Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
Best Of
Re: The importance of pH in steam-boiler water
Excellent info. Those old systems with the radiators in the condensate line may have been on to something. A few feet of fin-tube would surely cost less than an upgraded pump?
SWEI
0
Re: The importance of pH in steam-boiler water
@SWEI, Yours is a modification I frequently suggest. A building that has a lot of domestic hot water usage can install a shell and tube heat exchanger in the return line and use the hot condensate to preheat the DHW.
1
Re: Improperly Piped Steam Boiler
Since the radiators are oversized for the heat load convert the system to hot water. Remove orifices in traps you only need 1 gpm to get 10,000 of heat to radiator. May not need pump looking at piping.
Re: Basement renovation
Its great thought of moving the wet returns below the floor level but the most important thing to be kept in mind while implementing is maintaining the slope of water flow if the wet returns came back.
Renovation builders
Renovation builders
Re: Leaking Burnham V84 Steam Boiler
V8 has such a bad reputation I wouldn't fool with it. And, personally, I would keep the oil and go with a MegaSteam. It's that much better of a boiler. @EzzyT and @Dave0176 are both excellent steam men. Sometimes, if you are really lucky, you can get both of them on the same job. Now that would be heaven!
Re: Dunkirk XEB - the good, the bad, the ugly
The output on the boiler you listed is 94k, 94,000/1900=49.47They measured all of the rooms, length x width x height. They measured all of the heating units (length), they measured all of the windows and doors. They asked me about the insulation in the house, (R-30 in ceilings and crawlspaces above heated rooms; R-19 walls; R-11 in walls between rooms.
How did they do the heat loss? To do the heat loss they need to measure all the rooms and look at windows, doors, insulation, basically as much of the house construction as they can.
Also, in speaking with the representative from Dunkirk, he informed me the unit is designed for houses where the maximum heat needed is 112 BTU/h and the minimum is 20 BTU/h and that the amount of heat released is determined by the thermostat. He rejected the statement that it was oversized for a 1900 sq. foot house, saying that as long as it was not required to provide more than 112 BTU/h for any prolonged period, it was fine for installation.
Re: Leaking Burnham V84 Steam Boiler
If you've got gas in the area you'd be a fool to go with oil. It's still more expensive than gas and comes with a whole boat load of pain in the butt.
ChrisJ
1
Re: Altitude and Deration
direland said:
0-2000' low altitude no de-ration
2000'-4500' high altitude 10% de-ration necessary
Over 4500' high altitude 4% per 1000 or part there of.
0-2000' low altitude no de-ration
2000'-4500' high altitude 10% de-ration necessary
Over 4500' high altitude 4% per 1000 or part there of.
This is the correct way to derate an appliance. Tried to upload a picture i guess it didnt work.The last post is almost 3 years old?
You aced your gas test? Which gas.......</blockquote
The same Test I took for Gasfitter Class A and B in Canada. I had to make a account to post my input on your comment of others.
I also agree with other, that manufactures has their own procedures on de-rating an appliance or caloric value of a gas for high altitude, but on my provincial and my Red seal test, direland answer is the correct one.
0
Re: Right or repipe it
Yes it was! When I first looked at it, I started to say the same things that were said by others. Then I decided this had to be a trick question, of some kind so I decided to wait and see what others had to say. LOL Just goes to show there's more than one way to do things, conventional or not, if they work properly, that's the goal state.You mean like, how bullhead tees in a main work properly 99% of the time?
ChrisJ
0


