Re: New Crown boilers - updated piping
That's a tiny main vent. Should be a Gorton #1 minimum.
Re: Need more consistent domestic hot water
how many people actually need a. 199k tankless?
I lived with a 110 combi and a 133, plenty of dhw even when we’re were a 3 household.
The learning curve with a tankless is you never run out of hot water at the designed flow rate.
With a tank type you always run out at the designed capacity.

Re: Need more consistent domestic hot water
I'm not sure what your point is. Either you run higher pressure or you get a bigger meter.
The heater does the job it says it does. It takes what it takes.

Re: Burner Issue CLUELESS at this point
What type of situation is this that would have too much liability for a service company to come do service?
Re: Many years of issues with radiant floor heat.
Lots of chatter.
First. Changing the pressure the system operates at will have absolutely no effect on the heat distribution at all. None. Zip. Nada. 20 psig is ample, and it would probably be just fine at 15 psig.
Second, as @hot_rod points out, your problem isn't flow rate through the piping. You are getting an entirely reasonable delta T. So there's not much point in worrying about that.
Third, you are getting a reasonable input temperature to the loops. The near boiler piping isn't ideal, perhaps, but it works so leave it alone.
Fourth. The bad news. The floor arrangement, as installed, simply isn't capable of pumping enough heat into the room to keep it warm. Furthermore, spoiler alert, raising the input temperature enough to do so will damage that flooring as well as giving you a hot foot. A wood floor should not be run over 80 F, so even if you had piping which made the floor temperature reasonably even you couldn't get more than 20 BTUh per square foot out of the floor, regardless of input temperature. So raising your input water temperature isn't going to hellp.
You have a design which simply won't work. They happen.
The solution, though, isn't rocket science either: as has been suggested, additional emitters in that space. I'd suggest panel radiators. They aren't unattractive, they don't take up much floor space, they work well with the water temperatures you are working with, you can get beneath the floor to install the piping… What's not to like?
Re: Noisy circulator pump in new installation
Can't quite make it out, so I'll have to ask. Where in the circuit does the expansion tank and automatic feed valve tie in? And what pressure (looks like about 15 psig?) is the tank and feed set at?
What I'm concerned about is that the noise may be cavitation at the inlet to the pump. Whether this might happen is related to what is between the point of constant pressure at the tank and the inlet to the pump.
By the way — nice neat job of putting it together.
Re: High and low limit on the boiler
Well said, Ed. And so true.
But………are we talking a 368………..or a 568? 😉
Big difference!!!

Re: Is there a way to save this boiler?
Another Burnham gone at 8 years old. Way before it's time.
I could not reward Burnham with another sale after that, especially after only 8 years.
Too bad. Some Burnham models are sensitive to chlorides in the water. Also there was an issue with some models that were designed so that flue gas and steam were on the opposite sides of the cast iron, and they (Burnham) said it caused failures.
Your leak looks pretty small so it will get you to this summer.
Now you have to do your homework. Why? because there is a shortage (big time) of people that really know steam. Many will say they do and they do not.
This forum is filled with posts from homeowners (not there fault) that trusted the contractor to do the right install and install the boiler correctly.
Sorry you lost that boiler
Be happy you came here first, many have suffered bad installs and repeat bad installs when both boilers fail.
- Post your location (city/state) someone may be able to recommend a contractor. Also chek "find a contractor on theis site
- Measure all your radiators. Height, length and depth. Post back, Someone will help with sizing a new boiler.
- Why? because most contractors will guess and sell you more than you need. If a contractor does not measure the radiators show him the door. That is one way to weed out the bad ones.
Re: Attempting To Connect Ecobee 3 With Taco Zone Board And Air Handler
Why would an air handler be installed in such an inaccessible location? How long has it been there? There's nothing you can frame out in a wall or ceiling for better access?

Re: High and low limit on the boiler
Some boilers work ok with a tankless and some are awful. We used to have tons of the Ever hot external tankless coils. They are still available, but they probably don't sell many.
Ever see the tankless coil on an Arcoliner? Impressive. Probably good for 10 GPM. You can run the boiler at 160° and still have sufficient hot water (@3 gpm). If you ran a 1.00 nozzle, the hot water would be endless!