Re: How well is my heating working at lower water temps?
Hydro coils are hard to dial in. What I have found works is once you get your outdoor rest in the ballpark is try reducing the water flow rate through the coil. Up to a certain delta T, the heat output (ie supply air temp) does not change much but you get much lower return water temperature which is what matters for condensing efficiency.
Kaos
Re: How well is my heating working at lower water temps?
You might appreciate the "beestat" phone app. It can display the ecobee data in various ways, time to heat, estimates temp loss based on outdoor temp, etc. This all can be informative for fine tuning of those supply temps or outdoor resets curves.
Re: HVAC Heat Shortcycling
Maybe this video will help you a bit, not the greatest IMO, but maybe better than nothing. Looks like his gas valve was failing but he never measured the voltage applied to it.
What does your flashing error code indicate ?
Re: HVAC Heat Shortcycling
It sounds like a one hour lockout. There should be a code while the fan is blowing cold. Time to break out the thermometers and manometers.
HVACNUT
Re: HVAC Heat Shortcycling
My HVAC came he checked few things here and there and suggest to replace the heater
Another Salesman!
Find a different service provider.
Where are you located?
pecmsg
Re: HVAC Heat Shortcycling
9 flashes does not seem to be on the error code list, so it may be the control board, its not happy with its self. It may be failing solder joints on the board.
Re: Clogged Heat Exchanger
Then @pecmsg's advise is not for you. He was referring to the water side as far as adding chemicals.
Let me read the manual to see if there is a maintenance procedure that will work for you.
Re: Lochinvar NKC150N - DHW High Temp Issue
Yeah, that "someone" was me. Check the back of your low voltage circuit board like I described above. If that looks OK and if you stay connected with us, we'll move on to the next thing until we figure it out. That's the way it works here.
Re: Monoflow system does not heat well
I agree with @Ironman.
I had an issue with my own house LOL.
Had an old boiler with a Monoflo system 1 zone. The system had a Taco 110. When that failed I put in an 007 and it worked fine.
When I sold the house, I put in a new boiler and an indirect used the same 007 but now had (2) 1" zone valves, indirect and heat. I had put in Honeywell zone valves with a Cv of around 5 I think.
Heating load was only 50 K with a 1 1/4 Monoflo loop. Sounded like a low pressure drop to me. On DHW it was ok with the indirect near the boiler.
On heat the 007 just wouldn't do the job the water was real sluggish getting around the main and this was without the indirect calling.
I took the Honeywell's out and put in 1" Taco valve I think the Cv was 7.5 or 8 and that solved the problem. Maybe I could have swapped to a larger circ for less $$$?
Re: How well is my heating working at lower water temps?
Initial glance on that graph, you can go down on the supply temp if you so desired. Even at the coldest part of the morning (6F?), your system not only maintains but brings up the temp. It doesn't seem to be struggling at all in that 24 hr period. Lowering the supply temp will minimize the cycling frequency but won't necessarily improve your overall energy efficiency as those air handlers can use a good amount of energy for delivery. I've seen many at 500 watts or more. Do you know how much your's pulls?
Do you know your btu/h output during that long 0400 run?
What design temp you are targeting?
This is from ecobee Thermostat? What equipment settings do you have it set for?