Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
Best Of
Re: Burner keeps locking out..tried several things .. what to try next?
Here we go again. How many of these oil line issues have we had lately??
Another suction leak! The technicians you have obviously can't find the leak. You have a suction leak, find it and fix it and your problems are over.
Overhead line if it was me I would change it to two pipe or you can try a Tiger loop
Where are the technicians who can flare tubing and get a line tight?
I admit on threaded fittings leaks are more common since Teflon tape has been prohibited
Another suction leak! The technicians you have obviously can't find the leak. You have a suction leak, find it and fix it and your problems are over.
Overhead line if it was me I would change it to two pipe or you can try a Tiger loop
Where are the technicians who can flare tubing and get a line tight?
I admit on threaded fittings leaks are more common since Teflon tape has been prohibited
Re: Mod CON? Or Power vent 85%?
@Gordy Not sure if you're talking about me when you say "what gets me is that some say I'll only save 100 dollars a year. Now think of it collectively city wide, state wide, country, world wide. That's not peanuts. Every little bit adds up to huge energy savings in the big picture."
Sure, it adds up when a few million people do it, but those other people aren't responsible for putting food on my table. You had an argument with me that I should dump X amount into my house which would take me 111 years to ROI and I told you that wasn't practical.
It still isn't.
Sure, it adds up when a few million people do it, but those other people aren't responsible for putting food on my table. You had an argument with me that I should dump X amount into my house which would take me 111 years to ROI and I told you that wasn't practical.
It still isn't.
ChrisJ
0
Re: lochinvar noble
What is the heat load? If it is close to the 110 output, then the Navian is way oversized.
That is the challenge with combo units, usually one or the other side is a compromise.
That is the challenge with combo units, usually one or the other side is a compromise.
hot_rod
2
Re: Steam from the Sun, and a Possible Use for Carbon Monoxide?
Let's hope it is not eight!!!--NBC
Re: Troubleshooting a noisy radiator
@mattm , I'm glad you have some relief and thank you for following up and letting us know how things worked out. Sometimes we never hear back. That hammer you now hear may well be a pipe or radiator out of pitch when they replaced the valve. That too can be corrected fairly easily by making sure that radiator is still pitched towards the supply pipe. If it is, then raise both ends of the radiator up a bit with some shims under each leg and then re-pitch the radiator towards the supply pipe. What that will do is raise the horizontal supply pipe under the floor and give it a little pitch. Best of luck to you!
1
Boiler Piping
I'm going to start from the beginning so please bear with me. Three years back my wife and I purchased an old Masonic Temple which had been partially converted to offices. The existing steam system was one of the scarrier things I have witnessed but that is another story. One of the contingencies was that the former owner install a new boiler system. I have 40 years in the trades as a carpenter and 3 years of hard knocks and learning about steam the hard way. When we went through owner training I asked about all the water hammer in the distribution header and I was told that this is normal for steam (the trainer was the owner of the installing company). As a wood tick who was I to argue with the expert. The pressurtrol was set at 10 lbs and some rooms were not getting heat. I consulted with another contractor and they said that we could try turning up the pressure a little (nothing about venting). The first year we went around and fixed leaks in the system but it didn't help with the rooms that were under heating. It should of dawned on me that the radiators that were leaking the most were also getting hottest, it was a venting problem not pressure. Being tired of the "Experts advice" I started to do some research myself and I ran on to the Wall. It didn't take much reading to find out that this is the place where the true Steam Experts hang out. The first thing I did was purchase Dan Holohan's book The Lost Art of Steam Heating (I wish I had it long ago).
After reading for about 2 hours I went over and turned down the Pressuretrol to 1.5 lbs. and it's a miricale suddenly there's heat to all the rooms. We had some problems with overheating and we installed the Danfoss TRV,s on the 2nd and 3rd Floor 1-pipe system. And the complaints are gone (mostly).
After reading Dan's book further I realized that the near boiler piping needs work. We still have water hammer in the distribution header, although it has been reduced considerably. Now's where the experts come in. The existing header is constructed as follows.
*Header constructed of 6" pipe (see pics)
* 3" takeoff to Second Floor radiators (1-pipe system), 2" takeoff to 1st Floor North zone and 1st Floor South zone (2-pipe system).
* All 3 zones have a motorized zone valve. I know that this isn't Ideal; but I don't know how to get away from this. The tenants in the offices are really particular and if the temperature varies by a couple of degrees I'm getting a phone call.
* The existing header doesn't provide a way for the condensate to get out other than fall back into the boiler with some collisions into the steam along the way.
* The cross header is welded and does not have swing or slip joints (see pics). I'm not sure if we should cut the elbow and tees out, rotate them 90 degrees and add elbows to allow for expansion? I think that the vertical leg would rotate on the unions. Are we flirting with disaster with the current piping configuration? Thoughts?
* There are 2 Dunkirk D248-400 boilers that are piped together before they go into the distribution header. Based on Mr. Holohan's book my thought is to seperate them and put them into the header individually(see sketch). We removed radiators to do some apartment build outs and no longer run the 2 boilers in tandem (the apartments are on seperate forced air systems). When we were running both boilers, one boiler would shut down and it would suck the water out of the other causing excess makeup water to flood the system and blow the excess out of the condensate pump reservoir. We have 875 sq. ft. of EDR left in the building heating 6,500 sq ft with the average ceiling height at 9' With the latest improvements the building heat is staying at the set thermostat temperature even on sub zero days.
* As currently constructed the 2 First Floor zones are on the same 2" takeoff. Would it be better to have 2 seperate takeoffs? The zone valves are located about 2' after the header and then are reduced to 1 1/2" after the zone valve. If we do 2 takeoffs for the Floor should we use 1 1/2" or 2" from the header to the zone valve?
* Should we install a vent to remove the air from the distribution header?
* Is the attached sketch for the new header on the right path to remove water hammer and provide dry steam? I truly appreciate all of the advice I get from all of you as I have gained more knowledge reading information on this site and Mr. Holohans book than by talking to the local "experts". I've tried to explain this to the best of my very limited knowledge hopefully there is enough information that you folks can make some sense of it all. THANK YOU All.
After reading for about 2 hours I went over and turned down the Pressuretrol to 1.5 lbs. and it's a miricale suddenly there's heat to all the rooms. We had some problems with overheating and we installed the Danfoss TRV,s on the 2nd and 3rd Floor 1-pipe system. And the complaints are gone (mostly).
After reading Dan's book further I realized that the near boiler piping needs work. We still have water hammer in the distribution header, although it has been reduced considerably. Now's where the experts come in. The existing header is constructed as follows.
*Header constructed of 6" pipe (see pics)
* 3" takeoff to Second Floor radiators (1-pipe system), 2" takeoff to 1st Floor North zone and 1st Floor South zone (2-pipe system).
* All 3 zones have a motorized zone valve. I know that this isn't Ideal; but I don't know how to get away from this. The tenants in the offices are really particular and if the temperature varies by a couple of degrees I'm getting a phone call.
* The existing header doesn't provide a way for the condensate to get out other than fall back into the boiler with some collisions into the steam along the way.
* The cross header is welded and does not have swing or slip joints (see pics). I'm not sure if we should cut the elbow and tees out, rotate them 90 degrees and add elbows to allow for expansion? I think that the vertical leg would rotate on the unions. Are we flirting with disaster with the current piping configuration? Thoughts?
* There are 2 Dunkirk D248-400 boilers that are piped together before they go into the distribution header. Based on Mr. Holohan's book my thought is to seperate them and put them into the header individually(see sketch). We removed radiators to do some apartment build outs and no longer run the 2 boilers in tandem (the apartments are on seperate forced air systems). When we were running both boilers, one boiler would shut down and it would suck the water out of the other causing excess makeup water to flood the system and blow the excess out of the condensate pump reservoir. We have 875 sq. ft. of EDR left in the building heating 6,500 sq ft with the average ceiling height at 9' With the latest improvements the building heat is staying at the set thermostat temperature even on sub zero days.
* As currently constructed the 2 First Floor zones are on the same 2" takeoff. Would it be better to have 2 seperate takeoffs? The zone valves are located about 2' after the header and then are reduced to 1 1/2" after the zone valve. If we do 2 takeoffs for the Floor should we use 1 1/2" or 2" from the header to the zone valve?
* Should we install a vent to remove the air from the distribution header?
* Is the attached sketch for the new header on the right path to remove water hammer and provide dry steam? I truly appreciate all of the advice I get from all of you as I have gained more knowledge reading information on this site and Mr. Holohans book than by talking to the local "experts". I've tried to explain this to the best of my very limited knowledge hopefully there is enough information that you folks can make some sense of it all. THANK YOU All.
Re: Radiator Average Water Temperatures
I have noticed, when sizing fin-tube radiators, that manufacturers of high efficiency products provide ratings for average water temperatures (AWT) down to 90F. Other manufacturers of standard radiators provide correction factors down to the same number. I am a bit skeptical of a radiator operating effectively at these low temperatures especially at our design temperatures of -13F here in the North. The convection off these radiators has to counteract the cold air spilling off a window and I would think you would not want to go below 130F as an AWT. Does anybody know where there is some independent technical information on performance of baseboard vs AWT? Does anyone have experience with going low with AWTs - how low can you go? This would be for a "code" building, not a super insulated - triple glazed project. Thanks CamIf you are bent on low low temperature fin tube operation , one option is to force the convection.
Jaga has a product that matches to some of their fin tube offering that adds small microprocessor driven fans. They show performance #s down to 30C.
An interesting company with a unique niche product.
hot_rod
0
Re: lochinvar noble
If we ever become empty nesters the Vitodens 222-F would be my Ferrari of choice. 
Re: Buffer tank or no buffer tank
It makes no sense to zone smaller than the minimum firing rate of a mod/con. At some point, it has to become cheaper to heat a single bathroom, say, with electric, rather than adding a buffer to run the boiler longer at higher btu than is needed, for longer than would be needed, in the name of efficiency. There has to be a limit to the insanity.
2
Re: Taco VDT Pump
I was going to use one
on a wood boiler connection to its thermal storage. After getting cost on both . THE VDT verses a pump and Tekmar 157. The Tekmar was by far more cost effective.
on a wood boiler connection to its thermal storage. After getting cost on both . THE VDT verses a pump and Tekmar 157. The Tekmar was by far more cost effective.
TonyS
0
