Re: Boiler insulation refresh
Any insulation will be on the jacket, not on the boiler sections — at least on the ones I've looked at.
Re: Boiler insulation refresh
It cant hurt. I would use the foil backed fiberglass duct wrap. Or you could probably use bare fiberglass. You could get a can of spray glue and glue the fiberglass to the inside of the jacket panels (clean them off first) Just insure that you don't block any air openings that allow combustion air into the burner.
Re: Issue with Navien flow sensor
Maybe put in a PRV to lower the pressure to 40psi maybe water hammer is causing it? Just a wild guess.
Re: Temperamental heating
Pipe pitch, broken, dilapidated straps that were securing the proper pipe pitch.
Re: Cost of Insulating Steam Pipes worth it?
In terms of return on investment, I would have to say it's a tossup. However, there are other benefits to insulating the mains — and efficiency is probably the least of them. The most important is that insulating the mains increases — sometimes substantially — the speed with which steam reaches the length of the main from a cold start. The means that it is much easier to get a good balance for the heating in various parts of the building, and it also means that the total run time of the boiler will be less. How much less? Hard to quantify.
There is also the benefit of reducing heat loss from the mains, of course. Whether that is a plus or an actual disadvantage depends on what, if anything, the basement is used for and how well it is connected to the rest of the structure. I warn you that there is a rather lively debate on this aspect…
In my opinion, insulating the mains is worth the cost — but some of the benefit will not be apparent to strict bean counting.
In another topic. The crossover trap and rip which you note are essential to correct operation of the system. Assuming that the crossover trap is working, the sole main vent at the boiler is ample. The other main which goes to the large radiator (sometimes referred to in old literature as a condensor), and it was thought to help speed up steam flow to the end of the main) should also have a crossover trap. It would worth figuring out where it might have been, and replacing it. Without it air removal from that main will be dependent on venting through the radiators. This is adequate, but slower than it might otherwise be — and limits the extent to which you can throttle radiators on that main, should you wish to do so.
I wouldn't be at all surprised to discover that this system was intended to operate on less than 1 psig, possibly as little as 8 ounces gauge. Depending on the radiator fittings (inlet and outlet) it is quite likely that it will operate more evenly and more efficiently if the pressure is limited to 8 ounces gauge.
The system should not water hammer at all. Water hammer is very rarely to be expected, but is almost always related in older structures to sections of main or runouts which have inadequate — or even reverse — pitch. It would be worth investigating and checking the full length of all the mains and runouts to ensure that they are, in fact, still pitched properly. Pay attention to sags.
And to this before you insulate!
Re: Cost of Insulating Steam Pipes worth it?
Since it is grossly oversized then insulating your pipes will make the short cycling more of a problem. You are already overpaying for the heat you need, what is a little extra insulation going to do for you?
After you come to replacing that boiler, years from now, with the proper size boiler, then I would look into insulating the pipes then.
Just an opinion, not based on facts.
Re: Excited about Boiler Design
Poly tarps are an inexpensive option for crawls. Insulate the walls of the crawl space. Tar paper is messy to kneel on and rips easily.
Air leaks where the plate and rim joist wood framing touches the foundation is "low hanging fruit" for those spray foam cans. Rigid foam board for the rim and joist bay ends, adhered in place with spray foam
hot_rod
Re: National Radiator Company - Natural Gas Boiler
Sounds like the "Black Toggle" which is a relay is not working.
Make sure the thermostat is turned up.
At the top of the control are terminals T & T Find a scrap piece of wire and hold a jumper between T & T (if you feel comfortable doing that). T & T are just low voltage 24 volt so you will not get hurt but there is also 120 volt power in that relay box.
Between terminals #1  there should be 120 volt power at all times.
Terminals X & X probably start the burner they are just contacts the power comes from the boiler thermopile and is probably millivolts
Terminal #3 should be live 120 volt which is powered from terminal #1 When the relay pulls in it powers terminal 4 internally from terminal 3. Terminal 4 I would guess powers the boiler circulator pump.
If the relay pulls in when you jump T & T the problem is in the thermostat or thermostat wiring.
Re: New Flue installation / touching pressure tank -- problem?
ask them to come back and correct; is a simple fix. As Ed said, the just need to extend the vent line coming out of boiler or main line going into chimney a couple inches. May be able to move enough by reorient the 45 or 90
PC7060
Re: Peerless boiler keep shuting off
Hello kjohn0402,
" I changed the blocked vent shutoff, thermal cut-off switch, boiler damper, and boiler aquastat relay, but it keeps shutting off. I have to reset it from the thermal cut-off switch to turn it back on. "
Item A; blocked vent shutoff,
Item B; thermal cut-off switch,
Item C; boiler damper,
Item D; boiler aquastat relay
The flame rollout switch is not included in the list, but probably not the issue since it is a one time fuse.
Are item A and B the same in your description ?
" The damper isn't closing " Why not ?
If the Block Vent Switch keeps tripping, I would check for the Damper not functioning correctly, restricted or blocked flue, insufficient draft, how does the combustion air get into the room (or the building).