Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
Best Of
Re: Which is the C (common) terminal on a Honeywell Aquastat L8148E?
this is all that is needed
TV on L8184E control = R on the NEST
Z on L8184E control = C on the NEST
T on L8184E control = W on the NEST
Don't change any jumper between Z and W on L8184E control. Leave it where it is.
Must I remind everyone that Electric is colorblind and it can't read either. This works for the control that @erikengquist shows in the picture. L8148E. It does not work for other controls like the L8148A
TV on L8184E control = R on the NEST
Z on L8184E control = C on the NEST
T on L8184E control = W on the NEST
Don't change any jumper between Z and W on L8184E control. Leave it where it is.
Must I remind everyone that Electric is colorblind and it can't read either. This works for the control that @erikengquist shows in the picture. L8148E. It does not work for other controls like the L8148A
Re: Troubleshooting of recurring overheating events
Hello @zxcv_1984,
Intermittent problems can be the worst. A lot of time can be spent trying to catch them in the act. Sometimes it helps if whatever stimulus is causing the problem can de determined. Is it Weather related, water ingress, amount of use, vibration, loose connections, chafed wires, etc.
If the sensors and their electrical connections are all fine, wouldn't the controller shut the pump off correctly to limit the storage tank temperature ?
If the relay that controls the pump was sticking, for example, how would the controller shut the pump down for an overheating event, it would need a secondary means.
Is the normal operating high limit temperature setting too close to the overheating limit temperature setting ?
Intermittent problems can be the worst. A lot of time can be spent trying to catch them in the act. Sometimes it helps if whatever stimulus is causing the problem can de determined. Is it Weather related, water ingress, amount of use, vibration, loose connections, chafed wires, etc.
If the sensors and their electrical connections are all fine, wouldn't the controller shut the pump off correctly to limit the storage tank temperature ?
If the relay that controls the pump was sticking, for example, how would the controller shut the pump down for an overheating event, it would need a secondary means.
Is the normal operating high limit temperature setting too close to the overheating limit temperature setting ?
3
Re: How accurate are the efficiency percentages claimed by the mod con boiler mfr's?
@pecmsg: thanks for your comment; that's what I think too. I don't think I have ever seen my car mileage even close to the advertised mileage. Probably the mfr is using a brand new boiler and if it doesn't give them the result they want, they are going to try another until they get the result they want. What about a boiler that's been used for one season let alone 10 seasons(half way through the life cycle)? Won't the efficiency go down (even a little) as the the little spaces in the heat exchanger get filled up with debris?
1
Re: How accurate are the efficiency percentages claimed by the mod con boiler mfr's?
The return water temperature drives the boilers efficiency, they can and do reach high 90% efficiencies
Cycle efficiency and system efficiency is another discussion
hot_rod
1
Re: Indoor Reset
Just Wish
They'd give some details on the actual operation of the brain--in particular how it deals with situations where it's forced to go into digital operation. Also, some details about how it handles WWSD would be very valuable.
It appears to allow a substantial drop in system temperature when it's near what I consider WWSD, but I have a sneaking suspicion that if it's say 20° outside and the load is still very low that it won't allow so much drop.
Would hate to make the tank too big and create much of a parasitic load in non-conditioned space, but at the same time want to ensure the boiler finds enough load to keep burn time reasonably long...
Let's see:
Say I want to reserve 11,000 BTUs with a 7° temperature variance. So, I can put 7 BTUs into each pound of water. 11,000 / 7 = 1571 pounds of water. 188 gallons--tank TOO big and/or temp variance too small.
If I work the other way:
Say a 60 gallon tank weighing 500 pounds. With a 10° differential I can reserve 5,000 BTUs.
If the load on the system is 10,000 BTU/hr and the burner can deliver a minimum of 22,000 BTUs in an hour and IF (the BIG if) the boiler allows a 10° variance at whatever outside temp this loss corresponds to, I think the burner would fire for about 40 minutes, then go off for about 30.
Sound logical? 10° supply temp variance over 70 minutes doesn't sound too bad...
Send me those losses and other data, Mike! Make sure you include city--I'll look up weather data.
They'd give some details on the actual operation of the brain--in particular how it deals with situations where it's forced to go into digital operation. Also, some details about how it handles WWSD would be very valuable.
It appears to allow a substantial drop in system temperature when it's near what I consider WWSD, but I have a sneaking suspicion that if it's say 20° outside and the load is still very low that it won't allow so much drop.
Would hate to make the tank too big and create much of a parasitic load in non-conditioned space, but at the same time want to ensure the boiler finds enough load to keep burn time reasonably long...
Let's see:
Say I want to reserve 11,000 BTUs with a 7° temperature variance. So, I can put 7 BTUs into each pound of water. 11,000 / 7 = 1571 pounds of water. 188 gallons--tank TOO big and/or temp variance too small.
If I work the other way:
Say a 60 gallon tank weighing 500 pounds. With a 10° differential I can reserve 5,000 BTUs.
If the load on the system is 10,000 BTU/hr and the burner can deliver a minimum of 22,000 BTUs in an hour and IF (the BIG if) the boiler allows a 10° variance at whatever outside temp this loss corresponds to, I think the burner would fire for about 40 minutes, then go off for about 30.
Sound logical? 10° supply temp variance over 70 minutes doesn't sound too bad...
Send me those losses and other data, Mike! Make sure you include city--I'll look up weather data.
Re: Indoor Reset
Danfoss has
an indoor reset control. It was built to help overcome solar gain problems. I tried on on my office which has a long windowed south facing wall. Mine was tied to a 3 way Esbe valve with a motor actuator.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
an indoor reset control. It was built to help overcome solar gain problems. I tried on on my office which has a long windowed south facing wall. Mine was tied to a 3 way Esbe valve with a motor actuator.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
1
Re: Indoor Reset
Another Level
Between the "smart" boiler and "more and better sensors".
It's the boiler that learns how to adapt to the system to which it is connected. Ideally it learns how to keep everything (boiler and system) operating at peak efficiency. Such is relatively simple if the system has constant and proportional flow. It gets much more difficult with a barrage of digital inputs.
In that regard, modulating boilers are different. I believe that the Vitodens is the only one capable of learning in the way.
Fortunately it does NOT lock you out from being able to control the supply temperature--it learns to adapt to the temperature curve you set.
As I mentioned elsewhere, my Vitodens is learning to use the volume of the system as its buffer when demand is lower than low-end modulation. I suspected this would happen--in fact I reasoned that it must happen were this boiler to be "perfect". So far, it does appear perfect.
Interesting that the control unit displays not only current outside temperature, but "damped" outside temperature. (The damped temp is blank on mine.) I suspect that in Germany MANY more options are available and that you can install a 2nd outdoor temp sensor on the "hot side" of the structure instead of just the "cold side". The unit will then use the difference between the two to establish a damping factor that makes a corresponding adjustment in the supply target.
Anyone know if such a sensor is available HERE and can be installed in a system of type 000:000???
This is going to sound like a bizarre idea, but here goes anyway:
Say you have a proportional system with very low heat loss--not much greater than the low-end modulation rate of the boiler.
One approach to this problem would be to drive the system through a buffer and allow a wide variance in the buffer tank temperature between "charges" with heat.
As an alternative, why not install a well-insulated hot water tank in series with the system load. The burner WILL find all of that extra water. Even with extremely low loads, you should still get nice, long firing cycles.
Between the "smart" boiler and "more and better sensors".
It's the boiler that learns how to adapt to the system to which it is connected. Ideally it learns how to keep everything (boiler and system) operating at peak efficiency. Such is relatively simple if the system has constant and proportional flow. It gets much more difficult with a barrage of digital inputs.
In that regard, modulating boilers are different. I believe that the Vitodens is the only one capable of learning in the way.
Fortunately it does NOT lock you out from being able to control the supply temperature--it learns to adapt to the temperature curve you set.
As I mentioned elsewhere, my Vitodens is learning to use the volume of the system as its buffer when demand is lower than low-end modulation. I suspected this would happen--in fact I reasoned that it must happen were this boiler to be "perfect". So far, it does appear perfect.
Interesting that the control unit displays not only current outside temperature, but "damped" outside temperature. (The damped temp is blank on mine.) I suspect that in Germany MANY more options are available and that you can install a 2nd outdoor temp sensor on the "hot side" of the structure instead of just the "cold side". The unit will then use the difference between the two to establish a damping factor that makes a corresponding adjustment in the supply target.
Anyone know if such a sensor is available HERE and can be installed in a system of type 000:000???
This is going to sound like a bizarre idea, but here goes anyway:
Say you have a proportional system with very low heat loss--not much greater than the low-end modulation rate of the boiler.
One approach to this problem would be to drive the system through a buffer and allow a wide variance in the buffer tank temperature between "charges" with heat.
As an alternative, why not install a well-insulated hot water tank in series with the system load. The burner WILL find all of that extra water. Even with extremely low loads, you should still get nice, long firing cycles.
Re: Indoor Reset
Bob,
The Vitodens appears capable of what you say, yet it has no indoor temperature sensor. Only the outdoor sensor and whatever sensors are built in to the boiler itself. (Still not sure if it senses return temp or not by the way.)
Cloudy/rainy weather finally went away and days are significantly warmer with nights significantly cooler. Still not cold and the boiler is having to learn how to most effectively run in digital operation--remember it can't modulate down to nothing. Low end is about 22 mbh.
This is an old gravity system so there's LOTS of water in the mains. Also, the radiant floors are just connected to the mains with no form of control. Even with all of the TRVs satisfied, there is still a small amount of flow and small heating load from the radiant areas. Therefore there is always some circulation in both main pairs.
The old boiler (a simple standing pilot cast iron cube) was connected to mechanical outdoor reset and WWSD. Circulator constantly running except when stopped by WWSD. Once the house was maintaining heat, the boiler firing time became remarkably consistent--about 2 minutes, 20 seconds. Only the interval between firings would change with outside temp.
There is no low-loss header for the Vitodens and I speculated that it would turn the mains into a buffer. Guess what? It is.
While the Vitodens is still learning, it's a precocious kid that learns fast.
When outside conditions are such that lowest modulation is still too much heat, operation is really interesting:
After not firing for quite a period, the burner will come on at full fire. You can watch the actual supply temp rise rapidly. Within a few seconds, the burner shuts down. This repeats every few minutes for a few times. Then, the burner will come on and ramp down immediately. Actual supply temp is at the reset setpoint and it STAYS there for a very long time--easily 20 minutes! At the end of the cycle, the supply temp starts rising quite rapidly (after having stayed steady) and the burner shuts down.
Then the burner stays off for a long period and supply temp begins a very gradual decline.
My only explanation is that the boiler is learning to charge the buffer (e.g. all of that water in the mains) in a manner to allow the longest possible burn time with minimal target supply temperature overshoot or undershoot.
The Vitodens appears capable of what you say, yet it has no indoor temperature sensor. Only the outdoor sensor and whatever sensors are built in to the boiler itself. (Still not sure if it senses return temp or not by the way.)
Cloudy/rainy weather finally went away and days are significantly warmer with nights significantly cooler. Still not cold and the boiler is having to learn how to most effectively run in digital operation--remember it can't modulate down to nothing. Low end is about 22 mbh.
This is an old gravity system so there's LOTS of water in the mains. Also, the radiant floors are just connected to the mains with no form of control. Even with all of the TRVs satisfied, there is still a small amount of flow and small heating load from the radiant areas. Therefore there is always some circulation in both main pairs.
The old boiler (a simple standing pilot cast iron cube) was connected to mechanical outdoor reset and WWSD. Circulator constantly running except when stopped by WWSD. Once the house was maintaining heat, the boiler firing time became remarkably consistent--about 2 minutes, 20 seconds. Only the interval between firings would change with outside temp.
There is no low-loss header for the Vitodens and I speculated that it would turn the mains into a buffer. Guess what? It is.
While the Vitodens is still learning, it's a precocious kid that learns fast.
When outside conditions are such that lowest modulation is still too much heat, operation is really interesting:
After not firing for quite a period, the burner will come on at full fire. You can watch the actual supply temp rise rapidly. Within a few seconds, the burner shuts down. This repeats every few minutes for a few times. Then, the burner will come on and ramp down immediately. Actual supply temp is at the reset setpoint and it STAYS there for a very long time--easily 20 minutes! At the end of the cycle, the supply temp starts rising quite rapidly (after having stayed steady) and the burner shuts down.
Then the burner stays off for a long period and supply temp begins a very gradual decline.
My only explanation is that the boiler is learning to charge the buffer (e.g. all of that water in the mains) in a manner to allow the longest possible burn time with minimal target supply temperature overshoot or undershoot.
Re: Indoor Reset
Indoor Reset ( I like the name)
Paul,
Our company has a patent pending on a technology that will not likely be out until some time in 2005 or 2006 called Dynamic Demand Profiling. Essentially, we have found a way of calculating the precise heat loss of a structure from information available in virtually every heating system, without a multitude of sensors (indoor or outdoor). Our reset formula is based upon an algorithm that calculates the "Thermal Resistance" of the structure and accurately resets the Mean Delivered Water Temperature based on the current rate of heat loss.
Modulating the water temperature in theory will increase occupant comfort, but we see no evidence that it will incease system efficiency. We have, however, found that moduating the Differential based on the system's capacity to recover (BTU input vs BTU loss) is an effective way of increasing efficency through fewer but longer burn cycles (not a new idea).
The problem is that wide swings in delivered water temperatures (Differential) works against the occupant comfort objective of reset, so a comprimise must be made.
I don't know if this is what you were thinking about, but it is something that we are working on.
Bob Tonner
President
InfinityLab Inc.
www.infinitylab.com
Paul,
Our company has a patent pending on a technology that will not likely be out until some time in 2005 or 2006 called Dynamic Demand Profiling. Essentially, we have found a way of calculating the precise heat loss of a structure from information available in virtually every heating system, without a multitude of sensors (indoor or outdoor). Our reset formula is based upon an algorithm that calculates the "Thermal Resistance" of the structure and accurately resets the Mean Delivered Water Temperature based on the current rate of heat loss.
Modulating the water temperature in theory will increase occupant comfort, but we see no evidence that it will incease system efficiency. We have, however, found that moduating the Differential based on the system's capacity to recover (BTU input vs BTU loss) is an effective way of increasing efficency through fewer but longer burn cycles (not a new idea).
The problem is that wide swings in delivered water temperatures (Differential) works against the occupant comfort objective of reset, so a comprimise must be made.
I don't know if this is what you were thinking about, but it is something that we are working on.
Bob Tonner
President
InfinityLab Inc.
www.infinitylab.com
