Re: 1930's Hydronic System help understanding
The only thing you need to calculate is the water circuit with the highest resistance to flow. Building height means nothing. PSI means nothing. Find the circuit that has the most resistance at the flow it needs. That is the head the pump needs to overcome. Then use that head with the total flow you need for all circuits.
Re: Trouble getting an Air-to-water heat pump for radiant retrofit in Virginia
Second chart is COP vs outdoor temperature:
I'm going to throw a couple of asterisks in here. First, the Arctic only reports three numbers, one of them is 3.1 at 19F, which is the yellow ball. I think that's an error, looking at where the other yellow dots are. If you take that one out the yellow line would be pretty much in a line with the others.
Second, the Mitsubishi, blue line, is a vapor injection model and unlike the others it doesn't have a straight line, it's really two lines depending on whether VI is enabled. It typically kicks in around 20F, and COP suffers while capacity is retained.
Re: Difficulty in Properly Sizing Equipment - 2140 Sq Ft New Construction Spray Foam House
Thank you for your kind words and confidence in Energy Kinetics, @2Luckysat .
The stackable Frontier EK1 is an excellent choice based upon your description. Because your home is will be so tight, it may be under negative pressure; for that reason you may want to consider a sidewall vented version, which will also save the chimney costs. The vent fan is quiet and should last a long time, it does not add significant complexity as there is only on additional proving switch and the fan motor. Today's oilheat is ultra low sulfur fuel which means boiler scale buildup is virtually eliminated. Going in the natural draft chimney direction (at least 10' high), we recommend a 5" corrugated metal liner although a 6" liner would also be more than adequate.
I think that it makes sense to install a heat pump for anyone replacing or installing a new AC system. The hybrid solution with a boiler and high efficiency water heater affords great flexibility and peace of mind in a potentially uncertain energy future. I agree with your two zone approach as well. For some extremely tight homes (near the passive house standard for heat loss); I saw a presentation where PVC was connected through rooms with a bathroom fan to redistribute the heating/cooling effectively with a single heat pump; the key in all applications is to make sure that distribution is adequate make all rooms similarly comfortable.
For the heat loss calculation, your heating and AC pro should be able to provide the calculations. As you mentioned John Hachmann, I'm sure he can facilitate your request if needed.
Adding further detail for @DCContrarian , after 400 kWh consumption, the all electric rate drops by about $0.04/kWh for PSE&G Long Island (see this link). @Hot_water_fan , good comments regarding output - one of the best sources and analysis that takes into account many field performance studies of heat pumps can be found here. This demonstrates that high efficiency cold climate heat pumps operate at a COP from about 2.0 to 2.5 at 30°F, and efficiency drops further as temperatures fall (a COP of 2, or 200% efficiency would lower $0.25/kWh to $0.125 or about $5.00/gal of oil equivalent; this compares to oil at $3.50 per gallon at 85% efficiency or $4.11 equivalent - a lower cost to operate with added comfort and quietness of operation). This reinforces the hybrid solution for heating economy, comfort, and emissions reductions with an efficient boiler and biodiesel blends.
Best,
Roger

Re: Difficulty in Properly Sizing Equipment - 2140 Sq Ft New Construction Spray Foam House
What are your local utility costs? Around me oil is about 3x the operating cost of a heat pump so it makes no sense for a new build.
You area already adding ducting for AC, so your additional cost is only the up charge to a heat pump which will be a fraction of the cost of oil tank, boiler, plumbing and rads.
18/BTU per sqft in zone 4 sound very high for a tight new construction. I would doublecheck the manual J assumption as something is off. It should be closer to 8-12btu/sqft.
Even assuming 39k is correct you could heat the house with a combination of:
https://ashp.neep.org/#!/product/64682/7/25000/95/7500/0///0
and
https://ashp.neep.org/#!/product/64684/7/25000/95/7500/0///0
These are modulating units, if you look at the turndown on cooling it is pretty decent so even though it is oversized for cooling load, it should still turn down enough.
My guess once you get your manual J dialed in, a single 2 or 2.5 ton cold climate heat pump can heat and cool your place without issues.
Bonus of a heat pump is the SEER rating on it is much higher than your typical AC, so your cooling costs will also be significantly less.

Re: correct gpm for open loop geothermal
Standard condenser water flow when you recycle the water is 3 gpm /ton nominal. Older ac systems that used city water and dumped it were based on 1.5 gpm/ton because the city water was colder.
So heat pump or not it doesn't change much your between the 1.5 and 3 gpm/ton. Don't forget 1 ton of cooling is 12,000 btus but you have the added heat of rejection from the compressor which is usually figured at 1.3 x 12000 btu or =15,600 btu/ton which used to be referred to as "tower tons" as a cooling tower was used.
Well water may be as cold as city water or it may not be. I seriously doubt the 1 gpm/ton the well guy said is correct
The manufacturer would be the best place to go to get specific information based on water temp and gpm flow. There will be some leeway on this
Re: correct gpm for open loop geothermal
As @DCContrarian and @ethicalpaul have stated, the gpm from the well for geothermal is related to the heat added or rejected. Exactly the same equation as standard hydronics. Any refrigeration problems with the condenser or pressures or all that magic will have nothing to do with it.
It would, though, be worth checking what your water intake and discharge temperatures are. You really don't want to freeze that drain field or the piping to it…. and, oddly, you don't want to cook it either. Discharge water temperatures much over 80 F will sterilize the soil in and over the drain field, which is not good.
Re: correct gpm for open loop geothermal
2.2 gpm per ton is a temperature change of 11F.
1 gpm per ton is a temperature change of 24F.
For heating, in many places that 24F drop would freeze up. Even at 2.2 gpm your source water can't be below 43F or you risk freezing.
Re: How to prevent hydronic piping from freezing?
There is a timer called ThermGuard that connects across your thermostat and will turn on your boiler for a programable set amont of time and a programable number of times per hour. It has a defult setting of turning on the boiler for 5 minutes every half hour. I purchased one for an area in the home that I didnt plan to heat but never installed it so I cant say anything about its reliability.

Re: How to prevent hydronic piping from freezing?
A word of caution, if there is any interface between your domestic hot water and the circulating heat system, then you must use only propylene glycol, never ethylene.

Re: correct gpm for open loop geothermal
Is this system a water furnace? How deep is the well, how far away is the dump point?
Check the gas pressure first before you do anything.
The well water is going to be cold 52 degrees or less so please keep that in mind when looking at the whole picture.
I guess you could flush the exchanger with strong vinegar and see how much build up is in it, you may very well have no restriction of flow.