Re: Wiring HydroStat 3250 With Multiple Circs and ZVC
You can run the heating pump on C1 terminal of 3250. XX on ZVC to TT on 3250 is 24v only. Still need 120 from DHW pump to ZR.
Line and low voltage can not run in same conduit. Low voltage can be secured to the outside of conduit carrying line voltage but only to the appliance it’s controlling
Re: Wiring HydroStat 3250 With Multiple Circs and ZVC
TT is 24V only, 3250 has an integral transformer
Re: Do your techs wear shorts?
These didn't, at least not to The Lovely Naoko, who has the most sensitive nose I've ever encountered ;-)
@PC7060 , looks like the half-off sale is over. Current prices are roughly 25% off list.
Re: Radiator below waterline on 1PS system
I think that radiator was salvaged from somewhere else and just had a bleeder on it, I don't think it is necessary for it to work. The radiator should fill to the water line of the boiler and the air vent out through the mains and vents on the system until it is full to the water line.
Be careful about giving them a replacement with similar EDR. The part that is below the water line is what will heat and its output will only be whatever the hot water output of that area is at whatever temp the condensate is. Might be important that it has similar volume below the water line.
It is going to be cold until enough condensate has been produced by the system so it will heat a significant time after the system heats and stay warm after the system shuts off (or maybe just stay warm the whole time depending on what the cycle rate and duration of the system looks like).
Since there is no place for the air to vent out at the radiator, that riser to the main will trap a column of air and keep steam from getting to the water in the radiator and causing water hammer.
If you were to move the radiator above the water line that would require re-engineering of how it is connected to the system so that it can get steam and get rid of condensate without the condensate from the system running through it and possibly doing a 2 pipe on a 1 pipe sort of setup to allow the condensate to drain below the main.

Re: Mini split condenser fan intermittent
All valid points! I was under the impression that the ability to turn off the "auto" function was effectively an override for the "get to work you lazy machine" people, which in this case, I am. When in auto, it'll idle all day and eventually get where it needs to go, but typically if I push enough buttons it will consent to doing what it's capable of. I can't hear the compressor at all and never could, but maybe I'm just hard of hearing. It would stand to reason that the two are synced, but I'd find it hard to believe that the compressor is stopping along with the fan while there is a tremendous load on the other side of the wall. I do suppose it's possible that the inlet sensor is picking up a cooler temp than actual, but I have a thermometer on the wall 2 feet from the head and another across the building 40 feet away which both are within 1 degree of the remote's reading regardless of the remote's location in the space so I'd like to think that's not the case. I have not had a chance to open it up again yet, but I will certainly keep you posted when that happens. Thanks again!

Re: Can Pex be fished through copper ?
You can run it at 190 f. You may get more expansion noise the hotter you run it and the more it cycles on/off vs just an outdoor reset temp matched to the load.

Re: Radiator below waterline on 1PS system
Nick_Castrads, I believe this arrangement is a variant of what Holohan called a "Brooklyn Special" He mentioned this about 7 years ago.
Re: How an intermittent problem avoided a catastrophe, this Fridays case
I had a job once where a carpenter had an HVAC contractor pull a permit for him so he could install an LP gas fired furnace. The carpenter ran the fuel line from the LP tank, which happened to be the size of a train car and hooked it up to the furnace with no regulator. Fortunately, the gas valve blew apart internally and failed to open otherwise that would have been a tragedy for anyone in the building and around the site. The scary part is the carpenter had no idea of what he was doing and no idea of the damage he could have caused. We are in a dangerous business and always have to keep our eyes and ears open, they could be our best tools that we own.
Bob Cermignano
Re: Distance between outdoor second stage regulator relief discharge and interior appliances - code
What @mattmia2 said.
Keep the regulator away from air intakes , flue outlets, electrical meters etc. Anything indoors is not considered.
Putting the boiler inside and the reg outside on the same wall will only be a problem if the flue and air intake are near the regulator.