Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
Best Of
Re: NYC Council bill being drafted for radiator inspection
maybe a part of the inspection can be recording each radiator pressure, with a penalty for overages of 2 psi, payable for each radiator,
that might get the boiler keeper's attention to dial it down,
# yeah, fer real
that might get the boiler keeper's attention to dial it down,
# yeah, fer real
4
Re: The case of the steam filled room. this Friday's case
This is probably the case of the plugged pigtail. When I was still working we never allowed 2 pressure controls on one pigtail and that includes the modulating control.
Re: Boiler Failure After Two Years
A mag sep is you best removal device for magnetite, any type of filter or membrane would plug quickly. You would be flushing and servicing a filter weekly 
The magnetite particles can be tiny, .05 micron. The oxide needs to be attracted to a magnet out of the flow. You would need a microscope to see the fine particle size of magnet, it can look like ink, we refer to it as boiler ink.
Not air so much as O2 that causes ferrous metals to break down. The system can be 100%, air and fluid tight, hold a 100lbs air or water test and O2 can still get in. Heating water drives the O2 out, you have "dead" water in a boiler after some run time.
However O2, at the molecular level can still enter an air tight, dead water system. Even even barrier pex allows SOME O2 in as do seals, packings, etc.
The magnetite particles can be tiny, .05 micron. The oxide needs to be attracted to a magnet out of the flow. You would need a microscope to see the fine particle size of magnet, it can look like ink, we refer to it as boiler ink.
Not air so much as O2 that causes ferrous metals to break down. The system can be 100%, air and fluid tight, hold a 100lbs air or water test and O2 can still get in. Heating water drives the O2 out, you have "dead" water in a boiler after some run time.
However O2, at the molecular level can still enter an air tight, dead water system. Even even barrier pex allows SOME O2 in as do seals, packings, etc.
hot_rod
2
Re: New Carpet Upstairs - Rainforest Downstairs
I am betting on that the old carpet or padding removal pulled a nail/ staple out of something....
7
Re: Barometric damper not closing on oil boiler
Back in the 1950s there was a company that manufactured a draft regulator that was adjusted by turning the horizontal axis up to 30° from the horizontal. I believe it was made by the Boston Regulator Company. I actually remember installing some of them in the 1970s. They are all long gone by now, so I would venture to say that you do not have a Boston barometric regulator, so you need the horizontal axis to be level with the horizon. A picture of the Barometric Draft Regulator will help in identifying the brand and type of regulator you have. Could you post a photo?
Re: Steam pipe style convectors
Are they 1.5" SCH 40 pipe, or actually 1.5" OD?
1.5" SCH 40 pipe would be 0.497 sq ft EDR per 1' of pipe
If it's actually 1.5" OD that would be 0.393 sq fr EDR per 1' of pipe
1.5" SCH 40 pipe would be 0.497 sq ft EDR per 1' of pipe
If it's actually 1.5" OD that would be 0.393 sq fr EDR per 1' of pipe
1
Re: The case of that time the boiler blew up with Ray inside the boiler room, this Friday's case.
Can't find the video. However, I have been in the boiler room on a few occasions when a boiler blew up. Let me change the wording as was explained to me by a Pa State Boiler inspector. When there is an explosion caused by the fuel in the boiler that is called a "furnace" explosion and when the pressure vessel explodes that is a "boiler" explosion. All my events were "furnace" explosions and all were eye openers. The first explosion was with an Erie City water tube high pressure steam boiler that was cold and needed to be started. With out my knowledge, the gas/oil selector switch was replaced by the head electrician. I arrived at the site, did a visual check of the boiler and turned on the on/off switch to fire gas. The mis-wired switch put 120 volts directly to the 2 gas valves when the on/off switch was actuated, and after the burner purged and the pilot lit, there was a big bang, and that was the event. All the windows were blown out of the boiler room onto the street, the front burner mounting plate was buckled, and a lot of the internal fire brickwork was shifted a lot. This happened on Friday the 13th I believe in 1974 or 1975. Of course the company I worked for was charged with the mishap and their insurance paid the bill. I had trouble hearing for days and I still blame that event on my hearing deficiency. There were a few others but this was my worst.
Re: Bridge Collapse
Oh I rather agree. Redundancy is good. And, in fact, most ships do have pretty good redundancy -- provided there is time. Evenalmost all the accessory equipment for the main engine is duplicated. There is, however, only one main engine. Very few cargo ships have more than one main engine. Many cruise liners have two or more main generators, which in turn power electric motors which move the ship and provide other power on board, although even there certain electrical faults can black out the ship (there was a big ferry a few years back in British Columbia to which that happened).
It will be interesting to see how much control they got back over their rudder. A look at the track chart suggests that they may have gotten some back -- but I assure you, having done it, that on any reasonably large single screw ship or boat at minimum steerage way, if you don't have the prop wash over your rudder you are pretty much a passenger for any significant and quick course change.
They simply didn't have time. I'll grant that the engine shouldn't have quit. But... engines do.
I will maintain that the lack of fendering on those piers, particularly with the example of the Sunshine Skyway, set them up in the accident waiting to happen class of emergency preparedness...
It will be interesting to see how much control they got back over their rudder. A look at the track chart suggests that they may have gotten some back -- but I assure you, having done it, that on any reasonably large single screw ship or boat at minimum steerage way, if you don't have the prop wash over your rudder you are pretty much a passenger for any significant and quick course change.
They simply didn't have time. I'll grant that the engine shouldn't have quit. But... engines do.
I will maintain that the lack of fendering on those piers, particularly with the example of the Sunshine Skyway, set them up in the accident waiting to happen class of emergency preparedness...
Re: Switching main vent from Gorton no.1 to no.2 (edited, updated new info) (edit with plan)
Perhaps covered above but I assume you are going to "add" the #2 to the #1 rather than just replace? On an antler. If you just type in "antler" in the search on this forum you will find numerous threads with pictorial examples.