Best Of
Re: Weil McLain AB-80H Control Board Fire
Reminds me of a 200-ton Carrier water cooled chiller we had that lost a control board.
After many, many calls to Carrier we were told they did not have a board for that chiller configured. We had to give them the exact Model and serial # and they would configure the board. When we get the board just plug it in and away we go.
Of course, our customer who used the chiller for process is screaming because it was going to take a week to get the board.
So the board shows up late one day and two of us head up there to get the chiller running. My partner puts the board in and is checking parameters and tries to start the chiller ...no go. He works on if for 20 min and is getting all frustrated, so he walks away and I (the guy who hates microprocessors) get into it.
After a couple of min, I find the problem.
We have a water-cooled chiller, and they programmed the board for an air-cooled chiller. Changed one parameter and we were online.
But remember.
They HAD to have the Exact model and serial #s
I trust no manufacturers.
After many, many calls to Carrier we were told they did not have a board for that chiller configured. We had to give them the exact Model and serial # and they would configure the board. When we get the board just plug it in and away we go.
Of course, our customer who used the chiller for process is screaming because it was going to take a week to get the board.
So the board shows up late one day and two of us head up there to get the chiller running. My partner puts the board in and is checking parameters and tries to start the chiller ...no go. He works on if for 20 min and is getting all frustrated, so he walks away and I (the guy who hates microprocessors) get into it.
After a couple of min, I find the problem.
We have a water-cooled chiller, and they programmed the board for an air-cooled chiller. Changed one parameter and we were online.
But remember.
They HAD to have the Exact model and serial #s
I trust no manufacturers.
Re: Oil Boiler to Gas conversion - is my math around savings right?
11:30 AM EST 1/2/24The delivery cost is much higher with NG, locally about 8X the commodity cost.
Wholesale spot price for Heating Oil is $2.55 a gallon (135,000 BTUs).
Wholesale spot price for Natural Gas is also $2.55 (One Million BTUs).
BTU for BTU, oil is 7 1/2 times as expensive as natural gas.
Both oil and gas have transportation and distribution costs. So retail prices are higher for both.
https://finviz.com/futures.ashx
Re: Surging
I appreciate the info. I guess the hardest part is knowing if I'm skimming well. Also, without draining wont my water just stay red being the treatment didnt work?Fred said:You've already recently drained and skimmed. I would skim first then drain and refill but the critical issue is skimming well, slow and long enough to ensure you get all the oils out of the boiler. I use the Steamaster tablets. I think they are worth it but I usually only add two tablets at the beginning of the heating season. The bottle suggests 4 or 5 times that amount but that amount also causes a very unstable water line.
fxrgrunt
1
Re: Oil Boiler to Gas conversion - is my math around savings right?
I don't think fuel prices are a concern of the rules, Ed. They are a commodity price that is readily available everywhere.
Prices of project work are, like if he said "my installer says he can convert me to gas for $xxxx"
Prices of project work are, like if he said "my installer says he can convert me to gas for $xxxx"
Re: Well that isn't going to work (outdoor unit iced over)
Many years ago, in the 1980's I had a neighbor that had the same problem. This unit had a defect in operation that no factory service tech could fix. Consequently, the mfg gave him a 10 year 100% warranty including all service calls. In the 11th year he called me and asked for my help. Long story short, that heat pump had a bad condenser fan motor, a bad defrost timer, and a bad auto reset high pressure switch. The high pressure switch would cut off the compressor at 280 PSI which is not high enough to allow the unit to defrost. I replaced the necessary parts including the high pressure cut out and "shazam", the unit functioned correctly for the first time in 10+ years. There is a lot more to the story that puts the MFG in a bad light so enough for now. So, call a good HVAC and have that unit repaired. Having it iced up like it is will cost you a lot of money in operating $. My 2 cents.
Re: Tiny home in floor radiant hydronic heating (warmboard) help
About the only small enough lp heater is a 6,000 btu/ hr water heater. They are noisy and fairly inefficient
When you run a heat load on a tiny home, it is tiny also. I used a small electric boiler on an 8x20’ home I built. I actually downsized the element in the Thermo 2000 boiler.
One thing to be aware of is the amount of actual floor space to cover the load. With built ins you end up with maybe a 3’ wide strip of useable radiant floor heat. Mine was spray foamed and had good windows, so the load was under.2,000 btu/ hr. The heat from cooking or running a small over is about all you need for heat🤔
When you run a heat load on a tiny home, it is tiny also. I used a small electric boiler on an 8x20’ home I built. I actually downsized the element in the Thermo 2000 boiler.
One thing to be aware of is the amount of actual floor space to cover the load. With built ins you end up with maybe a 3’ wide strip of useable radiant floor heat. Mine was spray foamed and had good windows, so the load was under.2,000 btu/ hr. The heat from cooking or running a small over is about all you need for heat🤔
hot_rod
2
Re: Why is like this Inside Attic having lot of Moisturization Water on Top of Insulation in Winter
Gas fired appliances that are not properly vented can add a lot of moisture to the interior of a home. If you have any, check the combustion exhaust vents when they are running.
bburd
1
Re: Why is like this Inside Attic having lot of Moisturization Water on Top of Insulation in Winter
If it turns out you don't have a roof leak or an improperly terminated bath vent fan or stove hood fan venting in the attic, etc. Water vapor condenses when it's temperature drops below the dew point. Sheetrock and insulation is water permeable. If you have high humidity in the living space the moisture will migrate though the ceiling materials and will condense into water where it cools. Most of the time this happens on the underside of the roof sheathing in a poorly vented attic. In your case it may be happening at the insulation top surface. A cool very humid interior and very cold attic might create the results you are reporting. Lots of: breathing people, cooking, showers, plants or leaks, a wet slab, wet soil in the crawl space. The water is coming from somewhere!
Teemok
1
Re: Why is like this Inside Attic having lot of Moisturization Water on Top of Insulation in Winter
Hi, Is there a crawl space under your house? If so, have a look down there and see if there is any water or moist dirt. The water is coming from somewhere. ☔️
Yours, Larry
Ps. Also, have a look at your water meter. Is there any motion on the dial when no water is being used?
Yours, Larry
Ps. Also, have a look at your water meter. Is there any motion on the dial when no water is being used?
NEST With Two Wires
I've been using a resistor between the "C" and "W" terminals of the zone valve control with great success. The 220 ohm resistor that Taco recommends works, but the resistor gets very hot. I've gone back to the 1,000 ohm resistor that Taco used to supply. It provides less of a trickle current, but providing that the thermostat is off long enough, it will charge the NEST.
Clarification: The control pictured below is a pump control (Taco SR506) which does not have a large enough transformer to power any more than 2 or 3 power stealing thermostats. We added an external 75 VA transformer for the 6 NEST thermostats.