Best Of
Re: Lochinvar / Knight Boiler 80-285 Issues
When was the last time the boiler"s heat exchanger and sensor cleaning? Service Due is probably a reminder to do a service after a programmed length of time in the boiler's program. The time is set in the programing. Much like a maintenance reminder lite on your car's dash.
Re: Simulating my home heating system for fun and profit
This is interesting stuff…. The folks at Brookhaven labs can take the winter off now!
Re: Boiler sizer-
I changed out that same boiler for someone, only it was 100,000 Btuh input.
It is notable that that boiler is rated for 100 PSI.
I did that change out because the old boiler was stuck in a closet with water heater on a carpeted floor.
The carpet was burned and after pulling the old unit out there was a hole burned in the floor……hopefully not your situation. The pump was not accessible being in the back corner, the exp tank was the same. The age was with the 1960's house.
I did a simple heat loss on the house, (1960's double wide with hydronic baseboard heat….how about that?) Old school, one page, heat loss called for 63,000 required. It came down to the fact that he had only 100' of 3/4" BB connected in a single loop.
100' of 3/4" BB at 550 BTUH per foot meant the BB could only deliver 55,000 BTUH at 170 average water temp.
So a Buderus/Boch GC 124/19 85% AFUE rated at 74,000 input was installed. Approved for combustible floor installation, has riser legs and also 2" concrete block platform was installed under it.
The homeowner did call the first winter that it was not quite warm enough in the house (usually runs temp at 74 or so). So he turned up the water temp for that time.

Re: Firebox question on old oil burner?
owners son who was 15 at time of 1980s said it was asbestos everyone else says he is wrong I think you guys are right so I’ll give you results of lab when they come back. You old timers usually know your stuff quite well

Re: Oil burner turns on for less than a second
The 1K1 contact sends 120 volts to B1 in the aquastat. If you check across neutral and B1 you'll likely see voltage interrupted.

Re: Boiler sizer-
If you have been in the house for a while you probably have some experience with what percentage of the time the boiler is firing during the coldest weather. If it’s firing 75% of the time or more during the coldest nights, don’t reduce the size. If it’s firing continuously and the room temperature remains below setpoint increase the size.
If you’re new to the house, I suggest having someone clean it and adjust the burners. Some of the cast iron boiler designs have a very long lifespan, some fail very predictably at 7 years or 14 years, etc. The boiler has been there for quite some time, it may be one of the designs that lasts indefinitely. Since you would replace it with a non-condensing boiler, there isn’t a significant efficiency gain or impressive technology update. Don’t express an urge to replace the system to your heating professional at this point. Many heating professionals will interpret that to mean that you’re hoping they can find something that helps you justify the expense of a new system to yourself even if they might otherwise say it’s aging well and will last at least another 5 years. If there’s any sign of a boiler leak or burner defects or other significant problem they’ll tell you.
Every boiler manufacturer periodically loses control of the quality of their grey iron casting line and the boiler sections have excessive internal stresses and/or material consistency issues. The result tends to be boilers that leak and fail in much less than 20 years. Sometimes just 2 to 5 years. Since your objective is reliability my suggestion is to keep an eye on the casting you have and when it needs to be replaced look for one from a manufacturer that hasn’t had any models with problems in the last 10 or 15 years. Don’t consider a sheet steel boiler instead of cast iron, there are a different set of problems that limit their working life. There have been good welded steel plate boilers made or imported from Europe in the past. I’m not aware of any being widely marketed for gas burners right now, but I don’t follow it that closely.
Re: Arctic Heat Pumps Air to Water Heat Pumps for Cold Weather!!
Hi Paul,
I am a hydronics specialist. Arctic Heat Pumps is a Air to Water Heat Pump or Hydronics Heat Pump. They are from Winnipeg Canada. It is very cold up there!! Near the Arctic Circle. The Heat Pumps work great up there in that environment. So they can handle any weather the lower 48 can deliver!!
Re: Arctic Heat Pumps Air to Water Heat Pumps for Cold Weather!!
I can provide design assistance and training for anybody in my territory on Air to Water Heat Pumps. I won major awards on designing Hydronic Systems. I also was a hydronics installer. I have scene it all in the field of hydronics.
Re: Lochinvar / Knight Boiler 80-285 Issues
" let me ask you this…if i were to start replacing parts, assuming something has failed, where would you start? "
check for 120v at the higher red circ, or from its controller(back of boiler) and the green one at the ceiilng also, if they have power, then the circ is bad, or jammed,
you mentioned the water was dirty, dirty water might have seized the circ(s),
the red one, isolate the circ with the valves above and below as you did earlier, on the end of the circ motor, that screw head, take it out, expect minor water, see if you can turn that shaft inside there to free it up or prove loose, put screw head back in.
may be able to do same on upper green circ,
if you don't have 120v at the circs, you have a controller or thermostat problem, did you check batteries at the stats?

Re: Lochinvar / Knight Boiler 80-285 Issues
purge on the boiler screen is part of the ignition / burn / shutdown sequence, not what we're looking for,
purging air from the zone loops is playing with all your valves, a hose, and forcing water where air should not be,
you need to figure why the circ(s) aren't circing,
one must be working in that your domestic hot is working,
can you post one distant picture showing the whole deal down there, floor to ceiling, left to right,
