Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
Best Of
Re: Radiant: Between Joist - Are my Joists and subfloors drying out and twisting/slight movement?
New Information:
I thought of something thismorning that may be the cause that I forgot about. Specifically in the wall directly where the floor is raising There was a leak in my chimney flashing that leaked into my attic > eventually the water made its way down that wall. It must have made its way to the bottom of the wall and into the subfloor. The radiant must have dried it up causing the plywood underlay and possibly the laminate to raise/warp. The laminate looks fine on the top but perhaps the plywood is warping or both. It seems a little ridiculous for the radiant to dry the wood out that much in and older house that has been heated and lived in for that long (1970 house).
I am going have to slide the floor a part and investigate more.
I thought of something thismorning that may be the cause that I forgot about. Specifically in the wall directly where the floor is raising There was a leak in my chimney flashing that leaked into my attic > eventually the water made its way down that wall. It must have made its way to the bottom of the wall and into the subfloor. The radiant must have dried it up causing the plywood underlay and possibly the laminate to raise/warp. The laminate looks fine on the top but perhaps the plywood is warping or both. It seems a little ridiculous for the radiant to dry the wood out that much in and older house that has been heated and lived in for that long (1970 house).
I am going have to slide the floor a part and investigate more.
2
Re: Cast iron radiator at high flow rate
@hot_rod , the place I've seen over-pumped rads is in converted gravity systems. These have larger pipes feeding the rads than newer systems do, since the original motive force acting on the water is so small. Over-pumping one of these can, and does, cause the water to short-circuit through the rads. Here is an extreme example (note that we eventually replaced the original boiler some years ago):
https://www.heatinghelp.com/systems-help-center/adjusting-the-flow-rate-for-an-old-gravity-hot-water-system/
which led to further research that produced this:
https://www.heatinghelp.com/systems-help-center/sizing-circulators-for-old-gravity-hot-water-heating-systems/
https://www.heatinghelp.com/systems-help-center/adjusting-the-flow-rate-for-an-old-gravity-hot-water-system/
which led to further research that produced this:
https://www.heatinghelp.com/systems-help-center/sizing-circulators-for-old-gravity-hot-water-heating-systems/
Re: Punctured Kitec Pex-Al-Pex lines - best path forward?
I didn't think there was a 3/8 Kitec? What is the O.D.?
1/2" is .640 outside.
A company in Canada makes Kitec fittings
www.veratek.ca
1/2" is .640 outside.
A company in Canada makes Kitec fittings
www.veratek.ca
hot_rod
2
Re: Oversize boiler or juuust big enough, based on past utility usage, and other questions
....I don't know why I thought DHW would be less of a demand.FWIW: in Downeast Maine, my on-demand water heater is twice the BTU of my hot air furnace. Yes the air is cold, but water in Maine ground is colder (not in degrees but in heat-suckage)....
Yeah, back in New Jersey in a UN-insulated 1830s house the water-heat was a trivial load on a massive steam-boiler, but opposite here.
My recent experience with a "just right" hot air and A/C system is that I coulda used the next size up on both burner and chiller. It works but has to run up to 23 hours/day and won't recover quickly after a deep set-back. Bigger parts would be more idle/standby losses but I can't see it would be unaffordable.
BTW, IMHO: get the place rented ASAP. I think the recent panic in housing is about to turn cold.
2
Re: HePEX expansion noise or use Pex-Al-Pex?
The tube really should not move in the aluminum plates. Use a brand that has a tight grab on the tube. Do not fasten the end of the loops so movement can occur there.
Any of the brand name he-Pex should work, stay with one that has a coating over the EVOH barrier. The hard, high gloss coatings tend to make noise.
Go with an A Pex for best flexibility
Any of the brand name he-Pex should work, stay with one that has a coating over the EVOH barrier. The hard, high gloss coatings tend to make noise.
Go with an A Pex for best flexibility
hot_rod
1
Re: Help Please! Old 2-pipe System
Others will have better ideas than I do about testign steam traps. Failed closed is harder to test, you can get some idea about if they are failed open if it is steam hot on both sides of the trap.
Steam in the returns will cause 2 big problems.
1. If it reaches the return vent it will close the vent and stop all venting of air from the system.
2. If it reaches the outlet side of a steam trap through the return before steam reaches the trap through the supply it will close the trap and stop the radiator(or main) from venting air any further.
3. It can cause water hammer
Steam in the returns will cause 2 big problems.
1. If it reaches the return vent it will close the vent and stop all venting of air from the system.
2. If it reaches the outlet side of a steam trap through the return before steam reaches the trap through the supply it will close the trap and stop the radiator(or main) from venting air any further.
3. It can cause water hammer
1
Re: Help Please! Old 2-pipe System
If everything is set up right steam should never reach the traps on the radiators.True. However, the amount of time and testing -- and precision of control -- required to reach that wonderful state is beyond what most people will be willing to pay for. Ideally, one would have both the precisely adjusted and never to be touched inlet control device and, for the occasion when the pressure gets too high, the trap. Further, there is an assumption made that the system is so well balanced that steam arrives at every radiator at exactly the right time for it to put out exactly the right amount of heat to heat that space that day. Good luck with that one.
I agree, I'm not a purist. Put the traps on -- they're not that expensive -- and relax. And if you never get the differential pressure too high they'll last pretty well forever. The system Cedric powers has aboout three dozen traps (Hoffmans) which were installed in 1930 -- and haven't been touched since and still work just fine
Re: Help Please! Old 2-pipe System
If everything is set up right steam should never reach the traps on the radiators.
1
Re: Help Please! Old 2-pipe System
You can test the traps simply by measuring the temperature drop across them when the radiator is fully hot. The inlet should be at least 5 degrees hotter than the outlet (use an IR thermometer, but be aware that if the finish on the two pipes is different the temperatures may not be accurate. And measure the outlet as far away from the trap as is reasonable...)
Re: Help Please! Old 2-pipe System
there are instructions for the valve about where to set the stop based on the edr it is connected to, right?Yes, there are. They are internal, however, at least on Hoffman valves and a pain. Perhaps more to the point, the markings are correct for one and only one differential pressure (I believe it is 4 ounces per square inch) (the same problem exists for orifices -- they are correct for one, and only one, differential pressure).
Mind you, I'm not saying that using a steam trap to keep steam out of the return instead of a precisely set valve or orifice is as elegant as the valve or orifice. It isn't, and there's a certain pleasure and pride in getting a regulating valve or orifice system set up properly. But doing that requires that the boiler be precisely matched to the radiation demand (and let's not forget that that varies with room temperature...) (or has a narrow band pressure control) and that the boiler pressure is allowed to reach optimum pressure quickly and then stabilises there, and that someone has been able to take the time and go around to the entire system and set the valves or swap orifices until the whole thing is in balance.
