Re: Radiant Heat. Should I raise the temp?
Carpet with pad below? That could be a tough go for radiant heat. Here are some examples of R-value for floor coverings
The slab surface temperature is what you want to know and then see what the wood flooring manufacturers allow. If it is glue down flooring, check the adhesive limitations.
Was a heat load calculation and design done for the system? That would show how the carpet dictates the floor btu output.
That 120- 90 is a wide delta, 10- 15 is typical for residential home radiant. It depends on when you measure that ∆. If you could increase the flow rate the floor surface would even out, be more consistent across the surface and may helps.
Increasing temperature or increasing flow will get you more btu/ ft output. This graphic shows the result of the loop temperature from beginning to end as flow is increased, same SWT.
There is a point of diminishing return, from .5- 1 gpm you see a good boost, the red output curve starts to flattens at around 1.5, it is may not be worth the pumping power to get higher flow rates for minimum increase. You have flow meters on the manifold 1/2" loops you could push .75- .80 gpm maybe, through the under-heating loops.
How long are the loops? What tube spacing? Plain water in the system? Your manifold pump will be the limit to what you can actually flow. It's nice to use a multiple speed circulator to get some adjustability.
You want to measure the loop delta after it has been running for a period of time. When the supply and return temperature stabilize, that is thermal equilibrium, measure at that point.
The delta is ever-changing in hydronic systems it is not something that you can "set" the load at any given point in time, how much heat the loops dissipates, that determines the operating delta.
Trust the onsite measurements to determine the output, the universal formulas can deceive as my mentor explains it.
hot_rod
Re: Single pipe vented steam heat
draining and replacing brown water without addressing pH level is chasing your tail.
The fresh water just makes more rust faster
The tech is right. But I say you shouldn’t need more than 5 gallons per season
Re: Williamson GSA-100 Steam Boiler Tappings
The WM block, and the Williamson block, are exactly the same. WM offers the tankless coil option. Williamson does not. But on their typical standard boilers, the blocks are exactly the same.
Re: Williamson GSA-100 Steam Boiler Tappings
Yes. They don't approve its usage, but it is there. The only reason that it's not approved, is because they need to differentiate themselves a bit from Weil Mclain
Re: Attached EDR vs Boiler SF of steam
If the radiation can't keep up it doesn't matter how big you make the boiler it'll just keep cycling on pressure.
What pressure was your boiler running during this event?
ChrisJ
Re: Rehashing the old Williamson vs Weil McLain comparison, and new boiler specs
I am partial to the vomiting part. Then you know for sure its a bad boiler.
Re: Service for an old HydroTherm HC125B boiler in Westchester County NY
@walterk55 The Hydrotherms are great boilers; able to leap tall buildings in a single bound.
One of my customers has me come out every year to check her HC-85. She has radiant heating and her boiler had sooted up a few years ago; we took it apart and washed down the heat exchanger and were able to bring down carbon monoxide levels from 450ppm to less than 50.
So, whoever you hire, make sure they have a combustion analyzer and that they know how to use it.
Compared to a condensing boiler, there’s not much maintenance to do on a Hydrotherm. Check and clean the burners, check combustion levels, check the pressure on your expansion tank if it’s a bladder type and make sure the small swinging door at the burner box is properly installed. Check the wiring for any wear or melting of covering.
Re: Why did they do it this way?
I usually follow it up with two F & M (Fee & Mason) split ring hangers from the space just under the pressuretrol/Vaporstat over to the nearest immovable object (larger pipe) so no one can knock in to it and push it off kilter. Mad Dog