Best Of
Re: pls help me id "epoxy" substance
Hi, Can I hazard a guess that this is a drain line? If so, A good fix would be to cut out the cracked part and use no-hubs to replace the pipe. Some Band-aids like stretchy silicon rubber tape can last a very long time, but are still considered a patch. As the cast iron loses integrity, other problems like sagging can crop up, which is a reason to go with the most durable fix. In the long run, this will save you time.
Yours, Larry
Re: Cleaning HVAC Ductwork?
Unless they run a camera thru the entire ductwork, live, to prove to you that it's actually ALL clean and sanitized. Which they won't, because it won't be.
Re: Cleaning HVAC Ductwork?
Your right but it wasn't always that way. With modern burners and boilers, I don't consider oil boilers dirty but they have to be set up properly.
I agree that a lot of boilers can go maybe 4-5 years without being cleaned. But they are still thing that need to be done during a proper tune up. Nozzle, filter, electrodes check combustion and oil pressure and test safety controls as a minimum. In fact the nozzle can go many years with clean oil.
Re: Adding a radiant manifold to existing single zone loop
I would purchase a Taco SR 502 (or 503) to operate the zone one and the zone 2 circulators separately using separate thermostats. Here is that diagram
Any Questions?
Re: Need help with Radiant How to go laying panels over existing floor
Thank you everyone for the input, I agree abandon redoing the floor especially having to modify the rest of the house for the new height. @PC7060 The boiler is going to have to have re-piping done regardless of which way I choose to go. Which I'm looking at going towards the Ceiling heat option.
@hot_rod Can you refer me to any training for radiant installation? for the future? any suggestions would be great, or books/ literature . Thank you for your time
Re: Help with screw nut
Be advised we can be more powerful than the metal, it may fail when you succeed.
Lance
Re: Where's the capacitor?
I can tell you since those motors first came out, I've never replaced a capacitor. Can't even remember replacing a psc burner motor in the last 8 years.
What problem are you having?

Re: Cost to clean a heat exchanger?
@dandub1960 @mattmia2 @HVACNUT @EdTheHeaterMan @Alan (California Radiant) Forbes @captainco
I wanted to follow up on original post because I appreciate everyone's help and wanted to thank you. I had the original installer of the boiler come out and ran another combustion test (results in image). Tech took the sample from under the draft hood. We also discovered a little nozzle looking piece on the ground next to boiler. I believe he said it was an orifice that goes over the pilot burner, and without that orifice on there the pilot would be burning unrestrained and could give some crazy numbers in a combustion test. So basically the tech who took the original test sampled from wrong location and did not reassemble all the parts!
Re: Cost to clean a heat exchanger?
Did the tech leave behind a printout of the combustion test? At 3 years old, that boiler should be spotless inside. At 20 years it should be spotless. If there's soot, then the tech needs to find out why, not just clean it.
HVACNUT
Re: Vent piping advice
follow the manual,
except, that air intake, looks weird, I would expect you want the 12 inches from the bottom of the intake gooseneck, to the roof deck directly below the intake, not to bottom of rafters at the deck penetration,
call them and ask to explain why the intake is on the deck




![IMG_4981[1].JPG](https://us.v-cdn.net/5021738/uploads/9VAXSHCMQS8F/img-4981-5b1-5d-jpg.jpg)