Re: 1 1/2 thermostatic radiator valve
On two pipe steam yes.
On one pipe steam, only if the radiator or TRV is equipped with a vacuum breaker.
Re: Gas line too small
Yes. or to contact the utility and ask them. part of the requirements of their mechanical permit to install it. don't pay the contractor until it is working and they have fixed the damage from the new gas line. you will have to pay the utility to install the larger line and meter. or maybe the contractor will suddenly figure out that they can install a smaller boiler and melt it more slowly with the existing gas supply.
Re: new crown gas fired steam boilers - water needed every week
This is best practice. Since your vent takeoff is at the ell on the end of the pipe, next best is to raise the vent not less than 8" above the ell. Higher is better.
As is, condensate will go straight into your vents and kill them in short order.
Re: new crown gas fired steam boilers - water needed every week
I would say it like "As is, if your boiler surges, water might go into the vent and carry some rust chunks into it will make it fail"
In normal operation the condensate gently rolls down the pipe and doesn't go anywhere but down. There is no "slug of water"
It's so cheap and easy to isolate the vents, though, I agree it's best practice to pipe it that way.
Re: new crown gas fired steam boilers - water needed every week
it isinsufficient, please replace with "a 3/4 street elbow to at least an 8" nipple. Put a Gorton #1 main vent on the end."
I would say "can you show me the new Hoffman main vent that you installed? What model number is it?"
It should be a #75 that looks like this:
Just for your information, when we say a given vent is insufficient, we mean it is too small in venting capacity to successfully vent a main. We don't even know for sure if the vent above is large enough, but it sure looks to me like you have a radiator vent on your main currently and that would be too small. Plus it looks old. But you can tell better than I can from the photo.
And as I recall, the Hoffman main vent above is about the same capacity as the Gorton #1 so if they are in love with Hoffman and want to install that, that is fine.
The additional fittings, the elbow and nipple, are to physically isolate the vent from the main pipe to protect it from water in the main. This is pretty standard stuff that should not be a surprise for them.
Re: Curious about combustion analysis?
@guzzinerd, I've created a new discussion for you here.
@EdTheHeaterMan, thanks for the heads up.
Re: Ascent EK1T smells like raw diesel
If you happen to be in the Hudson Valley NY area my company is trained on Energy Kinetics boilers and would be happy to assist you with this problem.
Re: Swing Joint on steam main
Actually it is just a straight run with the exception of 1 small rise in elevation of about 6 inches.
The boiler is in line with the border of the yellow and red buildings at the far right and the line ends in the basement below the sidewalk of the second storefront.
Re: 1 1/2 thermostatic radiator valve
Low pressure, two pipe, steam. Thought I mentioned that but I didn't. Editing now. Thanks for the heads up.