Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
Best Of
Re: How to ream pipe over 4"?
This machine has a reamer built in... it handles up to 6" pipe
https://www.wheelerrex.com/products/threading-and-grooving/pipe-threading-machines/6-inch-pipe-threading-machines/
https://www.wheelerrex.com/products/threading-and-grooving/pipe-threading-machines/6-inch-pipe-threading-machines/
Re: Elevated CO on burner tune up
It's only usable on an IOS device for free. It's a FileMaker database file, so you would need to download FileMaker Go (free) on the app store first.
Then open file from dropbox link, then 'Share', then 'Send copy of file', then select FileMaker Go. You can put a shortcut on your home screen to open directly from there.
Send me a PM.
Here's my YouTube channel with instructions on how to put it on your IOS device, and how to use most of the modules.
You could use it on any desktop, but you have to purchase the FileMaker database program to run it. Not really worth it unless you want to modify the program.
Then open file from dropbox link, then 'Share', then 'Send copy of file', then select FileMaker Go. You can put a shortcut on your home screen to open directly from there.
Send me a PM.
Here's my YouTube channel with instructions on how to put it on your IOS device, and how to use most of the modules.
You could use it on any desktop, but you have to purchase the FileMaker database program to run it. Not really worth it unless you want to modify the program.
Re: Plastic gas venting
PP isn't that much more money than PVC. And you have a locking ring vs primer/cement. You waste any cut pipe as it has a hub. Comes in 1ft, 2ft, 3ft, 6ft, 10ft lengths so measure lengths needed instead of buying all 10ft lengths like you would with PVC.
1
Re: The case of the non heating steam system, this Friday's case
Sorry everyone Had a routine medical test and they wouldn't let me have my cell. All is well. I thought for sure I would stump you on this. @ethicalpaul got it first. There was a steam pipe behind the thermostat that went to the attic. They kept it valved off before the boys moved there. Here is the link
https://youtube.com/watch?v=Bn9wCCs8ZE8
https://youtube.com/watch?v=Bn9wCCs8ZE8
Re: Plastic gas venting
@PeteA
If the new boiler can use 2" based on the footage and fittings used why not just cut the 3" flush with the wall and slide the 2" through it. Seal it with HT silicone.
If the new boiler can use 2" based on the footage and fittings used why not just cut the 3" flush with the wall and slide the 2" through it. Seal it with HT silicone.
Re: PowerFlame JR50A Issues
One damper should be roughly 1/4" open. It should not be leaking fumes around the blast tube. 2.2vdc is on the low side is this a UV detector or Flame rod? Honeywell 7800 control?
I don't remember the lowest the signal can go but most control MFGs whatever the minimum signal they say you have to have a higher signal to make the burner reliable. 5.0 is max I believe. @.2 sounds like they low end.
Pilots on PFs tent to be tricky. Take the pilot assembly out and clean it good. Adjust the gap on the electrode. Then get the pilot lit and put the control on hold and watch the signal. Make sure the electrode wire is good.
Play with the air setting and with the pilot reg to get the best (and steadiest signal) steady is important a
signal jumping from lo-hi is worse that a lower signal that is steady
And lastly. Check the 120 volts. Don't forget and a lot of techs don't realize this. If you ignition trand is rated 120/600 you only get the 6000 if you feed it with 120. Feed it with 115 you only get 5700out.
If ll else fails and you can't find the issue try a larger IG trans Webster used to make a 120/8500 volt singl pole. Not sure if that is still available. That used to fix the PF "C" burner when they had pilot issues.
Never had too many issues with the J but never worked on as many of those.
Work on those to get a stable signal and if you achieve that then maybe the transformer.
Propane or NG? Some utilities when the weather gets cold "shave the gas" by adding propane to the NG which can cause issues. Did this just start having problems?
What does the signal come up to when the Main Flame is on?
I don't remember the lowest the signal can go but most control MFGs whatever the minimum signal they say you have to have a higher signal to make the burner reliable. 5.0 is max I believe. @.2 sounds like they low end.
Pilots on PFs tent to be tricky. Take the pilot assembly out and clean it good. Adjust the gap on the electrode. Then get the pilot lit and put the control on hold and watch the signal. Make sure the electrode wire is good.
Play with the air setting and with the pilot reg to get the best (and steadiest signal) steady is important a
signal jumping from lo-hi is worse that a lower signal that is steady
And lastly. Check the 120 volts. Don't forget and a lot of techs don't realize this. If you ignition trand is rated 120/600 you only get the 6000 if you feed it with 120. Feed it with 115 you only get 5700out.
If ll else fails and you can't find the issue try a larger IG trans Webster used to make a 120/8500 volt singl pole. Not sure if that is still available. That used to fix the PF "C" burner when they had pilot issues.
Never had too many issues with the J but never worked on as many of those.
Work on those to get a stable signal and if you achieve that then maybe the transformer.
Propane or NG? Some utilities when the weather gets cold "shave the gas" by adding propane to the NG which can cause issues. Did this just start having problems?
What does the signal come up to when the Main Flame is on?
Re: Purple primer mess
So the clear primer cleaned up the purple primer for the win! I vote for cleaner primer with purple marker
Re: I'm finally building a new garage/woodshop. slab-radiant is a must!
I have radiant floor heat in my shop and really like it. My shop is 30' x 40' x 12 high. Approx. R-22 in ceilings and walls. Insulated overhead garage door. My calculated heat load was about 17.500 Btuh using Manual J. I heat it with a 50 gallon tank type electric water heater. The calculations and the actual performance have matched well; no surprises. I live in Nebraska and can keep 60 degrees down to 0 degrees F. The room also cools decently with a 14K window air conditioner.
2
Re: Is it ok to Modify Gas Pipe Line behind the Gas Range in this way
Hi there, when I pull out Bottom Tray of my Gas Range then I can see like this below. So what is this WHITE KNOW inside it, and is there any way I can Turn OFF Gas in case if I notice any Gas Leak in this way.
And what is the name of this WHITE KNOW Bottom of my Range inside it, and at this place my Hand can reach.
please let me know....Thanks



And what is the name of this WHITE KNOW Bottom of my Range inside it, and at this place my Hand can reach.
please let me know....Thanks




1




