Re: Which is better heat pump or a hybrid heat pump
Heat transfere from a heat pump is the refrigerant, a properly sized system with wall mount indoor heads using a quality cold climate product will work fine in most all cases. When we install heat pump ducted systems the dynamic changes, the heat transfere is no longer coming off the coil directly heating the space, it now has to over come velocity loss and heat loss from the ductwork in an unconditioned attic, basement, or crawlspace. A good percentage of homeowners don't want to see a head on the wall, and may even have existing ductwork.
In this instance I would always consider a hybrid option. You may get 10 plus months out of the year the gas valve doest turn on, but the guarantee is there you will make set point no matter what.
If you live a place like northern VT with a -20 design temperature you should have redundancy, wood stove or pellets with heat pump only.
In this instance I would always consider a hybrid option. You may get 10 plus months out of the year the gas valve doest turn on, but the guarantee is there you will make set point no matter what.
If you live a place like northern VT with a -20 design temperature you should have redundancy, wood stove or pellets with heat pump only.
Re: Modcon vs CI Gas Usage - Baseboard Heat
Well...your numbers are right there. The absolute maximum you could save would be the 11 % or so. That will assume that the mod/con is condensing all the time (which it won't be) and that both boilers are otherwise set up and operated optimally.
The modulation does make a difference -- but mostly so that the boiler can condense more of the time. Again, assuming that the mod/con is making use of all its features (particularly outdoor reset) and you don't do strange things with the thermostats. It will help some in reaching towards that 11 % -- but you won't get over that.
The modulation does make a difference -- but mostly so that the boiler can condense more of the time. Again, assuming that the mod/con is making use of all its features (particularly outdoor reset) and you don't do strange things with the thermostats. It will help some in reaching towards that 11 % -- but you won't get over that.
Re: Radiator making loud water hamming noise and water sloshing sound
Now you’re on it! Find that pipe below floor. Radiator takeoff tee should be on a 45 slant. Allows condensate to hug the pipe wall. Drips become Missile hammers. Follow the pipe. Near the end it may have an end of main vent. If plugged radiator is trying to vent branch. Watch the level of the main. It must pitch. Watch for sags. Mentally be the condensate. How does get home. Steam rides top of pipe, condensate runs like a river in the bottom.
Just an idea.
Re: Low water cut off malfuntions
What are other possibilities for the crack? Can the probe low water cut offs misread if sludge is present?
1
Re: Radiator making loud water hamming noise and water sloshing sound
The valve could be your problem.
@Gordo has a U tube video about the pitfalls of a straight globe valve on a radiator that you might want to peak at on U tube. Some designs don't allow the water to drain. You could remove the valve and hook it up without the valve and see how it works.
@Gordo has a U tube video about the pitfalls of a straight globe valve on a radiator that you might want to peak at on U tube. Some designs don't allow the water to drain. You could remove the valve and hook it up without the valve and see how it works.
Re: Radiator making loud water hamming noise and water sloshing sound
Off-topic, I know, but how well does that room heat? With the air vent in the upper position intended for hot water systems, you are probably getting no more than 50% of the steam rating of that radiator.
If the room heats well, I'd leave it alone. If not, there should be a boss further down on that side of the radiator where the vent should be installed for steam heat.
If the room heats well, I'd leave it alone. If not, there should be a boss further down on that side of the radiator where the vent should be installed for steam heat.
bburd
1
Re: Finding Leaks
Also what makes you think it is building no pressure? the vaporstat is set to something insane that i can't read so i wouldn't expect it would ever shut off, that gauge isn't a type that can accurately read low pressure, that mercury vaporstat has to be level to be accurate, and have you checked that the pigtail is clear in to the boiler? The vaporstat also has to be perpendicular to the curl in the pigtail so it stays level because that pigtail curls and uncurls some with temp changes.
2
Re: Finding Leaks
Flood the boiler, fill it to above the top of the boiler and see if water comes running out somewhere.
A mirror will find leaks at valve packings and joints and such but my bet is on the boiler having failed above the water line. If you're lucky it is just a fitting but at the age of that boiler a leak in or between sections is likely.
A mirror will find leaks at valve packings and joints and such but my bet is on the boiler having failed above the water line. If you're lucky it is just a fitting but at the age of that boiler a leak in or between sections is likely.
1
Re: System Design: Solar Thermal Power Generation
I'll start you with the collector area, anyway. If we assume, conservatively, that you can get a 10% thermal efficiency out of it (which is, in my opinion, high for the temperatures you mention), and we also assume you are in New England or actually anywhere pretty much east of the Mississippi and north of the Mason-Dixon line, the general rule is that you can get 3 hours of effective collection per day. Some days you'll get more. Some, particularly in the winter, you will get less.
So... crunching all those numbers together with the dear old solar constant, which is conveniently 1 KW per square meter, we find that you can get an average energy output of 0.3 KWh per square meter of effective collector area per day. So your 5 KWh per day energy will take about 17 square meters of net effective area. Note that that's net effective area -- the area which is actually receiving sunshine and conducting, effectively, to the heat transfer medium.
Now you also mention wanting to generate power from the stored energy in the morning. That energy will have to have been stored the previous day (if you are lucky and it isn't cloudy several days in a row, which is often the case in the winter). You mention 6 to 8 hours. That won't cut it. You need an absolute minimum of 24 hours, and anywhere in the northeast more like 72 hours would be more conservative.
Personally I would like to see you also double check your power and energy requirement relative to your load, which you don't mention. Even with a pretty high efficiency heat pump, your 5 KWh energy only rises to about 50,000 BTU, or about 4,000 BTUh over a day of heat demand.
So... crunching all those numbers together with the dear old solar constant, which is conveniently 1 KW per square meter, we find that you can get an average energy output of 0.3 KWh per square meter of effective collector area per day. So your 5 KWh per day energy will take about 17 square meters of net effective area. Note that that's net effective area -- the area which is actually receiving sunshine and conducting, effectively, to the heat transfer medium.
Now you also mention wanting to generate power from the stored energy in the morning. That energy will have to have been stored the previous day (if you are lucky and it isn't cloudy several days in a row, which is often the case in the winter). You mention 6 to 8 hours. That won't cut it. You need an absolute minimum of 24 hours, and anywhere in the northeast more like 72 hours would be more conservative.
Personally I would like to see you also double check your power and energy requirement relative to your load, which you don't mention. Even with a pretty high efficiency heat pump, your 5 KWh energy only rises to about 50,000 BTU, or about 4,000 BTUh over a day of heat demand.
Re: Burnham Oil Burner creating tons of soot
I'm curious, Has anyone been able to get this running properly while they are standing there? In other words does it run for a period of time only to act up shortly after the crew has left? Or has it never run properly at any time? This sounds so much like a loose or cracked nozzle adaptor.
Grallert