Re: Not Really a Radiator Vent. What am I?
Was it "Kent" cigarettes that had the "Micronite" filter?
I recall cutting the filter apart and there was a small mini filter ahead of the standard filter. It was thought to be the finest imported asbestos available.
BTW, would have been dry.

Re: Taco Switching Relay- Aged Out?
if it's a 15-year-old relay, equipped with ice cube relays, the relays are replaceable. the current solid-state relays are not. If it's not broken why replace it. you can always replace it if necessary.
Re: Way overfired boiler
Change out the two cross over traps they most likely are failed and if not they look to be a few years old and remove those no 1 Gorton's and install either a pair of no 2 Gorton's or if you feel daring install a hoffmann 67 vapor vacuum vent . As others may have stated check the pigtails on your pressure trolls and do yourself a favor and get a decent 0-3 psia gauge .
i would hope that being a two pipe system that you have ensured that all traps are working properly and that none of them are passing steam into the dry returns . If so replace or repair .As for down firing have some one install a 2 stage gas valve and a vaporstat in conjunction w either the existing pressuretrol or yet another vaporstat
peace and good luck clammy

Re: Piping for New Steam Boiler
@Noah_1 2 questions:
- What was your sq.ft. of steam number measured off your radiators?
Here's your boiler's EDR output including a 33% pickup factor- so the actual output is 1/3 more.
782 sq ft.
2. How does that compare to your measured radiation- in square feet?
Don't get hung up on heat loss or BTU's . Just Sq. Ft of radiation to Sq. ft. of boiler output 😉
Doesn't look like the pipes are insulated so you can write off the pickup factor (mostly). How well that 782 sq ft. matches your measured radiator EDR is what's important.
At the risk of sounding dumb, sq ft of radiation is the surface area of your rads, not the size of the rooms. (Seems your 200k number / 50 is the size of the house- 4000 sq ft)
Re: Looking for advice on balancing the system in my house to to help with heat and clanging
An off topic question…. how well does that "Magic Heat Reclaimer" work that is connected to your flue? I've always wondered how well they would work with a natural gas boiler. Does it "reclaim" much heat?
Re: New Steam Boiler Installed, Water Hammer, Prematurely Turns Off, Frustrated
Oh, this is 2 pipe. I thought it was 1 pipe from the boiler piping.
The vent(s) on the returns and the traps on the radiators need to both be working for the air to vent and the radiators to heat properly. In addition to either the traps or the vents being failed closed, traps failed open can let steam in to the returns and keep other radiators from heating by either closing the vent on the return or heating traps from the return and causing them to close. There should be no steam in the returns.

Re: Why are my wires on L8148L aquastate disconnected
OK, I suspect the solder joints that connect the relay to the circuit board are failing, common defect.
Your zone valve wiring is not quite the way I would do it, but it looks like it would work.
Re: Why are my wires on L8148L aquastate disconnected
i would always connect the R (load) from the transformer to the R on the thermostat. then connect the W from the thermostat to the motor on the Zone valve. This is a good habit to get into for future reference.Your diagram does not show the aux transformer connected properly. You need to use the Z on the L8148
I would also use the onboard transformer and not use the Aux (zone valve) transformer to power the control.