Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
Best Of
Re: Solar Radiant Heat for Airplane Hangar
Assuming you do not have any or much passive, here are some solar thermal numbers.
First knowing the load would be helpful. Assume 15 btu/ ft to maintain 60°, X 3100 46,500 BTU/hr.
Reasonable winter temperatures in Reno, mid 30's oct- Feb.
The solar collector output is all about the ambient temperature around them.
This graph shows 3 types of collectors and the formula for calculating efficiency.
Assume the temperature to the collector from the building is 95F- 35F ambient. Collector supplying about 100- 105°F
Divided by the radiation, 200 is a realistic winter time radiation number, summer may see up to 300.
So Ti- Ta. 95°- 35° divided by 200 =.3
On the bottom axis, find .3 run straight up to the collector slope. So a glazed flat plate would run about 45% efficient on that winter day. Unglazed collector, about 0%, sorry
it just cannot overcome that 35 ambient.
At the SRCC website you can pull down collector rating. Here is a typical 40 sq ft SunEarth spec.
Use cat. D for heating, so somewhere between 5- 15,000 BTU per DAY (6 hours) from a 4X10 collector
You need 46,500 BTU per HOUR. So about 800 sq.ft of collector gets you close. 20 collectors at around $800.- 1000. For maybe 6 hours of a design day load. You still have 18 hours of no sun heating to cover per day.
I've spent a lifetime trying to make solar thermal pencil out for heating. Even with wholesale cost on copper fin, glass and aluminum and making them yourself it doesn't pencil out.
The solar contractors I know shoot for maybe a 30% SF solar fraction. Cover 30% of the heating load. But the installed cost still puts it in the 1% ers price range.
When incentives were in place covering up to 50% of installed cost, ROI was still 15- 20 years out on a even a basic basic 2 panel DHW system.
Harvest all summer coast all winter? Maybe. This apartment building in Switzerland does it. Got $$ and room for about 50,000 gallons of insulated storage and 3000 sq ft of collector?
First knowing the load would be helpful. Assume 15 btu/ ft to maintain 60°, X 3100 46,500 BTU/hr.
Reasonable winter temperatures in Reno, mid 30's oct- Feb.
The solar collector output is all about the ambient temperature around them.
This graph shows 3 types of collectors and the formula for calculating efficiency.
Assume the temperature to the collector from the building is 95F- 35F ambient. Collector supplying about 100- 105°F
Divided by the radiation, 200 is a realistic winter time radiation number, summer may see up to 300.
So Ti- Ta. 95°- 35° divided by 200 =.3
On the bottom axis, find .3 run straight up to the collector slope. So a glazed flat plate would run about 45% efficient on that winter day. Unglazed collector, about 0%, sorry
At the SRCC website you can pull down collector rating. Here is a typical 40 sq ft SunEarth spec.
Use cat. D for heating, so somewhere between 5- 15,000 BTU per DAY (6 hours) from a 4X10 collector
You need 46,500 BTU per HOUR. So about 800 sq.ft of collector gets you close. 20 collectors at around $800.- 1000. For maybe 6 hours of a design day load. You still have 18 hours of no sun heating to cover per day.
I've spent a lifetime trying to make solar thermal pencil out for heating. Even with wholesale cost on copper fin, glass and aluminum and making them yourself it doesn't pencil out.
The solar contractors I know shoot for maybe a 30% SF solar fraction. Cover 30% of the heating load. But the installed cost still puts it in the 1% ers price range.
When incentives were in place covering up to 50% of installed cost, ROI was still 15- 20 years out on a even a basic basic 2 panel DHW system.
Harvest all summer coast all winter? Maybe. This apartment building in Switzerland does it. Got $$ and room for about 50,000 gallons of insulated storage and 3000 sq ft of collector?
hot_rod
3
Expansion on heat-pex piping.
I was looking for some input from the group how they handle expansion on long runs of heat-pex tubing. This is for a snowmelt job that has a run approximately just under 100ft of 1 1/4" from the point of exit of the house to a 4 loop manifold. I ran the 1 1/4" heat-pex tubing in a 3' PVC conduit for the total run. Every time the snowmelt goes on the piping in the basement expands approximately 5"-6". I used expansion fittings for my connections. Just concerned over time they may leak because of the movement of back and forth. Spoke with Uponor and they told me not to be concerned, but we all have heard that before.
Re: Is there a two pipe steam doctor in the house?
After reading your reply 63-04 you say ,well I doubt I would have risked a 2 inch header , as stated I get beaten all the time by the all 2 inch header installer yeah it’s much cheaper but it ain’t better . As for wanding and cleaning ah yeah chemicals ain’t gonna do it . If piped properly and clean the water line shouldn’t bounce more then 1/2 inch durning the cycle . I would suggest your boss be the one who deals w it he sold it and he did the 2 inch header and should have honestly cleaned after the first steaming and then one or two return visits to ensure it’s clean . It s really part of the job which most shrug off and state that’s the way steam is well I’m here tell ya that ain’t the way it’s suppose to be . It looks from the eq drop that skimming wasn’t gonna happen when you pipe your eq drop in front of the skim port it’s highly unlikely it was in the thought pattern and really over looked . It’s a pet peeve of mine to make sure the skim port can be used other wise it serves zero purpose . The use of the standard boiler drains are crap I usually throw them in my brass scape and install full port ball valve for reverse flushing and removing all the crap the always returns when a new boiler is installed . It isn’t some thing that happens w just about every steam boiler ,multi returns visits to get the system clean,again personally the most common issue w mis behaving steam boiler is bad piping ,not cleaned . This is really the second half of the job and the one most don’t price in until beaten badly then they learn . Just like undersized header and wet steam there common and a lot of system will operate but as I always say never what they should be and the biggest thing the in knowing your successful in your install is when customer never knows weather the heat is on or off they just know that there comfortable . This what we all should aim for being we are all in the indoor comfort business ?I just saw you're in Mahwah. So are we. I work at Bolkema Fuel.
Peace and good luck clammy
I agree that installs should be done to best practices. We're learning on the job here. I've asked for training and my boss just says "get it done". I've told him our training methods are like that of a mother bird. She pushes the babies out of the nest and says "fly baby bird".
Since the boiler is less than a year old, and we've drained the system a few times, do you think there's any reason to skim and wand the boiler?
Re: Burner dropout after Roth Install
@STEVEusaPA
Agreed. But is it the cause of my intermittent issue since the purpose of the tigerloop is to remove the air? Or is it a secondary issue?
Agreed. But is it the cause of my intermittent issue since the purpose of the tigerloop is to remove the air? Or is it a secondary issue?
1
Main Vent Replacement Advice
Hi All, just got a house and I'm getting obsessed with the steam system. Everything I've read is telling me if I need advice to post here.
This is the thing that stuck out to me most when evaluating system - for my main vents I have two Vent Rite #33s on mains that are both about 60' long of 2inch pipe. From the way they're mounted it seems like these were a cheapo / quick fix option and I want to replace them.
People suggest Gorton #2s here, but my issue is that I am working with a 1/8" hole and not much headroom - so I think to install those I'd need to use a 1/8" inch nipple into a 1/2" reducing coupling on the background main, and a 1/4" to 1/2" similar on the foreground one, assuming I cant budge that existing coupling. Its odd to me, looks like they went from 1/8 -> 1/4 -> 1/8 again. I am pretty confident I could do this myself if everything goes smoothly.
Overall my system is working pretty good. I notice some sputtering and hissing from the radiators which is a little annoying at night and I want to do what I can to fix what's gotta be an issue on the mains before I replace the radiator vents.
Is this a sensible approach? My main concerns aside from my own incompetence is whether there's enough room for the Gorton to be properly distanced from the pipe, and whether it's bad for the vent to be mounted on an 1/8" hole when the aperture on the vent is 1/2" - makes me worry about velocity hitting the vent being bad for it.
Bonus pic of the boiler as well.. thanks for reading and/or for any advice !


This is the thing that stuck out to me most when evaluating system - for my main vents I have two Vent Rite #33s on mains that are both about 60' long of 2inch pipe. From the way they're mounted it seems like these were a cheapo / quick fix option and I want to replace them.
People suggest Gorton #2s here, but my issue is that I am working with a 1/8" hole and not much headroom - so I think to install those I'd need to use a 1/8" inch nipple into a 1/2" reducing coupling on the background main, and a 1/4" to 1/2" similar on the foreground one, assuming I cant budge that existing coupling. Its odd to me, looks like they went from 1/8 -> 1/4 -> 1/8 again. I am pretty confident I could do this myself if everything goes smoothly.
Overall my system is working pretty good. I notice some sputtering and hissing from the radiators which is a little annoying at night and I want to do what I can to fix what's gotta be an issue on the mains before I replace the radiator vents.
Is this a sensible approach? My main concerns aside from my own incompetence is whether there's enough room for the Gorton to be properly distanced from the pipe, and whether it's bad for the vent to be mounted on an 1/8" hole when the aperture on the vent is 1/2" - makes me worry about velocity hitting the vent being bad for it.
Bonus pic of the boiler as well.. thanks for reading and/or for any advice !


1
Re: Is there a two pipe steam doctor in the house?
@takoateli , let me make sure I have this right- if I'm standing where the water heater is and looking at the return pipes, which pipe is to the right of the Wiley return trap? Is it the end of the dry return or the end of the steam main?That is the return from the radiator traps. The end of the steam mains are to the left of the Wiley Boiler Return.
Re: Is there a two pipe steam doctor in the house?
You are quite correct. There should be no pressure -- and certainly no steam -- in the dry returns. This suggests, though, that there are two separate problems. One is that somehow steam is getting into that dry return. A connection which shouldn't be there, a failed open radiator trap, a pair of drips to a wet return which isn't actually wet (too high -- above the water lien), a blown water seal (too much boiler pressure)... several possibilities.Thank you sir! The main vents are working. When the system starts from a cold start the main vents let air out as the system fills with steam. When the steam fills the dry return they are closing.
It is likely that the presence of steam closed the main vent on that dry return which allowed the pressure buildup-- but... is there one? Is it functioning?
Go back to basics and take a look at everything -- and think like steam (which should be in the mains and radiators and nowhere else) and air (which has to get out of the radiators and then out of the dry return) and water (which has to get out of the radiators, into the dry return, and then through a drip to the wet return or boiler.
I believe one or more of the upstairs radiator traps are letting steam past, filling the dry return and causing the system to stop working.
What are "drips" to a wet return?
Where would the "water seal" be that could be blown?
Thanks!
Re: Is there a two pipe steam doctor in the house?
What size boiler ? Is that a 3 inch riser or was it reduced? Was this boiler skimmed ,from the drop on the equilizer blocking the skim port i would think not . I see no provision where left to wand the boiler or drain all contents out of the boiler . Possible you have some carry over condensate from the boiler being possible dirty . Are you using a vapor stat as a pressure control or still the pa404 . As other may have asked is the a good low pressure gauge aside from the zero 30 gauge . I usually add nothing and just flush wand and skim boilers I ve installed , some times it takes 2 or 3 times to get all the crap out and at last I’ll add surge master when I’m sure it as clean as it can be just for the o2 and for slight corrosion protection and a great indicator of make up water when it ain’t green they have been adding make up . Follow what other have stated and if there using water seal type traps and graduated supply valve then it gotta be a vapor stat and and low pressure other wise you will be just chasing your tail like a puppy . Usually no part of a steam system I replace has any copper except the water line feeding it . Full port tees w bushing and ball valves for flushing and draining other wise it just glam .The boiler is a peerless 6304. The riser/header is 2". We didn't skim it. We did put in Surgex. No vapor stat yet. Need to get the right pressure gauge. The boiler was just put in last year. Do you think it needs to be wanded?
Peace and good luck clammy
We flooded the system twice, once with cleaner, and flushed out what we could with a hose. I think all the sealer we added to the old boiler is out of the system.
Re: TT Solo
Not sure,but I think this model had a "recall" ..
It was an easy fix by adding a couple screws to the intake and exhaust ports on top of the boiler.
I'd also check if it was affected by the "Ignition Upgrade"
It was an easy fix by adding a couple screws to the intake and exhaust ports on top of the boiler.
I'd also check if it was affected by the "Ignition Upgrade"
Re: Aluminum High Voltage Wiring
Maybe I should have said reducing pins. Basically what Chrisj showed, but for larger size. Burndy AYP & others. Unfortunately, what I found in two minutes of googling on my phone is that Burndy had Al pins for aluminum & Cu pins for copper. The only one I saw that was dual rated was the AYP series, & they're Al body, so no go. Maybe I just answered my own question.
1