Re: Are mod-con high efficiency boilers false economy Vs traditional cast iron over a longer time frame?
Your list does not include FUEL COSTS.
Mod Con high-efficiency boilers provide substantial FUEL COST SAVINGS which your list of cons does not even include. If you are only looking at the installation and maintenance cost, but not the efficiency and fuel cost benefits, you are only kidding yourself.
We have 3 sister buildings, each about 45,000 sq ft, only one of which was retrofitted 16 years ago with Mod Con Boilers, Indirect DHW Tank, modern Ventilation systems, Driveway Melting and advanced process controls.
Fuel use on the two sister buildings with the 30-year old original natural draft boilers with ON-OFF control is DOUBLE that of the retrofitted building, because they also only think maintenance cost is important. I am quite happy to save about $20,000 / year on the fuel bill for the retrofitted building.
So the answer is - do the full economics - consider total long-term cost of ownership.
Doug
Mod Con high-efficiency boilers provide substantial FUEL COST SAVINGS which your list of cons does not even include. If you are only looking at the installation and maintenance cost, but not the efficiency and fuel cost benefits, you are only kidding yourself.
We have 3 sister buildings, each about 45,000 sq ft, only one of which was retrofitted 16 years ago with Mod Con Boilers, Indirect DHW Tank, modern Ventilation systems, Driveway Melting and advanced process controls.
Fuel use on the two sister buildings with the 30-year old original natural draft boilers with ON-OFF control is DOUBLE that of the retrofitted building, because they also only think maintenance cost is important. I am quite happy to save about $20,000 / year on the fuel bill for the retrofitted building.
So the answer is - do the full economics - consider total long-term cost of ownership.
Doug
2
Re: Are mod-con high efficiency boilers false economy Vs traditional cast iron over a longer time frame?
I'd look very carefully at circumstances for the fuel savings that are being presented. It is very likely that most if not all of the existing boilers were grossly oversized for the heat load and probably well past thier prime. This causes a very large reduction in efficiency.... especially when looking at atmospheric gas boilers. I have found that simply going from a 2x oversized atmospheric boiler to a properly sized atmospheric (in residential) is about a 12% reduction in fuel use. Tales of 36% saving are probably true, but how much savings would there be by just properly sizing the equipment? I have done many commercial projects where we replaced existing boilers with 2 or 3 staged atmospheric boilers and saw typical savings from 35 to 40%.
I just replaced my 60% oversized stack damper equipped atmospheric boiler in my home's high mass conerted gravity system( which I combustion tested and it was running about 30% excess air and about 84% efficient) and replaced it with an about 60% oversized tiny power burner gas boiler with stack damper ( firing about 30% excess air and 84% efficient) and it looks like I have reduced fuel usage about 20%.
A simple on/off cast iron boiler connected to a single zone high mass system is a very efficient combination. There is no need for outdoor reset, as the mass of the system automatically resets the water temperature, and the boiler will have very long on cycles with very long off cycles for very high operating efficiency. About the only gains you will have with a condensing boiler is due to the condensing, which is probably worth about 12% reduction in fuel use. These mod con fuel savings will also be offset in part due to higher electrical usage of a typical modcon ( 2 pumps, blower motor and onboard electronics running nearly 24 hours a day all winter long.
Also, Mod cons have been around a lot longer that 15 years or so. They have been in use in Europe for more like 30 to 35 years ( the Triangle Tube models are one example) and the typical life is in the 12 to 15 year range.
In my book mod cons are simply not cost effective. Focusing investment on reducing heat loss of a structure is likely much more cost effective, because it has a 4 fold impact....Lower heat loss at a given outdoor temperature, a reduction in the length of the heating season ( a building is self heating due to internal gains) , cooling loads are probably reduced, and you are more comfortable year round.
I just replaced my 60% oversized stack damper equipped atmospheric boiler in my home's high mass conerted gravity system( which I combustion tested and it was running about 30% excess air and about 84% efficient) and replaced it with an about 60% oversized tiny power burner gas boiler with stack damper ( firing about 30% excess air and 84% efficient) and it looks like I have reduced fuel usage about 20%.
A simple on/off cast iron boiler connected to a single zone high mass system is a very efficient combination. There is no need for outdoor reset, as the mass of the system automatically resets the water temperature, and the boiler will have very long on cycles with very long off cycles for very high operating efficiency. About the only gains you will have with a condensing boiler is due to the condensing, which is probably worth about 12% reduction in fuel use. These mod con fuel savings will also be offset in part due to higher electrical usage of a typical modcon ( 2 pumps, blower motor and onboard electronics running nearly 24 hours a day all winter long.
Also, Mod cons have been around a lot longer that 15 years or so. They have been in use in Europe for more like 30 to 35 years ( the Triangle Tube models are one example) and the typical life is in the 12 to 15 year range.
In my book mod cons are simply not cost effective. Focusing investment on reducing heat loss of a structure is likely much more cost effective, because it has a 4 fold impact....Lower heat loss at a given outdoor temperature, a reduction in the length of the heating season ( a building is self heating due to internal gains) , cooling loads are probably reduced, and you are more comfortable year round.
Re: Are mod-con high efficiency boilers false economy Vs traditional cast iron over a longer time frame?
An interesting topic with regards to cast iron lasting 30 years is: what will be available in terms of new products in the next 10 - 15 years? Who knows, but like most things HVAC has seen some pretty amazing technological improvements in the last 10 - 15 years. I worked with my Dad when I was younger; at 80 he is still puzzled by boilers that you can hang on the wall... For every gallon of flue gas condensate produced you save about 8,000btus. There are products that "sit" in the middle of traditional cast iron boilers and low mass wall hung modulating condensing boilers. Take a look at the Viessmann CU3A - it's floor standing, high mass, fully modulating and condensing. No need for primary secondary piping, low loss headers, etc. That being said, qualified installation and the service that follows is key; so look for a contractor with a good history of installing such products if you find comfort "in the middle" of traditional and wall hung.
1
Re: Are mod-con high efficiency boilers false economy Vs traditional cast iron over a longer time frame?
You are posing a very tough question -- and one to which I personally think there is no definitive answer. Let me give you my impressions on your questions, though -- all of which are quite valid.
- Higher up front cost
This is quite true; significantly higher
- Shorter life span (15 yrs vs 20-30yrs ??)
This may not be as true as it once was.
- Annual expensive maintenance essential
Absolutely. And will be more expensive, though how much more expensive is questionable.
- Parts more expensive and may be more difficult to source
This is absolutely true. There have also been problems with many of the parts being specific to a particular maker and sometimes a particular model, and may be come difficult to impossible to source after several years, or if dealers change
- Unlikely to be running at 95% unless system is optimally designed and operated
- Cast iron radiators not optimal for low enough return temps for condensing
These two depend very much on how much oversize your radiation is in relation to your actual heat load. If the radiation is significantly oversized to your current heat load, you will be able to run lower temperatures and use the condensing more of the time. This will improve average efficiency, though you won't achieve the 95% except during those times you can run the water temperauture low.
- More complex, so more likely to have issues/requiring service visits, more of a PITA. The current boiler has never caused any problems in 10yrs since we have lived here.
Absolutely true
- I wonder if I ran the costs over a 30 yr time frame which one would come out ahead, with the least amount of headaches which is a big factor for me. No idea of course of future NG costs.
This is your big -- and unknowable -- variable: future fuel costs. Can the expected, conservative 5% savings in fuel costs outweigh the additional maintenance cost and lost opportunity cost from the additional capital expense. If you can figure that one out, let me know.
- Higher up front cost
This is quite true; significantly higher
- Shorter life span (15 yrs vs 20-30yrs ??)
This may not be as true as it once was.
- Annual expensive maintenance essential
Absolutely. And will be more expensive, though how much more expensive is questionable.
- Parts more expensive and may be more difficult to source
This is absolutely true. There have also been problems with many of the parts being specific to a particular maker and sometimes a particular model, and may be come difficult to impossible to source after several years, or if dealers change
- Unlikely to be running at 95% unless system is optimally designed and operated
- Cast iron radiators not optimal for low enough return temps for condensing
These two depend very much on how much oversize your radiation is in relation to your actual heat load. If the radiation is significantly oversized to your current heat load, you will be able to run lower temperatures and use the condensing more of the time. This will improve average efficiency, though you won't achieve the 95% except during those times you can run the water temperauture low.
- More complex, so more likely to have issues/requiring service visits, more of a PITA. The current boiler has never caused any problems in 10yrs since we have lived here.
Absolutely true
- I wonder if I ran the costs over a 30 yr time frame which one would come out ahead, with the least amount of headaches which is a big factor for me. No idea of course of future NG costs.
This is your big -- and unknowable -- variable: future fuel costs. Can the expected, conservative 5% savings in fuel costs outweigh the additional maintenance cost and lost opportunity cost from the additional capital expense. If you can figure that one out, let me know.
Re: Are mod-con high efficiency boilers false economy Vs traditional cast iron over a longer time frame?
I'm not a pro, just a semi- informed homeowner, so I'm not going to try to influence you either way. But I will ask some relevant questions and share my take on our heating system, which is quite similar to yours.
Question number one is how long you expect to live in this house. On one hand, you ask "would I be adding a lot more complexity and cost over the long run for short term gains in efficiency..." What do you define as "short term gains in efficiency?" If you're planning to live in the house another 30 years, that's *long* term gains in efficiency. And you seem to be taking the long view, because you talk about running the cost comparison over a 30-year period.
On the other hand, then you talk about "the least headaches, which is a big factor." I'm pretty sure you already know from your research which type of boiler is likely to give you "the least headaches" over 30 years.
I've gone through a similar evaluation cycle with our 4-unit 4800 sq ft condo building that I maintain in the Boston area. I've looked at converting our 100-year-old gravity converted system to ATW heat pumps, condensing boilers, etc. What I keep coming back to is the proven history of the 25-year-old cast iron Weil McLain boilers we run (2 of them). They've been bulletproof for 25 years and have survived periods of benign neglect, minimal maintenance, and occasional maltreatment (before I got here, of course.)
Every other alternative I've looked at is more expensive up front and will need more attention and is more likely to fail and need expensive parts, some of which may not be readily obtainable. In a communal building like this one where I may not always be around to fix things, reliability and simplicity are key.
So where I keep ending up is that it's not worth us trying to wring more efficiency out of our systems by converting to more expensive, more complex, more failure-prone systems. When we need a new boiler, it's going to be another cast iron 86%, probably another Weil McLain, but a smaller one to match our actual heat load.
YMMV. I'm sure you will hear good arguments for going the other route too.
Question number one is how long you expect to live in this house. On one hand, you ask "would I be adding a lot more complexity and cost over the long run for short term gains in efficiency..." What do you define as "short term gains in efficiency?" If you're planning to live in the house another 30 years, that's *long* term gains in efficiency. And you seem to be taking the long view, because you talk about running the cost comparison over a 30-year period.
On the other hand, then you talk about "the least headaches, which is a big factor." I'm pretty sure you already know from your research which type of boiler is likely to give you "the least headaches" over 30 years.
I've gone through a similar evaluation cycle with our 4-unit 4800 sq ft condo building that I maintain in the Boston area. I've looked at converting our 100-year-old gravity converted system to ATW heat pumps, condensing boilers, etc. What I keep coming back to is the proven history of the 25-year-old cast iron Weil McLain boilers we run (2 of them). They've been bulletproof for 25 years and have survived periods of benign neglect, minimal maintenance, and occasional maltreatment (before I got here, of course.)
Every other alternative I've looked at is more expensive up front and will need more attention and is more likely to fail and need expensive parts, some of which may not be readily obtainable. In a communal building like this one where I may not always be around to fix things, reliability and simplicity are key.
So where I keep ending up is that it's not worth us trying to wring more efficiency out of our systems by converting to more expensive, more complex, more failure-prone systems. When we need a new boiler, it's going to be another cast iron 86%, probably another Weil McLain, but a smaller one to match our actual heat load.
YMMV. I'm sure you will hear good arguments for going the other route too.
3
Re: Steam Main trap
That is a header or end of the main drip trap.
Believe it or not the correct way to size this trap is by calculating not the steam but the WEIGHT of the pipe valves and fittings in the steam line upstream of that trap. Then you figure the amount of water being condensed by heating those pipes valves and fittings up to steam temperature.
I have done this and find that in almost every system a 3/4" F&T (any brand) will take cere of this load
Believe it or not the correct way to size this trap is by calculating not the steam but the WEIGHT of the pipe valves and fittings in the steam line upstream of that trap. Then you figure the amount of water being condensed by heating those pipes valves and fittings up to steam temperature.
I have done this and find that in almost every system a 3/4" F&T (any brand) will take cere of this load
Re: Dear Reader
Don't know what to say. I attended about 4 seminars, have probably 6 or 7 books and have read countless articles and have been hanging out here for around 20 years I think.
Thank you, Dan. You had a profound effect on my career (for the better). So glad I found you and this site. I wish I had found it sooner I would have made fewer mistakes.
I traveled as far as a couple of hours to some of those seminars.
When I have trouble on a job one thing always sticks in my head. "Get inside the pipe" if you were steam or water what would you do? I always remember that. Thank you, Dan, for all you have done and continue to do.
Thank you, Dan. You had a profound effect on my career (for the better). So glad I found you and this site. I wish I had found it sooner I would have made fewer mistakes.
I traveled as far as a couple of hours to some of those seminars.
When I have trouble on a job one thing always sticks in my head. "Get inside the pipe" if you were steam or water what would you do? I always remember that. Thank you, Dan, for all you have done and continue to do.
Re: Minnesota Right to Repair Law
Apple has been criticized for various things over the years, some deserved, some less so, but currently, their self-repair program is rather unparalleled.
They will send you the tools to borrow, and the parts, with detailed instructions and you can have at it:
https://support.apple.com/self-service-repair
They will send you the tools to borrow, and the parts, with detailed instructions and you can have at it:
https://support.apple.com/self-service-repair
Re: Minnesota Right to Repair Law
Louis Rossman has a youtube channel that was mostly about repairing Apple computers, mostly MacBooks. He got very much into right to repair laws because Apple goes to great lengths to make sure no one but their techs can repairs their products, in order to boost profits. Often they refuse to repair older products to boost sales of newer products.
Apple has made it impossible to repair some products. E.g. put serial numbers in hard drives and memory so that if you replace one the computer cannot start. John Deere did things like that. The Onewheel electric skateboard makes it impossible to replace the battery as i recall. Auto companies want to make it impossible repair newer cars. He has gotten involved in lobbying some states. I recall Apple mostly put him out of business with their scheming.
https://www.youtube.com/@rossmanngroup/videos
John Deere issue
https://www.youtube.com/watch?v=CSAPY5mYm3E
Apple has made it impossible to repair some products. E.g. put serial numbers in hard drives and memory so that if you replace one the computer cannot start. John Deere did things like that. The Onewheel electric skateboard makes it impossible to replace the battery as i recall. Auto companies want to make it impossible repair newer cars. He has gotten involved in lobbying some states. I recall Apple mostly put him out of business with their scheming.
https://www.youtube.com/@rossmanngroup/videos
John Deere issue
https://www.youtube.com/watch?v=CSAPY5mYm3E