Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
Best Of
Re: Leaking air vents on steam baseboard raditors and banging noise in pipes
A "C" vent is a fast vent and that type of convector is usually happiest with lower vent rates because of all the condensate the convector produces. Are the other convectors venting at that same rate?I need to do more research on convectors to better understand you feedback
You can get vent kits that come with a vent and 5 different vent orifices for that single vent, this lets you dial in the correct venting rate.
Generally you want to vent the mains slowly and the radiators slowly. Keep in mind this is a heating system and it has to be balanced so it comes up to heat at about the same time.
Bob
Re: Radiant Heating Pump pulling power, 0 GPM output. Advice Appreciated
Here is a better illustration of @hot_rod"s diagram. This shows the radiant floor tubing not in the picture. The instructions are the same. Close valve at the circulator pump (#3). Attach the hose from the water heater darin to #2 purge valve. let the water out at #1 purge valve.
Once that is all done, close the valve #1 first.
Then close the valve at the bottom of the water heater second.
Next close the valve #2
Now open valve #3
Check the pressure gauge. if the water pressure is over 50 PSI (or 115 feet) lower the pressure to about 20 PSI or so by letting some water out of valve #1. Then you should be good to go for the rest of the winter. .

By the way.. you still need a relief valve and other components on that heating system closed loop, if it has the heat exchanger coil inside the tank. Please let us know the model number so I can determine if you have the Combi Core® or not.
Once that is all done, close the valve #1 first.
Then close the valve at the bottom of the water heater second.
Next close the valve #2
Now open valve #3
Check the pressure gauge. if the water pressure is over 50 PSI (or 115 feet) lower the pressure to about 20 PSI or so by letting some water out of valve #1. Then you should be good to go for the rest of the winter. .

By the way.. you still need a relief valve and other components on that heating system closed loop, if it has the heat exchanger coil inside the tank. Please let us know the model number so I can determine if you have the Combi Core® or not.
Re: shut off valves turn but don't work
Hi, I see wrench marks on the newish-looking valve. Any chance someone removed the internals? 
Yours, Larry
Yours, Larry
Re: Hand held ultrasonic flow meter? Water differential pressure gauges/ Hydronic manometers?
Ultrasonic has its place in large diameter pipes with laminar flows like central plants or distribution pipes. That's really the only time i've seen them used. I'm looking at the price of the B&G or Winters meter I would invest a little more for a Alnor or go get a Shortridge hydrometer. Often places will rent these meters out for a monthly basis, which you can easily carry in the cost of a job. For quick down and dirty use an old JB refrigeration manifold with a quality gauge and get the peet's plug adapters like the pic Hot_rod posted. It gets you pretty darn close using the manufactures data sheets
Re: Hoffman 2 Vents?
The argument the dead men make is that open vented all the steam must be delivered against atmospheric pressure so the boiler must generate something over 14.7 psi to get it to move to the radiators. With sub-atmospheric delivery that 14.7 at the header is not needed so obviously the delivery is accomplished with a lot less effort.
I don't have any figures for how much this saves. But I can say for sure it does save. Igor published numbers with a pumped system and the savings was very significant.
But I will say it one more time - the real benefit to vacuum operation is on the comfort side. Radiators stay very noticeably warmer longer between burns which evens things out considerably and natural balancing occurs because radiators in the colder areas pull more of the available steam from the mains between cycles. My upstairs/downstairs difference which was significant (and a pain) disappeared altogether with vacuum operation. Steam returns much faster to the radiators on the next burn because every burn starts with the system at the deepest vacuum. Remember, all this happens every cycle and that adds up to a lot of steam travelling against less resistance mostly to the coldest places (wherever they are today) in real time.
If you haven't experienced this first hand then you really don't know.
One other thing, as Hoffman explained, in a one pipe system just one vacuum vent on one radiator will cause that radiator to pull a greater share of the total system steam than without it. Why? Because at boiler shutdown all the other radiators will instantly cease to pull steam from the main while that one won't stop. It isn't that much each time.....but it is every damn time, and it adds up.
I don't have any figures for how much this saves. But I can say for sure it does save. Igor published numbers with a pumped system and the savings was very significant.
But I will say it one more time - the real benefit to vacuum operation is on the comfort side. Radiators stay very noticeably warmer longer between burns which evens things out considerably and natural balancing occurs because radiators in the colder areas pull more of the available steam from the mains between cycles. My upstairs/downstairs difference which was significant (and a pain) disappeared altogether with vacuum operation. Steam returns much faster to the radiators on the next burn because every burn starts with the system at the deepest vacuum. Remember, all this happens every cycle and that adds up to a lot of steam travelling against less resistance mostly to the coldest places (wherever they are today) in real time.
If you haven't experienced this first hand then you really don't know.
One other thing, as Hoffman explained, in a one pipe system just one vacuum vent on one radiator will cause that radiator to pull a greater share of the total system steam than without it. Why? Because at boiler shutdown all the other radiators will instantly cease to pull steam from the main while that one won't stop. It isn't that much each time.....but it is every damn time, and it adds up.
PMJ
3
Grundfos Ups15-58fc speed switching guts
A while ago (2021) I was working on an air handler project and wanted to be able to switch my pump speed with a relay as part of a two stage air handler heating system. I was trying to keep the boiler in the fully condensing mode by slowing flow in the coil to get a high delta T. This is what I found inside a scrap 15-58 pump I had on hand. Yes, I tested it and the relay switching worked well. I know that most won't care and would never need to such info. Someone might find it useful at some point. NO, I don't think the 26-99 is the same. Obviously, use at your own risk. 

Teemok
1
Re: Cover-Tech Heat Pump Covers
The problem is the use of aluminum coils ... Nice set up...
Big Ed_4
1
Re: Water source heat pump piping
In both of the situations you quote, @WMno57 , there was almost certainly enough ground water movement so that you would be extracting heat primarily from the moving ground water, and not -- strictly speaking -- from the ground. And as we know, moving water is a grand way to move heat around! Particularly if Mother Nature does it for you...
So in those situations, it is likely that having all or part of the heat exchange grid pipes under the house world have worked quite well. Not any better than somewhere else on the property, but not much worse, either.
So in those situations, it is likely that having all or part of the heat exchange grid pipes under the house world have worked quite well. Not any better than somewhere else on the property, but not much worse, either.
Re: shut off valves turn but don't work
You can add a mini ball valve before the vent if this is one pipe steam

No air out = no steam in

No air out = no steam in
4




