Best Of
Re: Pricing on refurbished cast iron radiators
I can't necessarily address pricing, but a company I work with I believe sells several thousand used radiators a year here in Chicago. He's completely reinstalled all the radiators in many multi-unit buildings that are being brought back after sitting abandoned and all the radiators were stolen.
Miracle Iron Holland Furnace
I recently purchased a home built in 1910, which has a fully functional Miracle Iron furnace in it. I hear they are rare and people are interested in them. If you would like more information or photos please let me know
Re: Refurbished radiator making bird noises. Not vent?
I think I’ll try running it with a plug in the vent tapping next and see what happens
Re: Refurbished radiator making bird noises. Not vent?
My thought was that if there’s a hole I may hear air escaping
Re: Near boiler piping/replacement boiler
point the camera at the copper pipe not the aluminum fins
Or at the copper return pipe at the boiler.
hot_rod
Re: I get all the weird ones...
Can they use those clear, hanging thick plastic "drapes" that you see in factories? Trucks drive right through and they part like the Red Sea, then fall back in place...Conserves most of the heat and definitely better than keeping the door open (foolhardy).
I've also seen motion activated clear, superlight, plastic bay doors that open superfast and shut just as fast. Mad Dog
Re: Near boiler piping/replacement boiler
Hi all, I just wanted to give you some updates:
I had some repiping done - supply header is now 1 1/4" and return is 1". Left the circs on the return. Added a Caleffi 573 feed valve. Set low limit to off, so boiler is now a cold start. High limit is set to 180, economy off and differential to 30. Thermal pre-purge is enabled on the hydrostat 3250.
I changed the headbar to 1.00/85 and put in a .85 nozzle at 145 psi pump pressure.
Here are some numbers:
Boiler sat overnight with no calls and dropped to 105 degrees and 10psi water pressure.
I turned on two of the three heating zones to call the boiler on.
This is with the thermostat reading 72 degree house temperature, so it's not really testing at ideal conditions.
3 minutes runtime - stack temp=340, boiler temp=122
4 minutes runtime - stack temp=350, boiler temp=137
5 minutes runtime - stack temp=358, boiler temp=149
6 minutes runtime - stack temp=359, boiler temp=147
7 minutes runtime - stack temp=356, boiler temp=135 - return pipe just getting warm, water feed at 15 psi
8 minutes runtime - stack temp=357, boiler temp=134
9 minutes runtime - stack temp=362, boiler temp=144 - return pipe warm
10 minutes runtime - stack temp=368, boiler temp=155 - baseboard temp=126
11 minutes runtime - stack temp=374, boiler temp=161 17psi water feed, return pipe hot
12 minutes runtime - stack temp=375, boiler temp=165
13 minutes runtime - stack temp=378, boiler temp=171 - baseboard temp=145
14 minutes runtime - stack temp=379, boiler temp=175
15 minutes runtime - stack temp=383, boiler temp=180 - baseboard temp=157
I've never had the boiler run this long, but it might have to do with starting at such a low temperature.
The indirect called about 30 minutes later when the boiler was still at 180 high limit - here are the numbers for that:
145 degrees - boiler fires
2 minutes runtime - boiler temp=149
3 minutes runtime - boiler temp=157
4 minutes runtime - stack temp=350, boiler temp=166
5 minutes runtime - stack temp=360, boiler temp=171
6 minutes runtime - stack temp=372, boiler temp=177
6 minutes 30 seconds - boiler hits 180 high limit again with indirect still calling
I have to do a combustion analysis to see where my numbers are with the .85 nozzle.
Do my stack temperatures look good enough to prevent condensation, or should I increase to a .90 or 1.00 nozzle?
I couldn't measure the return pipe temperature exactly to see if I got 140 degrees after 5 minute. My infrared camera was not picking up the return pipe temperature that well.
Thanks!
Re: Sun Room- Add Sixth Baseboard Hotwater Zone or a Mini Split
I'd run the baseboard into the sun room — but on its own zone, as sun room heat demands are so different from other rooms.
As to freezing — unless that room is isolated from the rest of the house (doesn't sound like it) it's not much more likely to freeze than the rest of the house!