Re: Derating and/or 2-Stage Steam Boiler for Mouat
Boiler EDR is 1454, system load EDR is 1021. I have recently been thinking about your approach of pulsing, but was put off by the short-cycling.
1
Re: Derating and/or 2-Stage Steam Boiler for Mouat
@Harry_6 ,
What is the EDR of the Mouat system the boiler is connected to? I have a 463,000 BTU input connected to 1000 EDR.
I wouldn't dream of running my Mouat system without what amounts to PWM (pulse width modulation).
Unfortunately that requires a custom control. Even my boiler is too big to be allowed to run flat out to tstat satisfaction without building pressure and overshooting. So I break the burns up in shorter even pulses. Works like a charm.
What is the EDR of the Mouat system the boiler is connected to? I have a 463,000 BTU input connected to 1000 EDR.
I wouldn't dream of running my Mouat system without what amounts to PWM (pulse width modulation).
Unfortunately that requires a custom control. Even my boiler is too big to be allowed to run flat out to tstat satisfaction without building pressure and overshooting. So I break the burns up in shorter even pulses. Works like a charm.
PMJ
1
Re: What to do in case of power loss?
Hello @Chris Brown_2 ,
If the ideas previously mentioned won't work for you.
Hot water: Learn how to drain the system the best you can to avoid or minimize damage. Also learn how to re-fill and purge the air out of the system.
Steam: Drain the boiler and the wet returns.
In either case if you drain the boiler you should shut off the gas to the boiler.
Also since if it gets that bad you may want to use a hose to a floor drain and let the water feed to the boiler drip as you previously mentioned. That way there is flow through the boiler water feed pipes which are usually quite stagnant. Or drain the whole house of water. Automotive Windshield solvent / antifreeze can be added to the sink and toilet traps, there may be a more environmentally friendly product. Windshield solvent is inexpensive.
If the ideas previously mentioned won't work for you.
Hot water: Learn how to drain the system the best you can to avoid or minimize damage. Also learn how to re-fill and purge the air out of the system.
Steam: Drain the boiler and the wet returns.
In either case if you drain the boiler you should shut off the gas to the boiler.
Also since if it gets that bad you may want to use a hose to a floor drain and let the water feed to the boiler drip as you previously mentioned. That way there is flow through the boiler water feed pipes which are usually quite stagnant. Or drain the whole house of water. Automotive Windshield solvent / antifreeze can be added to the sink and toilet traps, there may be a more environmentally friendly product. Windshield solvent is inexpensive.
2
Re: Very Cool π Urinals at a Brewery
Our water source is ground water. About 55 or so year round.
Another factor is that many kids did not have running hot water at home, it had to be heated on the stove.
Most had indoor flush WC but certainly not all.
BTW, this was state of the art school building. Pneumatic Powers Day/Night controls on hot water heat with fresh air convectors in each class room. Pre piped for TV and phone. Ceramic tile in hallways and RR's.
I thinking the priest, who called all the shots, decided that those kids didn't need hot water. It was plumbed to the teacher's RR and kitchen.
Another factor is that many kids did not have running hot water at home, it had to be heated on the stove.
Most had indoor flush WC but certainly not all.
BTW, this was state of the art school building. Pneumatic Powers Day/Night controls on hot water heat with fresh air convectors in each class room. Pre piped for TV and phone. Ceramic tile in hallways and RR's.
I thinking the priest, who called all the shots, decided that those kids didn't need hot water. It was plumbed to the teacher's RR and kitchen.
1
Re: Very Cool π Urinals at a Brewery
My house came with a ci pedestal sink with separate hot and cold taps. The sink was kohler if i recall. The overflow was more rust than overflow inside. I have seen separate hot and cold taps in public bathrooms occasionally but i don't remember where. i have seen only a cold tap and a plug in the hot opening where there was no dhw too. I think some of them had the spring loaded auto shutoff cartridges.
1
Re: Very Cool π Urinals at a Brewery
I know this is somewhat off topic, but as I read this thread, I was reminded of these urinals that I saw at a school in Oregon.

1
Why my 85% efficient cast iron boiler is really only 78% efficient
As a homeowner/mechanical engineer who's always trying to understand how things work, it's bugged me over the years that even some heating pros disagree about whether an 85% boiler is really 85% efficient. What does it really mean when the boiler tech sticks his combustion analyzer probe in the flue, and the analyzer spits out the number 85% efficient?
I think I finally understand one source of confusion/disagreement. Heating pros, please feel free to correct me if I go wrong (and I know you will!)
For starters, I'm talking only about "combustion" efficiency. That means, how much energy gets lost up the flue vs. how much gets transmitted into the boiler mass itself and the water that passes through it.
The other efficiency measure, "thermal" efficiency, is a different subject for another time.
Back to combustion efficiency. In doing some online reading, I found this is a useful guide/reference.
https://tsi.com/getmedia/02417ee5-cccc-4dc7-80bc-f7f10924d20a/CA-basic-2980175?ext=.pdf
It seems that a major source of confusion/debate stems from the fact that when oil or natural gas burn, they produce two types of combustion products: "dry gas" (O2, CO, CO2, etc) and water vapor.
Typical combustion analyzers measure the amounts of dry gas (O2, CO, CO2) and the flue gas temperature, from which they can calculate (or use pre-programmed lookup tables to calculate) how much heat energy remains in the exhaust gas stream, as a percentage of the total available energy in the fuel. That's energy that gets lost up the chimney.
For example, in my 85% efficient oil boiler, the tech sticks his probe into the flue, and the analyzer measures the amount of O2, CO, CO2, and the flue temperature, and deduces that the exhaust gas stream still has 15% of the heat energy that was in the oil before it burned.
However, the combustion analyzer does NOT measure how much water vapor is also in the flue gas, and how much energy that vapor is carrying away. This is also called "latent heat." And the percentage of latent heat lost in water vapor varies by fuel. In heating oil, it's about 6-7%. It's higher in natural gas, because gas combustion produces more water.
So the REAL combustion efficiency of my oil boiler is 100-15-7=78%. 15% is lost to "dry gas" in the flue, and 7% is lost to "latent heat," or water vapor.
So if I want to calculate how many useful BTU's my boiler is outputting per gallon, I can multiply the BTU value of oil (138,490 BTU/gal) times 0.78 = 108,022 BTU useful heat per gallon. From my 85% (but really only 78%) efficient boiler.
Now to complicate things further, the heating industry is well aware of the fact that boilers like mine cannot condense and recover that water vapor that's costing me an extra 7% efficiency loss, because condensation would ruin my boiler. So in recognition of that fact, the heating industry gives me two DIFFERENT BTU values for heating oil: a "high heating value" (HHV) which I used in the above example, and a "low heating value" (LHV) which already has the latent heat of the water vapor subtracted from it. I found slightly different values of HHV and LHV for heating oil, but the two that I'm using here are:
HHV: 138,490 BTU/gal
LHV: 129,488 BTU/gal
Again, the HHV includes the latent heat of water vapor, and the LHV does not.
So, another way to calculate the useful heat output of my 85% (?) efficient boiler is to use the low heating value of 129,488 BTU/gal, knowing that the BTU's lost as latent heat of water vapor have already been subtracted.
So now I don't have to subtract that 7% for the water vapor. So my 85% boiler really is 85% efficient, if I use the low heating value for oil that already has the latent heat of water vapor subtracted from it.
So 0.85 x 129,488 = 110,065 BTU/gal useful heat output. (Note that this is about 2,000 BTU different from the previous calculation because I used a round number of 7% for the latent heat earlier, where the difference here between HHV and LHV is 6.5%)
So the truth is that my 85% efficient boiler is really 85% efficient ONLY if I start with the low heating value (LHV) of oil, which is about 130,000 BTU/gal.
But if I start with the high heating value (HHV) of oil, which is about 139,000 BTU/gal, then my 85% efficient boiler is really only 85-7=78% efficient.
That's my current understanding as a non-pro homeowner/engineer, and I welcome correction if I have gone astray. But this example helps me understand one of the sources of confusion about combustion efficiency and what it does (and does not) measure.
(Please also note that this does NOT get into combustion efficiency measurements for condensing boilers, which try to recover most or all of that latent heat by condensing the water vapor. Since I do not have a condensing boiler, that's a different discussion. But the principles are the same, ie that some heat is lost as "dry gas," and some (but hopefully much less, and ideally none) is lost as the latent heat of the water vapor.)
I think I finally understand one source of confusion/disagreement. Heating pros, please feel free to correct me if I go wrong (and I know you will!)
For starters, I'm talking only about "combustion" efficiency. That means, how much energy gets lost up the flue vs. how much gets transmitted into the boiler mass itself and the water that passes through it.
The other efficiency measure, "thermal" efficiency, is a different subject for another time.
Back to combustion efficiency. In doing some online reading, I found this is a useful guide/reference.
https://tsi.com/getmedia/02417ee5-cccc-4dc7-80bc-f7f10924d20a/CA-basic-2980175?ext=.pdf
It seems that a major source of confusion/debate stems from the fact that when oil or natural gas burn, they produce two types of combustion products: "dry gas" (O2, CO, CO2, etc) and water vapor.
Typical combustion analyzers measure the amounts of dry gas (O2, CO, CO2) and the flue gas temperature, from which they can calculate (or use pre-programmed lookup tables to calculate) how much heat energy remains in the exhaust gas stream, as a percentage of the total available energy in the fuel. That's energy that gets lost up the chimney.
For example, in my 85% efficient oil boiler, the tech sticks his probe into the flue, and the analyzer measures the amount of O2, CO, CO2, and the flue temperature, and deduces that the exhaust gas stream still has 15% of the heat energy that was in the oil before it burned.
However, the combustion analyzer does NOT measure how much water vapor is also in the flue gas, and how much energy that vapor is carrying away. This is also called "latent heat." And the percentage of latent heat lost in water vapor varies by fuel. In heating oil, it's about 6-7%. It's higher in natural gas, because gas combustion produces more water.
So the REAL combustion efficiency of my oil boiler is 100-15-7=78%. 15% is lost to "dry gas" in the flue, and 7% is lost to "latent heat," or water vapor.
So if I want to calculate how many useful BTU's my boiler is outputting per gallon, I can multiply the BTU value of oil (138,490 BTU/gal) times 0.78 = 108,022 BTU useful heat per gallon. From my 85% (but really only 78%) efficient boiler.
Now to complicate things further, the heating industry is well aware of the fact that boilers like mine cannot condense and recover that water vapor that's costing me an extra 7% efficiency loss, because condensation would ruin my boiler. So in recognition of that fact, the heating industry gives me two DIFFERENT BTU values for heating oil: a "high heating value" (HHV) which I used in the above example, and a "low heating value" (LHV) which already has the latent heat of the water vapor subtracted from it. I found slightly different values of HHV and LHV for heating oil, but the two that I'm using here are:
HHV: 138,490 BTU/gal
LHV: 129,488 BTU/gal
Again, the HHV includes the latent heat of water vapor, and the LHV does not.
So, another way to calculate the useful heat output of my 85% (?) efficient boiler is to use the low heating value of 129,488 BTU/gal, knowing that the BTU's lost as latent heat of water vapor have already been subtracted.
So now I don't have to subtract that 7% for the water vapor. So my 85% boiler really is 85% efficient, if I use the low heating value for oil that already has the latent heat of water vapor subtracted from it.
So 0.85 x 129,488 = 110,065 BTU/gal useful heat output. (Note that this is about 2,000 BTU different from the previous calculation because I used a round number of 7% for the latent heat earlier, where the difference here between HHV and LHV is 6.5%)
So the truth is that my 85% efficient boiler is really 85% efficient ONLY if I start with the low heating value (LHV) of oil, which is about 130,000 BTU/gal.
But if I start with the high heating value (HHV) of oil, which is about 139,000 BTU/gal, then my 85% efficient boiler is really only 85-7=78% efficient.
That's my current understanding as a non-pro homeowner/engineer, and I welcome correction if I have gone astray. But this example helps me understand one of the sources of confusion about combustion efficiency and what it does (and does not) measure.
(Please also note that this does NOT get into combustion efficiency measurements for condensing boilers, which try to recover most or all of that latent heat by condensing the water vapor. Since I do not have a condensing boiler, that's a different discussion. But the principles are the same, ie that some heat is lost as "dry gas," and some (but hopefully much less, and ideally none) is lost as the latent heat of the water vapor.)
2
Re: Very Cool π Urinals at a Brewery
Some years ago I was asked if I could fix the hot water supply in the restrooms of a 1961 parochial school.
I went to school there when it was built and never noticed any problem with the hot water.
Looking in the plumbing chase it was obvious that there was never any hot water connected.
The H & C were both connected to the cold supply.
Hanging down in the chase was a 3/4" line capped and connected to the hot supply line.
So added a tempering valve and separate hot supplies to the valves.
At several school reunions I asked class mates if they noticed lack of hot water. None did.
The conclusion was that there was little hand washing going on in the 60's-70's-etc.
I went to school there when it was built and never noticed any problem with the hot water.
Looking in the plumbing chase it was obvious that there was never any hot water connected.
The H & C were both connected to the cold supply.
Hanging down in the chase was a 3/4" line capped and connected to the hot supply line.
So added a tempering valve and separate hot supplies to the valves.
At several school reunions I asked class mates if they noticed lack of hot water. None did.
The conclusion was that there was little hand washing going on in the 60's-70's-etc.
4
Re: No heat on new panel rads, monoflow system
I donβt see a new clean piece of brass in the picture between those 2 Tβs.Βmattmia2 said:Actually, look at the cut sheet, they are designed to be installed the way they are installed: https://s3.amazonaws.com/s3.supplyhouse.com/product_files/78810-product.pdf I'm not saying that is the optimal way to use them but that is what veiga shows.
pecmsg
1
Re: Lost wrench for the Lost Art
https://www.wamc.org/new-england-news/2017-10-02/new-public-art-sculpture-installed
The Monkey Wrench Building
Springfield, MA
https://www.thereminder.com/localnews/springfield/monkey-wrench-building-is-undiscovered-gem/
Bemis & Call Tool Factory
Springfield, MA
https://lostnewengland.com/2017/12/bemis-call-tool-factory-springfield-mass/
Moore Drop Forging Company
Springfield, MA
http://alloy-artifacts.org/moore-drop-forging.html
Lotta wrench manufacturing history there.
The Monkey Wrench Building
Springfield, MA
https://www.thereminder.com/localnews/springfield/monkey-wrench-building-is-undiscovered-gem/
Bemis & Call Tool Factory
Springfield, MA
https://lostnewengland.com/2017/12/bemis-call-tool-factory-springfield-mass/
Moore Drop Forging Company
Springfield, MA
http://alloy-artifacts.org/moore-drop-forging.html
Lotta wrench manufacturing history there.
4