Re: Happy New Year!
You as well Erin &Andrew!
Your even hand on the rudder keeps us all on the right course.
PC7060
Re: From Wall Hung to Cast Iron -- radiant / baseboard / indirect hot water
Hello JPennHill,
" Buderus is out of business " I thought it was part of the Bosch Group now.
Maybe set up both types for redundancy, especially if the Buderus still works.
Re: 2 risers compared to 1 on steam boiler?
you guys are awesome. As always I have gotten my answer in abundance. I am a professional licensed yadi yadi with 20 years experience. I have seen countless “pros” that are just plain inadequate. It’s no news. I have also never seen a pro put in sight glasses on a steam header to actually dig deep and see what’s going on. When I saw some of your videos ethical I was seriously impressed. I love them and appreciate what you’ve done for the community immensely.
Re: "Navien Combi Boiler: PSI, Gas Consumption, Condensation, and Baseboard Concerns – Seeking Advice!
there have been cases of the diaphragm being stuck in expansion tanks. Stuck against the nipple of the connection. Increasing fill pressure may pop it off. But remove and check pre charge first.
The more condensate you get the higher the boiler efficiency. I’m surprised you see that much with a fin tube system.
If it is piped with copper? It should not have a lot of water capacity, a #30 tank should be adequate.
Tune the boiler as others mentioned. A heat load calc would tell you if it is an energy hog structure.
The control should have other functions to dial it in, ramp delay, anti short cycle, burnrr limit, boost function? It varies from brand to brand.
Yes the 74 degree indoor will cost more than degree.
hot_rod
Re: "Navien Combi Boiler: PSI, Gas Consumption, Condensation, and Baseboard Concerns – Seeking Advice!
- Run time is too low. See about limiting max fire %.
- Lower supply temps
- Condensation is the goal. Did you read the manual?
Re: "Navien Combi Boiler: PSI, Gas Consumption, Condensation, and Baseboard Concerns – Seeking Advice!
Performing a combustion analysis with a digital combustion analyzer during minimum and maximum firing rates is a critical step in the start up procedure of any condensing boiler. This is in the installation instructions and is not supposed to be ignored.
The expansion tank air pressure needs to be charged to the static pressure of the fill valve before installing the tank. If you actually did this and you still have pressure increasing near 30 PSI while the boiler is operating the tank is too small. Sizing information is available from the expansion tank manufacturers.
Install a condensate pump and neutralizer.
Re: New Boiler - Radiator Screaming
I think "Got Steam?" Is a must read for most people. I think the Lost Art is a great resource and read for those who need ALL the information. IMHO.