Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
Best Of
Re: Taco ZVC405 (replacing a ZVC 404) wont work with existing 2 Nest Thermostats 3 wire config
I'm pretty sure @SteveSan is correct, i.e. that Terminal #1 is a good place to land for a "C" connection.
@jcmathis44 Do you get 24 volts at the thermostat? Is the thermostat fully charged?
@jcmathis44 Do you get 24 volts at the thermostat? Is the thermostat fully charged?
Re: Aluminum High Voltage Wiring
It turned out that the wiring was fine. The detail that fried the elements was low water.
The water level probes sit in a small cylinder separated from the main tank that houses the heating elements. The cylinder is connected to the tank with two, 1" nipples - high and low - kept separate so that the water level probes don't see the violent changes in the water level when the boiler is steaming. The cylinder had become clogged with mineral deposits that prevented the probes from properly reading the water level in the tank and the tank ran out of water.



The water level probes sit in a small cylinder separated from the main tank that houses the heating elements. The cylinder is connected to the tank with two, 1" nipples - high and low - kept separate so that the water level probes don't see the violent changes in the water level when the boiler is steaming. The cylinder had become clogged with mineral deposits that prevented the probes from properly reading the water level in the tank and the tank ran out of water.



Re: Installation of my Burnham Steam Max Boiler 175K BTU Natural Gas
I like the near-boiler piping. Was the inspector happy?
It looks like the skim port has been reduced, but as long as they skimmed it and it's not surging, I'm happy.
What is the total EDR (sq ft of radiation) of your radiators?
Can we see the front of the two gray boxes over on the left side?
Is there just a single main? If not, can we see where the vertical supply feeds into them?
Can we see a picture of your main vent(s)?
Is that a check valve below your autofeeder?
It looks like the skim port has been reduced, but as long as they skimmed it and it's not surging, I'm happy.
What is the total EDR (sq ft of radiation) of your radiators?
Can we see the front of the two gray boxes over on the left side?
Is there just a single main? If not, can we see where the vertical supply feeds into them?
Can we see a picture of your main vent(s)?
Is that a check valve below your autofeeder?
Re: Solar Radiant Heat for Airplane Hangar
Un glazed solar thermal has a very small operating window. On a 35 degree day, 75 degree from the collector you are around 1% efficiency. You would need an awful lot of collector and roof area to even put a dent in a heating load.
When ambient and collector temperature are within a few degrees, expect 90% plus efficiency. But as the ambient around the collector drops, efficiency drops quickly, see the steep performance profile, the black line on the graph.
You really want glazed plate or tube collectors for cold weather operation.
When ambient and collector temperature are within a few degrees, expect 90% plus efficiency. But as the ambient around the collector drops, efficiency drops quickly, see the steep performance profile, the black line on the graph.
You really want glazed plate or tube collectors for cold weather operation.
hot_rod
1
Re: Replacing steam finned convectors
I'm not sure the mass makes as much of a difference in a convector. the convection is going to take most of the heat out of it pretty quickly and once there is no longer enough heat for much convection there is not going to be a lot of heat coming out of it.
1
Re: Bad circulator? System 2K boiler
@KyleO , it sounds like there may be a mechanical problem with the circulator. Sometimes there is a critical frequency where noises can occur, and it may be related to a very specific flow rate. Changing the cartridge in the circular would likely make the noise go away; there is no check valve in that circulator. It does seem odd that it does not make the noise when the burner is running, but does make the noise in the thermal purge mode (the flow rate should not have changed through that transition).
Best,
Roger
Roger
2
Re: Cold house
Sometimes room air circulation through baseboard radiators is blocked by carpeting, drapes or furniture. Air must be able to enter the radiator from the bottom and leave at the top, so an airspace of at least 1/2 inch and preferably 1 inch is needed. A sofa pushed against the wall can also restrict this.
bburd
1
Re: The case of Ray versus the A dimension
My feeling is that the Dimension A probably is more applicable to larger systems than typical residential stuff.
There are a lot of old building using 1 pipe steam that are a lot bigger than a typical house. Bigger systems usually +more pressure drop.
@RayWohlfarth
Not just steel but CI as well. A lot of the old CI boilers were 1pipe out (supply) and I Pipe in (return with a swing check)
Commercial stuff usually has (or is more likely to have) a condensate return tank or boiler feed tank so it doesn't need a Hartford Loop.
Equalizers have to be on a CI boiler now because they throw water into the header. (would be much better if the water stayed in the boiler like it did with old boilers) Steel boilers like a Scotch or Steel fire box boiler have a large area inside to release the steam from the water. On a CI boiler that space is all cut up into individual sections ....by the sections. Every section is an individual boiler. Steel boiler are just a huge tank of water with fire tubes running through them. No restriction on water or steam flow. CI The water and steam have to navigate all these passageways in the sections and the sections will run at different temperatures. A CI boiler with a power burner will always get hot and steam the rear sections before the front.
That's why on CI we need all these equalizers and external headers that a steel boiler can survive without.
And yes. The Hartford Loop was originally supposed to keep water in the boiler if the return line leaked but the best it could do is buy them some time. Coal fired there was no low water control. A lot of the old coal CI boilers had a fusible plug above the combustion chamber. If the boiler finally got low on water the plug would melt when the water got low then it would dump the remaining water on the coal fire in hopes of putting it out.
jmho
Even a huge steel boiler only has 1 supply weather it is 8, 10, 12" whatever no boiler header, no equalizer
There are a lot of old building using 1 pipe steam that are a lot bigger than a typical house. Bigger systems usually +more pressure drop.
@RayWohlfarth
Not just steel but CI as well. A lot of the old CI boilers were 1pipe out (supply) and I Pipe in (return with a swing check)
Commercial stuff usually has (or is more likely to have) a condensate return tank or boiler feed tank so it doesn't need a Hartford Loop.
Equalizers have to be on a CI boiler now because they throw water into the header. (would be much better if the water stayed in the boiler like it did with old boilers) Steel boilers like a Scotch or Steel fire box boiler have a large area inside to release the steam from the water. On a CI boiler that space is all cut up into individual sections ....by the sections. Every section is an individual boiler. Steel boiler are just a huge tank of water with fire tubes running through them. No restriction on water or steam flow. CI The water and steam have to navigate all these passageways in the sections and the sections will run at different temperatures. A CI boiler with a power burner will always get hot and steam the rear sections before the front.
That's why on CI we need all these equalizers and external headers that a steel boiler can survive without.
And yes. The Hartford Loop was originally supposed to keep water in the boiler if the return line leaked but the best it could do is buy them some time. Coal fired there was no low water control. A lot of the old coal CI boilers had a fusible plug above the combustion chamber. If the boiler finally got low on water the plug would melt when the water got low then it would dump the remaining water on the coal fire in hopes of putting it out.
jmho
Even a huge steel boiler only has 1 supply weather it is 8, 10, 12" whatever no boiler header, no equalizer
Re: Sidewall venting
@annie11771
Please see the Victory boiler manual attached. See page 4 it states that "all victory boiler models can be side wall vented" Page 5 has the horizontal venting instructions
When you say the chimney is collapsing do you know if it is the structural part of the chimney or the clay liner? A 1910 house may not have a liner.
In addition, usually it is just the upper part of the chimney that is exposed above the roof that deteriorates and they can usually be rebuilt from just below the roof.
But all cases are different I am just trying to find out what is going on and if whomever inspected it is exaggerating.
Please see the Victory boiler manual attached. See page 4 it states that "all victory boiler models can be side wall vented" Page 5 has the horizontal venting instructions
When you say the chimney is collapsing do you know if it is the structural part of the chimney or the clay liner? A 1910 house may not have a liner.
In addition, usually it is just the upper part of the chimney that is exposed above the roof that deteriorates and they can usually be rebuilt from just below the roof.
But all cases are different I am just trying to find out what is going on and if whomever inspected it is exaggerating.



