Re: Correcting my 2 Zone Monoloop System (Need Help)
I have never used a balancer on any small residential system. I find that with a circulator zone system, it is self balancing via the thermostat. if a zone is cold, that thermostat will stay on while the other zone thermostat is satisfied. If you are trying to balance individual radiators on a particular one pipe main, that is usually done with a damper in the radiator cabinet. If you are trying to get the two radiator branch to balance with the other radiators, try doing the individual radiator thing. and when using PEX for those branch runs, try using the next size larger PEX. Use 3/4" for the 1/2" pipes, and use 1" to replace 3/4" pipes.
Re: Correcting my 2 Zone Monoloop System (Need Help)
They uses 2 circulators to avoid having to balance the system. If there were only one circulator, because it is a center fed split main system, they would need balancing valves to make sure both halves of the loop had enough flow to make the monflo work. with 2 circulators, each circulator creates enough flow in each half of the loop.
Someone had the split loop design with one circulator and no balancing valves and couldn't understand why part of the loop didn't heat well.
Re: Steam boiler piped wrong
Re: Safety concerns and replacement options for a 140 co ppm 35 year old boiler
Re: Boiler Replacement Quote
Getting States to agree???? We can't even get the most populated county in the 50 states to agree. Mad Dog
Re: Boiler Replacement Quote
Half the business owners today have no idea what the yellow pages are. You must be over 50
Re: Plate heat exchanger
You can certainly do the job with hydronic hot water heat. You will need 2 circulators an expansion tank, air eliminators a heat exchanger, glycol and all the piping and wiring and controls.
For me the cost of the above would be prohibitive just to heat a bathroom.
I agree with @jumper above. Some electric baseboards or a wall mounted electric heater with a fan will keep the bathroom toasty
JMHO
Re: HTP Phoenix PH 199 throwing F11, false flame signal
Returned to the job with a replacement gas valve. Installed 2 weeks ago and have had no problem since.
Sent original valve back for warranty…..see how that goes.
There is a very fine mesh screen on the gas inlet connection and it was clean.
Just a side note for anyone who has to change one of these out, I recommend just removing the entire burner for better access to the 7 screws involved.
Thanks for input.
Re: heat exchanger needed for combining old & new systems?
Suppose you do not have Oxygen Barrier PEX, the nyou need a HX to separate an iron boiler from the rest of the system. If you are using a stainless steel boiler than no HX needed, but all the pumps and other accessories need to be Stainless steel or Bronze.
After you determine that, you will need two temperatures form that boiler at the same time. In the event that both the high temperature Radiator zone and the low temperature PEX zone calls for heat at the same time.
Here is a booklet you will want to read to know how to do that.
. Zoning with two temperatures starts on Page 24 in this booklet. There are other good sources available to find different ways to do that.