Re: Steam Boiler swap savings
Don’t dismiss the fine points of dialing in your steam heat’s operation. I’ll add to the consensus that Getting control of the pressure and assuring you have good venting is really where big savings can be had. I would add that you should confirm the boiler is piped to the instructions provided with the boiler (at minimum) and that it was properly skimmed when installed. The latter two points are important for production of “dry” steam. Dry Steam carries few water droplets with it, providing maximum efficiency in heat transfer. Wet steam is heavy and wastes energy.
Regarding target pressure, it might be worthwhile to understand what variety of steam system you have. The reason I mention this is that if yours is a two pipe vapor system and you’re running more than several ounces of pressure you’re bound to be wasting energy.
For example, if I shut off half my radiators and allow the pressure to rise to 3psi, the cycle length is almost as long as it is with all the radiators open but at much lower pressure. It’s not hard to see that one could spike fuel use tremendously if the pressure is too high for the task at hand. There is such a thing as a Vaporstat that is like your boiler’s pressuretrol but it’s calibrated in ounces. It may be worth investigating.
A steam heating system out of calibration can be an energy hog. One that’s dialed in should be very economical to run, all other things being equal. Obviously heat loss is the other half of the picture. But start with confirming optimum steam system operation since it’s on your mind already
Re: Happy New Year!
You as well Erin &Andrew!
Your even hand on the rudder keeps us all on the right course.
PC7060
Re: From Wall Hung to Cast Iron -- radiant / baseboard / indirect hot water
Hello JPennHill,
" Buderus is out of business " I thought it was part of the Bosch Group now.
Maybe set up both types for redundancy, especially if the Buderus still works.
Re: 2 risers compared to 1 on steam boiler?
you guys are awesome. As always I have gotten my answer in abundance. I am a professional licensed yadi yadi with 20 years experience. I have seen countless “pros” that are just plain inadequate. It’s no news. I have also never seen a pro put in sight glasses on a steam header to actually dig deep and see what’s going on. When I saw some of your videos ethical I was seriously impressed. I love them and appreciate what you’ve done for the community immensely.
Re: "Navien Combi Boiler: PSI, Gas Consumption, Condensation, and Baseboard Concerns – Seeking Advice!
there have been cases of the diaphragm being stuck in expansion tanks. Stuck against the nipple of the connection. Increasing fill pressure may pop it off. But remove and check pre charge first.
The more condensate you get the higher the boiler efficiency. I’m surprised you see that much with a fin tube system.
If it is piped with copper? It should not have a lot of water capacity, a #30 tank should be adequate.
Tune the boiler as others mentioned. A heat load calc would tell you if it is an energy hog structure.
The control should have other functions to dial it in, ramp delay, anti short cycle, burnrr limit, boost function? It varies from brand to brand.
Yes the 74 degree indoor will cost more than degree.
hot_rod
Re: "Navien Combi Boiler: PSI, Gas Consumption, Condensation, and Baseboard Concerns – Seeking Advice!
- Run time is too low. See about limiting max fire %.
- Lower supply temps
- Condensation is the goal. Did you read the manual?