Re: question about swing joint elbow orientation on a Roth tank
Use a 3 elbow swing. Have the pipe come in past the centerline of the tapping put a 90 on the pipe then a nipple and another 90 then a nipple and a 90 down into the tank. So you come in past the centerline turn then turn and go back to the tapping. I would arrange the fittings so they tighten when the tank is filled.
I am not sure Roth knows what they want.
If the tank settles as it is filled and they are worried about a gap why do they have pipe hangers shown in the diagram??
Seems to me the pipes need to be unsupported so they will float with the tank or you will have a gap. Swing joints can't swing when hung.
Common sense must prevail. Just hook it up
Re: Installing new bathroom zone on a pretty screwed up system
Radiantec is the bane of Vermont and all of their clients who "fall victim". I have encountered too many of those systems. You did the biggest correction by adding a Viessmann boiler, transfer plates and insulating below the stapled-up 7/8 tubing. It might help if you insulated the 1" "long manifolds" so that more heat could get to the indiv. 7/8" loops. The floor sections with 1" manifold must be "plenty warm"! It seems like your challenge is to balance the flow, set the Viessmann boiler program properly and let IT decide the water temperature—not the indiviual mixing valves. Something close to constant flow would be best.
Re: heating oil tank manufacturer's warranty voided by transfer of oil from the old tank?
Yup. The infamous TL.
Everyone insists you can run single pipe overhead
But the you end up with a TL more times than not.
Re: Snow Melt Mavens, I need your advice
what type of boiler? What was the SwT with the valve closed, and delta?
Was the system under load ? Melting snow during the adjustment?
With the bypass closed the boiler must have been seeing cool return? 30 degrees or lower?
hot_rod
Re: Remodeled House. Now Radiators Are Way Too Large
If somebody decides to install an air to water unit in the future, they will thank you!
Kaos
Re: Remodeled House. Now Radiators Are Way Too Large
Not over sized… sized for max efficiency.
Did this w/ my own home. Cast iron rads. love it.
Re: ADVICE/IDEAS NEEDED! 3 Commercial Hot Water Heaters
Hi, Before doing any boiler room work, I'd be measuring shower flow rates and water pressures over at least a 24 hour period. If pressures fluctuate, I'd be looking at pressure compensating showerheads. Neoperl makes the innards for showerheads. I'd be installing 1.5 gpm heads if what you have now is larger. Once that work is done, I'd be metering hot water usage so yo know just what the demand really is. With that info, you can work in the boiler room and size the equipment to the measured need. You might find a lot of savings in equipment costs once the hot water demand is controlled. I know I'm not answering your questions directly, but this sequence of doing the work gives you the best chance of success.
Yours, Larry
Re: Question about swing joints
The riser coming out of the vise needs to go up to just short of the hole in the wall for the pipe going outside. You need a little pitch from outside to the tank but not that much. By exagerating the pitch your losing some of the swing.
The pipe (both fill and vent) only need enough pitch so they will not hold oil
Re: Question about swing joints
Re: leaky sink trap connection
Me? Depends. If it's new work — like a new sink — I have pretty well gotten to the point of changing what's leaking. Between warped sink outlets and oddly oval pipes and defective seal rings… aargh. Trade off between time to trouble shoot and price of the parts. On old work, however, I'll take things apart and see how it was meant to work in the first place and then fiddle and fix…