Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
Best Of
Re: Solar Radiant Heat for Airplane Hangar
Un glazed solar thermal has a very small operating window. On a 35 degree day, 75 degree from the collector you are around 1% efficiency. You would need an awful lot of collector and roof area to even put a dent in a heating load.
When ambient and collector temperature are within a few degrees, expect 90% plus efficiency. But as the ambient around the collector drops, efficiency drops quickly, see the steep performance profile, the black line on the graph.
You really want glazed plate or tube collectors for cold weather operation.
When ambient and collector temperature are within a few degrees, expect 90% plus efficiency. But as the ambient around the collector drops, efficiency drops quickly, see the steep performance profile, the black line on the graph.
You really want glazed plate or tube collectors for cold weather operation.
hot_rod
1
Re: Replacing steam finned convectors
I'm not sure the mass makes as much of a difference in a convector. the convection is going to take most of the heat out of it pretty quickly and once there is no longer enough heat for much convection there is not going to be a lot of heat coming out of it.
1
Re: Bad circulator? System 2K boiler
@KyleO , it sounds like there may be a mechanical problem with the circulator. Sometimes there is a critical frequency where noises can occur, and it may be related to a very specific flow rate. Changing the cartridge in the circular would likely make the noise go away; there is no check valve in that circulator. It does seem odd that it does not make the noise when the burner is running, but does make the noise in the thermal purge mode (the flow rate should not have changed through that transition).
Best,
Roger
Roger
2
Re: Cold house
Sometimes room air circulation through baseboard radiators is blocked by carpeting, drapes or furniture. Air must be able to enter the radiator from the bottom and leave at the top, so an airspace of at least 1/2 inch and preferably 1 inch is needed. A sofa pushed against the wall can also restrict this.
bburd
1
Re: The case of Ray versus the A dimension
My feeling is that the Dimension A probably is more applicable to larger systems than typical residential stuff.
There are a lot of old building using 1 pipe steam that are a lot bigger than a typical house. Bigger systems usually +more pressure drop.
@RayWohlfarth
Not just steel but CI as well. A lot of the old CI boilers were 1pipe out (supply) and I Pipe in (return with a swing check)
Commercial stuff usually has (or is more likely to have) a condensate return tank or boiler feed tank so it doesn't need a Hartford Loop.
Equalizers have to be on a CI boiler now because they throw water into the header. (would be much better if the water stayed in the boiler like it did with old boilers) Steel boilers like a Scotch or Steel fire box boiler have a large area inside to release the steam from the water. On a CI boiler that space is all cut up into individual sections ....by the sections. Every section is an individual boiler. Steel boiler are just a huge tank of water with fire tubes running through them. No restriction on water or steam flow. CI The water and steam have to navigate all these passageways in the sections and the sections will run at different temperatures. A CI boiler with a power burner will always get hot and steam the rear sections before the front.
That's why on CI we need all these equalizers and external headers that a steel boiler can survive without.
And yes. The Hartford Loop was originally supposed to keep water in the boiler if the return line leaked but the best it could do is buy them some time. Coal fired there was no low water control. A lot of the old coal CI boilers had a fusible plug above the combustion chamber. If the boiler finally got low on water the plug would melt when the water got low then it would dump the remaining water on the coal fire in hopes of putting it out.
jmho
Even a huge steel boiler only has 1 supply weather it is 8, 10, 12" whatever no boiler header, no equalizer
There are a lot of old building using 1 pipe steam that are a lot bigger than a typical house. Bigger systems usually +more pressure drop.
@RayWohlfarth
Not just steel but CI as well. A lot of the old CI boilers were 1pipe out (supply) and I Pipe in (return with a swing check)
Commercial stuff usually has (or is more likely to have) a condensate return tank or boiler feed tank so it doesn't need a Hartford Loop.
Equalizers have to be on a CI boiler now because they throw water into the header. (would be much better if the water stayed in the boiler like it did with old boilers) Steel boilers like a Scotch or Steel fire box boiler have a large area inside to release the steam from the water. On a CI boiler that space is all cut up into individual sections ....by the sections. Every section is an individual boiler. Steel boiler are just a huge tank of water with fire tubes running through them. No restriction on water or steam flow. CI The water and steam have to navigate all these passageways in the sections and the sections will run at different temperatures. A CI boiler with a power burner will always get hot and steam the rear sections before the front.
That's why on CI we need all these equalizers and external headers that a steel boiler can survive without.
And yes. The Hartford Loop was originally supposed to keep water in the boiler if the return line leaked but the best it could do is buy them some time. Coal fired there was no low water control. A lot of the old coal CI boilers had a fusible plug above the combustion chamber. If the boiler finally got low on water the plug would melt when the water got low then it would dump the remaining water on the coal fire in hopes of putting it out.
jmho
Even a huge steel boiler only has 1 supply weather it is 8, 10, 12" whatever no boiler header, no equalizer
Re: Sidewall venting
@annie11771
Please see the Victory boiler manual attached. See page 4 it states that "all victory boiler models can be side wall vented" Page 5 has the horizontal venting instructions
When you say the chimney is collapsing do you know if it is the structural part of the chimney or the clay liner? A 1910 house may not have a liner.
In addition, usually it is just the upper part of the chimney that is exposed above the roof that deteriorates and they can usually be rebuilt from just below the roof.
But all cases are different I am just trying to find out what is going on and if whomever inspected it is exaggerating.
Please see the Victory boiler manual attached. See page 4 it states that "all victory boiler models can be side wall vented" Page 5 has the horizontal venting instructions
When you say the chimney is collapsing do you know if it is the structural part of the chimney or the clay liner? A 1910 house may not have a liner.
In addition, usually it is just the upper part of the chimney that is exposed above the roof that deteriorates and they can usually be rebuilt from just below the roof.
But all cases are different I am just trying to find out what is going on and if whomever inspected it is exaggerating.
Re: The case of Ray versus the A dimension
We should always have these discussions. When someone actually measures the actual performance of an assumption made by some dead man that maybe had a unique situation and therefore applied that "RULE" to every system regardless of the differences in the systems, we can see the "Myth Buster" at work. Thanks Paul for your comments and video. You actually taught me something so many months ago after our extensive discussion on that subject. 
The fact that the "Dimension A" is part of Steam textbooks means that at some point there was an issue, Could it have been on a system with steam mains that were too small and therefore there was a significant pressure drop off, or were there other factors …only the dead men know. But the explanation Ray offers does have its basis in physics of water and pressures and the like. So understanding that IF you happen to come across a one pipe system that does have that pressure drop issue, the Dimension A will resolve it. IF (and that is BIg IF PAUL) you find it, you can see the fix in your mind's eye without the need to install glass pipes and pressure gauges all over the place. But I really like the Weil McLain glass boiler and @ethicalpaul's glass pipes.

The fact that the "Dimension A" is part of Steam textbooks means that at some point there was an issue, Could it have been on a system with steam mains that were too small and therefore there was a significant pressure drop off, or were there other factors …only the dead men know. But the explanation Ray offers does have its basis in physics of water and pressures and the like. So understanding that IF you happen to come across a one pipe system that does have that pressure drop issue, the Dimension A will resolve it. IF (and that is BIg IF PAUL) you find it, you can see the fix in your mind's eye without the need to install glass pipes and pressure gauges all over the place. But I really like the Weil McLain glass boiler and @ethicalpaul's glass pipes.
Re: Need help evaluating a contractor/hydronic heat boiler plan
Code should / may require a back flow protector.
Either way their cheap insurance.
https://www.supplyhouse.com/Resideo-Braukmann-FM911-1-2-FM911-Backflow-Preventer-Boiler-Fill-Valve-Assembly-NPT-or-Sweat
Either way their cheap insurance.
https://www.supplyhouse.com/Resideo-Braukmann-FM911-1-2-FM911-Backflow-Preventer-Boiler-Fill-Valve-Assembly-NPT-or-Sweat
pecmsg
2
Re: New Burnham steam boiler only heats fully in the morning
Perhaps they all get hot only in the morning, because the thermostat is turned up from a low nighttime setback temp and has a longer run time than during the day when it is just maintaining. It seems like venting can be an issue, are the radiator vents adjustable?
3


