Best Of
Re: Thermostat Issue
@Alan (California Radiant) Forbes
What is the net result you want to accopmplish?
- To have the heat pump be primary when above a certain outdoor temperature an the Radiant to be the primary below that temperature
- Have the radiant be the primary all the time and only use the warm air when the radiant cant keep up
- Have the radiant as the primary and not use the warm air in the heating season.
I can draw you a diagram to do 1, 2, or 3.
Need model number of the air handler and the outdoor unit. It gets tricky if the system has a variable speed ECM blower motor. But it can be done.
Re: Thermostat Issue
I think @ratio has the right solution. If you want floor heat priority, you can also move the floor heat to W1 and the air handler to W2 and Aux. You would still need a normally closed relay to de-energize G when W1 is on.
Kaos
Re: Thermostat Issue
Aux is aux, the thermostat is working as designed. What the customer probably wants though is for the floor heat to be primary and the heat pump to be aux.
That thermostat is just sending an on/off signal to the heat pump, so there's no reason why the heat pump couldn't be aux in heating mode. However, there's no setting that allows you to use the aux device for cooling in the summer, so you'd have to rewire between seasons.
What kind of heat pump is it? Would it be happier with a sensing thermostat that allows it to modulate to meet load rather than an on/off? If that's the case then two thermostats set a degree or two apart, with the floor higher, is probably the best solution.
One other note: is the floor using electric resistance heat? I can't count how many times I've had guys say that they'll configure the floor heat so it's only on "to take the edge off" but that the heat pump will do most of the heating. That's not how heat works.
Re: Thermostat Issue
You could use a 3 pole relay to disengage the G & Ys when the radiant heat comes on.
Re: Radiator-Baseboard-Piping Complexities
I like the copper stub idea best. Fairly durable, easy to connect to, and the same trim covers will fit over it if you want chrome or?
hot_rod
Re: I need a small Weil-McLain part if you’ve got one
Well, that sucks.
Sometimes you can cut a longer terminal block down to the five terminals you need. So if you have something longer? You "might" be able use that.
Or you can combine two smaller ones? I wish I could be more definite in my response. It is a matter of trial and error for sure and worth a try if you cant get exactly what you need.
Intplm.
Re: Thermostat Issue
It looks like a heat pump. Unfortunately any thermostat set up for heat pump, the auxiliary can't become the primary.
One option would be to program the thermostat for 2 Stage AC, 1 Stage Heat. If the reversing valve is energized in cooling, jump R and O, or Y and O at the condenser. Then of course the radiant is the only heat source, and that's probably not why they purchased a heat pump.
Seperate thermostats might be the best way. There's obviously no floor sensor, so if the radiant thermostat is at 70°, the heat pump thermostat could be set to 69° or lower.
HVACNUT
Re: Thermostat Issue
Looking at the manual, it appears that this thermostat cannot operate the two systems independently. The "auxiliary" system will engage when the setpoint is 3 degrees above the current room air temperature. At that point, the FAU would engage. I do not see any possibility of operating the two systems independently.
Of course, if they don't push the recovery too far, the FAU would not engage.
Re: Traveling Boiler Techs
I never did that work but I used it one time.
I remember my first commercial boiler job with a combination Gas/Oil burner. Might have been a PowerFlame. I did the commissioning myself and could not get it to run correctly on low oil. So it never got to high oil. I could coax it to high oil flame and get that set up properly but the low oil would not light. I could get the low oil to light but the High oil was smokey. Spent 2 days trying to get it right. Finally I called Weil McLain tech support and they recommended that I purchase their start up service that came with one year of labor warranty.
I bit the bullet and paid the fee. When the tech from WM came, he was actually another contractor like me and I told him my problem. He did exactly what I already did and found the same problem as I did. But he had experience that I did not have, and he went off book. He replaced the nozzles with different specifications and got the firing rate on low and on high to be compatible with each other. That nozzle change I was not prepared to do. Live and learn. The book isn't always right. Once I had that knowledge I never needed to purchase the start up service after that.
Re: Fixing the gurgling at the end of my Steam Mains
Sound like you have a plan.
Having a male copper into a female black pipe seems to hold up well, like your is, I'm not actually sure what code is in this situation.
Once you get the main extended and draining properly that should further reduce any spitting from the vents, I would just see how it goes. The 4 vents have a lot of 90 degree bends to get to them, so it may be fine.