Best Of
Re: Long-term project to update old hydronic -- let's start with the Mercoid switch!
On a final note, I will admit that I really like having that nice, WARM, radiator next to me in the morning, and not sure how I will feel about a much cooler one (even if it keeps the house at the desired temperature). :)
Then you'll probably be pretty unhappy with a heat pump.
I'm also thinking your expansion tank is too small. Those gravity systems have a LOT of water.
Re: Long-term project to update old hydronic -- let's start with the Mercoid switch!
If it has a relief valve. I see what may be the discharge pipe for it. At 30psig it may be riding the relief valve because the precharge is wrong in the expansion tank or it is too small. Might be a higher pressure boiler too, I don't see a pressure rating on the ratings plate.
It is an old boiler but the savings in fuel from a new boiler will take decades to pay for the replacement. Looks like the mercoid aquastat has asbestos wiring in it but typically mercury switches will last forever in an application like that. The only application I know of where they have problems is in traffic light and flasher controls where they rock back and forth with a crank and clock motor and eventually after flexing once a minute or 2 for the better part of a century the wires eventually break.
The way to figure out if it will work at lower temps is to measure your radiators and figure out the EDR and convert that to output at different average water temps and compare that to a heat loss calculation. I bet under most conditions they don't get very hot before the heat call ends now but you should still keep the aquastat at 160+ or so.
Re: Long-term project to update old hydronic -- let's start with the Mercoid switch!
If that pressure gauge is correct, the water pressure in your system is too high. 30 psig should trip the pressure relief valve and put water on your floor. This is especially notable since the temperature gauge shows the boiler was cold when the photo was taken; water expands when heated and that will raise the pressure.
You may have a faulty or undersized expansion tank. Old gravity systems have a much larger water volume than more modern systems with fin tube or panel radiators, and the expansion tank size is based on the water volume.
you may also have a leaking pressure reducing (automatic water feeder) valve and/or a faulty pressure relief valve which is a critical safety device.
From what I can see on the rating plate, that boiler was oil fired when installed, and given the ratings for steam and water it burned up to 3 gallons of oil per hour. It is probably not the original boiler from 1925 but dates perhaps to the 1940s or 50s. This must be a large house!
bburd
Re: Long-term project to update old hydronic -- let's start with the Mercoid switch!
Two very different groups of actions here.
As you note, the number one priority if tightening up the house. That will determine how much fuel you use — although a newer boiler will, of course, make a difference too. But the envelope is the biggy.
The boiler… well, you probably need a new one. Until you do that, though, there isn't much point in worrying about the control. The old Mercoid may be out of adjustment — but it is reliable. You do want to worry about return temperature with the old boiler, though. They were never intended to condense, and so you want to make sure the return temperatures get above 140 for most of each heating cycle.
Re: What does "Wet Steam" mean to you?
My expectation would be that very wet steam would, after all the vents are closed, lead to higher pressure and eventually burner cycling. If there isn’t a proper header there could be cycling on the low water cutoff. Assuming all the pipes are pitched properly and the radiation is oversized for the house, I’m guessing you’d never know it was happening, except for the problems with vents getting debris in them. Just a guess.
Re: What does "Wet Steam" mean to you?
To measure create a simplified one pipe one radiator system. Put a drip right before the radiator inlet. Counterflow from boiler to radiator. Measure temperature at radiator (ideally multiple temperature sensors top, bottom, near and far). Configure boiler nbp to create driest and wettest steam. Run boiler for X amount of time. Over that time measuretotal condensate collected and measure area under each temperature sensor curve plotted as temperature vs time. Compare results for wettest steam config vs driest. Repeat 3 times each in randomized order.
Volunteers?😉
Re: What does "Wet Steam" mean to you?
Saturated steam (which is what heating boilers produce) is not "wet". It just means there's no superheat.
Wet means droplets. (Got this drummed into my head by a powerplant turbine guy- where you REALLY don't want droplets)
Re: What does "Wet Steam" mean to you?
😂I think you might have changed the question there! Sorry I forgot to vote, I would have selected 4, but with the caveat that not all wet steam is the same. The chart shows the power of steam heat is in the latent heat portion of the steam and you’re right that it’s hard to measure. But very wet steam carries a fraction of the heat transfer capability of ‘dry’ steam.
Re: What does "Wet Steam" mean to you?
It is very important that we use proper terminology when talking about technical issues. I have to look into my notes to verify this. When I got into steam heating 3 years ago I had a presentation that I would give to land lords and property managers. I wrote "wet steam is a condition in which 2% or more of the steam contains water droplets". Water is weighs much more than steams so I assume it is by volume. So no one gets confused, Steam is gas just like air, water droplets can float in air but will eventually come down due to gravity as with aerosol hair spray or an atomizer in an oil burner. These droplets can be small but they are not steam and do not have the same heat content as steam.
Re: What does "Wet Steam" mean to you?
By loud I mean hammering. I wouldn't know if my system's whooshing more than others.


