Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
Best Of
Good demo of steam expansion, condensation and air pressure
I always recalled my HS physics class where the teacher boiled water in a gallon gas can, capped and cooled it. Steam expands 1700 in volume to liquid water. This old Julius Sumner film demos this and the power of normal air pressure and condensation of steam.
📸 Watch this video on Facebook https://www.facebook.com/share/v/RWJUX1KsRyLkHgLJ/?mibextid=0csxmW
1
Re: Are mod-con high efficiency boilers false economy Vs traditional cast iron over a longer time frame?
Brick ceramic lined on outside needs a liner always in my book unless the home owners wants to pay a mansory contractor to re point and repair ,Andy then line it .b vent usually is not a issue usually if ran inside the house in a chase but when installed In a framed out box outdoors there can be issue w the roll out switch and spill switch due to the b vent cold temp ,it happens .. as stated before most if not all masonry chimneys on outside needs to be lined or pay some big bucks to repair and not line only to suffer the same damages in a few years . My adage is repairs and line it and be done ,no liner mansonary repairs are in the crystal ball of the future . Any contractor who shrugs off talking about the chimney are not the educated contractor you want ,they just want the sale ,they offer nothing for your benefit . My mantra is yeah I include a lots of stuff that most would not do or think about ,the reason is different concerns there’s is there pocket book mine is both of yours. But a lot don’t see it that way and I’m really good w that that’s why we live in the free est country in the world and any adult can make a decission weather informed or uninformed . Gotta love this country home of the free thanks to the brave .
Peace and good luck clammy
Peace and good luck clammy
clammy
1
Re: Are mod-con high efficiency boilers false economy Vs traditional cast iron over a longer time frame?
@flat_twin
I think that is great that your learned your boiler and system and bought the equipment to clean and service it.
Most customers are not going to be able to do that. Which will last longer a neglected CI boiler or a neglected Mod Con?
Granted neither situation is any good. Either one could fail, either one could make CO.
But the neglected CI boiler unless the sections crack and leak will be able to be kept running for 30 years or more. If the boiler doesn't leak anything on that boiler can be fixed with standard parts even if the boiler mfg goes out of business with 1 exception.......the burners.
A Mod Con can't do that.
And I am not against Mod Cons. They are great on the right job, there great when maintained and they are great when the MFG still has parts and parts availability is an issue. And it shouldn't be after 20+ years of Mod Cons.
I think that is great that your learned your boiler and system and bought the equipment to clean and service it.
Most customers are not going to be able to do that. Which will last longer a neglected CI boiler or a neglected Mod Con?
Granted neither situation is any good. Either one could fail, either one could make CO.
But the neglected CI boiler unless the sections crack and leak will be able to be kept running for 30 years or more. If the boiler doesn't leak anything on that boiler can be fixed with standard parts even if the boiler mfg goes out of business with 1 exception.......the burners.
A Mod Con can't do that.
And I am not against Mod Cons. They are great on the right job, there great when maintained and they are great when the MFG still has parts and parts availability is an issue. And it shouldn't be after 20+ years of Mod Cons.
Re: What temp for a shop?
I am going to have to chew on this for about a week, but if I figure it out and can actually do it, I feel like at that point I should fly to Las Vegas and bet it all!LOL, you'll get the hang of it. I use this website to download historical/recent degree-day data for any location:
Very cool answer, I will try it out for a bit.
Where did you find the degree day info?
https://www.degreedays.net/
You can pick your nearest airport and enter its airport code, then specify the time period you want the data for.
1
Re: What temp for a shop?
The heat loss of your steel building is proportional to the delta T, or difference between indoor and outdoor temperature, which varies of course.
In Montpelier VT, the outdoor design temperature is -6 degrees, so at 63 degrees indoor you'd have a delta T of 69 degrees. (The outdoor design temperature means that 99% of the time, the outdoor temperature will be higher, so this is your "worst case" design target for a heating system.)
If you knew how much propane you had to burn per hour to maintain that 69 degree delta T, you could then scale that number with different delta T's to find your burn rate at different outdoor and indoor temps, but you don't know that number to start with.
So an alternate method is to look up the number of heating degree days for the period over which you burned 390 gallons of propane. For Montpelier, you had 1009 heating degree days over the last 5 weeks (35 days, which is close enough to your 36 day period). Now you can divide 1009/390=2.6 degree days per gallon.
So now you know that for every 2.6 heating degree days, you burn 1 gallon of propane. One heating degree day is 24 hours during which the outdoor temperature averaged 1 degree below your indoor temperature. So with an outdoor temperature of -6 and a resulting delta T of 69, you're probably burning 69/2.6=26.5 gallons of propane per day, or 1.1 gallons per hour.
Now you have a ballpark burn rate of propane per hour based on a delta T of 69 (1.1 gallons/hr). And you can scale that for different delta T's. Suppose you want to raise the indoor temp to 70, which gives you a delta T of 76. 76/69 x 1.1 = 1.2 gallons/hr. So now you're burning 1.2 gal/hr instead of 1.1 gal/hr.
Of course, 99% of the time your outdoor temp is above -6. On a more average day, say it's 30 degrees. Then your delta T is 63-30=33, and your burn rate is 33/69 x 1.1 = 0.5 gal/hr. Or for an indoor temp of 70 degrees, it would be 70-30=40, and your burn rate is 40/69 x 1.1 = 0.6 gal/hr. So on that day, it costs you 0.1 gal/hr more propane to heat to 70 vs. 63.
So now you can play around with different delta T's based on different indoor and outdoor temperatures. For any given delta T, divide by 69 and multiply by 1.1 to get your gallon per hour burn rate.
This ignores a number of complicating factors, but it's accurate to a first approximation.
In Montpelier VT, the outdoor design temperature is -6 degrees, so at 63 degrees indoor you'd have a delta T of 69 degrees. (The outdoor design temperature means that 99% of the time, the outdoor temperature will be higher, so this is your "worst case" design target for a heating system.)
If you knew how much propane you had to burn per hour to maintain that 69 degree delta T, you could then scale that number with different delta T's to find your burn rate at different outdoor and indoor temps, but you don't know that number to start with.
So an alternate method is to look up the number of heating degree days for the period over which you burned 390 gallons of propane. For Montpelier, you had 1009 heating degree days over the last 5 weeks (35 days, which is close enough to your 36 day period). Now you can divide 1009/390=2.6 degree days per gallon.
So now you know that for every 2.6 heating degree days, you burn 1 gallon of propane. One heating degree day is 24 hours during which the outdoor temperature averaged 1 degree below your indoor temperature. So with an outdoor temperature of -6 and a resulting delta T of 69, you're probably burning 69/2.6=26.5 gallons of propane per day, or 1.1 gallons per hour.
Now you have a ballpark burn rate of propane per hour based on a delta T of 69 (1.1 gallons/hr). And you can scale that for different delta T's. Suppose you want to raise the indoor temp to 70, which gives you a delta T of 76. 76/69 x 1.1 = 1.2 gallons/hr. So now you're burning 1.2 gal/hr instead of 1.1 gal/hr.
Of course, 99% of the time your outdoor temp is above -6. On a more average day, say it's 30 degrees. Then your delta T is 63-30=33, and your burn rate is 33/69 x 1.1 = 0.5 gal/hr. Or for an indoor temp of 70 degrees, it would be 70-30=40, and your burn rate is 40/69 x 1.1 = 0.6 gal/hr. So on that day, it costs you 0.1 gal/hr more propane to heat to 70 vs. 63.
So now you can play around with different delta T's based on different indoor and outdoor temperatures. For any given delta T, divide by 69 and multiply by 1.1 to get your gallon per hour burn rate.
This ignores a number of complicating factors, but it's accurate to a first approximation.
2
Re: Are mod-con high efficiency boilers false economy Vs traditional cast iron over a longer time frame?
I agree with @SuperTech & @tim smith above. The number don't favor mod cons unless you can keep them condensing.
If the Homeowner can do his own service that helps.
I am very Leary due parts availability and parts prices. A blower motor assembly can cost 1/4-1/3 the cost of a whole new boiler. After 10-15 years (maybe less) the mfg has moved on to a different design and parts are no longer available
I have seen mod cons work great on the right installation.
We used then to heat a 100,000 gallon tank located outside that stored fire sprinkler water at 50 degrees. They condensed all the time and two 200,000 btu mod cons replaced an oversized 1,500,000 btu gas fired atmospheric boiler.
They save enough in gas costs to pay for the entire job in less than a year. But that is a commercial job.
As @tim smith mentioned residential is different.
If the Homeowner can do his own service that helps.
I am very Leary due parts availability and parts prices. A blower motor assembly can cost 1/4-1/3 the cost of a whole new boiler. After 10-15 years (maybe less) the mfg has moved on to a different design and parts are no longer available
I have seen mod cons work great on the right installation.
We used then to heat a 100,000 gallon tank located outside that stored fire sprinkler water at 50 degrees. They condensed all the time and two 200,000 btu mod cons replaced an oversized 1,500,000 btu gas fired atmospheric boiler.
They save enough in gas costs to pay for the entire job in less than a year. But that is a commercial job.
As @tim smith mentioned residential is different.
Re: Are mod-con high efficiency boilers false economy Vs traditional cast iron over a longer time frame?
Here's another thought. Have you considered an Energy Kinetics EK1 Frontier? Again, I'm a homeowner not a pro, but many pros here have high praise for the Energy Kinetics. The benefits for you are that it's higher efficiency than a standard cast iron boiler, but it's non-condensing, so you don't get the problems associated with a condensing boiler. If you get the stackable EK1 Frontier, you get a compact system with a 40-gallon water tank for your hot water.
https://energykinetics.com/system2000-quietest-most-efficient-boiler/
So that might be the best of both worlds for you: higher efficiency with the good reliability track record of the Energy Kinetics, without going to a condensing boiler that brings more problems. And the stackable design is more compact than a traditional cast iron boiler with an indirect tank.
https://energykinetics.com/system2000-quietest-most-efficient-boiler/
So that might be the best of both worlds for you: higher efficiency with the good reliability track record of the Energy Kinetics, without going to a condensing boiler that brings more problems. And the stackable design is more compact than a traditional cast iron boiler with an indirect tank.
2
Re: Subdural’s Triumph
I was starting 7 boilers in a Boston high rise of 34 floors, and they had a women electrician running that job. One of the hardest workers I ever saw. We have several women pipe fitters/plumbers in our local union hall and get several new female apprentices every year.
Re: Subdural’s Triumph
Some of the best tradespeople I've worked with over the years have been women. Not quite so much tendency to take the if a little hammer doesn't work, try a bigger one approach. There are a few -- a very few -- jobs where sheer physical strength is helpful, of course -- but even there sometimes...
Re: Subdural’s Triumph
mattman said:When I worked for a mechanical contractor we had a tinner that was as skinny as could be that outworked half the men in the shop.
And she was a woman
3
