Re: My steam boiler water got a little contaminated, so what can we learn?
in one of your previous videos you had great success with Squick. any reason not to go that route first?
Re: My steam boiler water got a little contaminated, so what can we learn?
the manual is a compromise of multiple factors, some of which may not apply to your situation. among other things they are probably trying to cover les than ideal near boiler piping. probably the conditions it was tested under for the various certifications and it was probably somewhat arbitrarily picked.
Skimming, cleaner and temperature concerns
Happy new year all. We've had a new 10 section Weil Mclain 80 series oil fired boiler installed and the skimming done by the installers was not as thorough as it ought to have been. We're priming and surging and foaming and dancing and occasionally tripping out in low water. I boiled a sample and it frothed like crazy. Getting the guys back is going to take time and I'd honestly rather do it myself.
- I'm thinking of using TSP since I'm familiar with it and it's readily available here. Does anyone feel strongly about washing soda vs TSP? The installers used nothing but water.
2. We've got a new feed water tank controlled by the primary low water cutout, so I can't open the feed valve to adjust the water level. Where would you connect feed water? There's a garden hose style valve at the bottom beside the return. Forgive the terrible photo.
3. How much of a concern is thermal stress/shock during skimming, draining, filling and restarting from cold? Our previous boiler cracked and the suspicion is that cold water entering a hot boiler and excessive thermal cycling were to blame (building owner is 90 years old and will insist on setting back the thermostat as soon as his rads get warm. Combined with electric heaters in his office satisfying the thermostat, the old boiler would run as little as 2 hours a day. Long story. We've put an aquastat on the header to keep the boiler from going cold and a steam injector on the feed water tank to try and keep cold water away from hot castings. Am I concerned over nothing?
Any other tips or thoughts?
Thanks in advance
Re: How long is a steam radiator supposed to stay on before cycling?
A radiator — one pipe or two doesn't matter — will continue to make heat as long as the boiler stays on. It will only stop when the boiler stops
What happens on one pipe is that when the vent closes the air is out, but steam will keep coming in and condensing as long as the boiler runs. The only way you can stop it from heating is before the boiler starts — if you close the vent then, it simply won't heat up.
It would seem that your building's boiler is just staying on…
Re: How to completely turn off a Vent-rite #1
turn the valve off completely instead of relying on the air vent or screw in a TRV with an integral vacuum breaker like this one:
Re: My steam boiler water got a little contaminated, so what can we learn?
It sounds like we both agree that lower isn’t good and this is why I don’t like people relying on auto-feeders. They spend too much time at lower levels
Totally agree with that.
Re: Wiring Weil-McLain AquaPlus to a Taco SR503-5
For DHW priority.
Red on the aquastat to R Zone 1 (priority) on the zone panel.
White on the aquastat to W Zone 1 (priority) on the zone panel.
Yellow on the aquastat (AC1) to Zone 1 (priority) C on the zone panel. (AC1 shows it as the grounded side)
Green on the aquastat (AC2) to R on the zone panel.
Enable the priority, the switch array on the Right hand side.
Connect the Main X-X and Priority X-X (DHW) End Switch terminals to the appropriate place on the boiler.
Connect the heating zones to Zone 2 and Zone 3.
Make sure the circulators are wired appropriately.
Re: Honeywell Help
@Melby More pictures and more clarity and information, boiler make and model about your present issues may help us help you. The thing you call a spring is a Relay.
When the thermostat circuit closes TV to T that puts 24 VAC across W and T (the relay coil of 1K). Relay contacts 1K1 close energizing the circulator (120VAC), contacts 1K2, 1K3 close enabling the burner (24 VAC circuit).
@HomerJSmith if you like repairing Aquastats, next time consider this. Desolder the relay solder joints, unfold the pins so they are vertical (or perpendicular to the circuit board) wrap thermostat wire (or the like) around each pin snugly and extend it at least about 1/2" onto the circuit board and solder it all securely. The added copper wire will make the solder joint must more robust.
Re: My steam boiler water got a little contaminated, so what can we learn?
"And yes I think the upper inside of the sections is getting constantly bathed in boiling water…that is the point."
So if the point of a higher water level is for the upper surface to run "cooler", that would be measurable, yes? An infrared thermometer should be able to pick it up. My bet is, once the water is boiling and steam is being produced, there will not be any difference.
"So my question is why aren't you running your water level higher?"
Mine has been at the recommended water level (it's clearly marked on the front of the boiler) once the mistake was understood.