairs to witness the miracle it action. The boiler temp came up nicely, with pressure building to about 8 inches WC at start of steaming. It climbed a bit above 16 inches in the early mid cycle, then fell back to 10 to 12-ish as cold condensate began to return to the boiler. Best of all, the sight glass level remained firmly in the +1 to +1.5 inch area the entire time, until the CycleGard threw in it's random "intermittent level test" sending us into vacuum for a brief minute. Once steaming again level came right back to +1. Like I said, a freakin' meer-kle.
Okay, so before we call the Vatican for insights on how my demon-possessed new boiler, regularly spewing it's charge from both ends days before, had suddenly become a docile and a well-behaved heating appliance, I should fess up to two changes I made last night, before settling into the couch with the Missus, for reruns of Uhtred, son of Uhtred, season 2. The first was to move the old Hoffmann 75 sitting atop my condensate system doing nothing but helping to tune the hiss of escaping air, over to steam tail #2, where it might actually do some good. Secondly, after contemplating Paul's admonishment to not worry about adding 8-way until all the oil was cleaned out, it occurred to me that I still had a partial quart of Hercules Boiler Cleaner, which i had used with the old Burham when it sounded a bit too rumbly. So I quickly perused the instructions: "Removes oil, scale, sludge" hmmm well not a lot of scale or sludge yet I assume, "emulsifies oil and grease", that sounds good, "helps stop priming, foaming, and surging", okay I am in. I grabbed my channel locks to open the pipe-bombed shaped chem add port my boiler guy had provided, added a precisely metered 2 1/2 to 3 glugs of the fluorescent green elixir straight into the port, and closed her up. Off to Uhtred.
The rest is, as they say, for the history books. Shout it from the rooftops, "This **** really works! All hail Hercules Boiler Cleaner!"
Re: So fresh water carrying O2 causes corrosion. How about a HOT WATER TANK feeder into the boiler?
You are filling mostly with mostly nitrogen, their is approximately 20% O2 in H2O, 78% nitrogen.
I think you are thinking of how much oxygen and nitrogen is in our air
Yes and the air that is within the water.
Amtrol talks about the air, O-2 and nitrogen component. They did studies on the amount of "air" in water that enters you building.
This Amtrol Handbook should be required reading for anyone in the hydronic business. So, so many problems could be avoid if hydronic folk read this book. It is one of my most used books.
Excellent explanations of p
umping away, air removal, sizing, compression vs hydro pneumatic tanks, troubleshooting, etc.
I think an online version is out there.
hot_rod
Re: Becket Oil burner whining noise.
@VibratingBuzz welcome to Heating Help! I recommend you start a new discussion so that your comment doesn't get lost at the bottom of an older thread. The original poster here hasn't been back to the site in years.
Re: WarmRite System - No flow
Here is an example of a complete system photo that I was able to match to the manufacturer's suggested design.
You can see how all the components are connected in the big picture
Re: WarmRite System - No flow
Can you step back and take some photos of the entire system and near boiler piping? Trying to diagnose with those close up photos is next to impossible.
Example:
My tire will not hold air pressure! Is this the right place to add air pressure to my tire? I have been adding air for about an hour (I think) but no air is staying in the tire. Could the valve be blocked?
The photo below will tell more of the story:
Re: 1920s Steam System - How to Add Main Vents
the problem is that if it is hollow it might shear off and you'll have to make 2 cuts almost to the threads with a hacksaw or thin reciprocating saw blade then knock out the piece with a chisel. a pipe wrench or big crescent wrench will get it out if it is going to come out.









